Has Anyone Ever Installed DIP Water Main in Contact With RCP Storm Drain?

04/15/2010 8:58 AM

I have run into a situation where I need to install a 8" DIP water main in contact with a 48" RCP storm drain. Has anyone ever dealt with this situation? Is there some type of HDPE or rubber pad I can install between the two? I can not go under the storm drains because of other utilities and can not go around because of wetlands. The alignment can not be shifted. A long time ago, I saw a similar situation, and the old time engineer cut a section of an old tire, wrapped it around the pipe, and laid it on top of the storm drain. This may be my only option. There is only 30" of material to the surface above the storm drains. Any help is appreciate.

__________________
You cannot escape the responsibility of tomorrow by evading it today - Abraham Lincoln
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Construction Engineering - New Member Engineering Fields - Civil Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member Popular Science - Weaponology - New Member United States - Member - New Member Hobbies - DIY Welding - New Member

Join Date: Apr 2007
Location: Latitude 38.701979 Longitude -90.439540 Coordinates 38.701979, -90.439540 N38°42.11874, W090°26.3724
Posts: 668
Good Answers: 15
#1

Re: Has Anyone Ever Installed DIP Water Main in Contact With RCP Storm Drain?

04/16/2010 8:41 AM

Has your local controlling authority for both the water line and the storm line been informed of this problem? They will usually have a solution for such situations. You'll probably not like the solution but they make the rules.

We've always tried to keep 10 feet clearance vertically and horizontally between utilities and sewers as required by the utilities. But when this isn't possible we have had to encase them in concrete spanning both the sewer and water line so many feet (usually 5 feet min) in each direction. Basically you are making a concrete bridge over the intersecting area.

__________________
scotchdrnkr
Register to Reply
Power-User
Engineering Fields - Civil Engineering - Member Engineering Fields - Construction Engineering - Member Engineering Fields - Mining Engineering - Member United States - Member - Member Popular Science - Weaponology - Member Hobbies - Target Shooting - Member Hobbies - Car Customizing - Member

Join Date: May 2008
Location: Cary, NC, USA
Posts: 131
Good Answers: 7
#2
In reply to #1

Re: Has Anyone Ever Installed DIP Water Main in Contact With RCP Storm Drain?

04/16/2010 10:28 AM

I am the local controlling authority. Sometimes you can not meet your own specifications, this is one of those situations. Like I said, can not go around, can not go under, have to go over. The cover over the storm drains is the issue - 2.8' of cover and trying to place an 8" DIP water main on top of the storm drains and keep adequate cover for the water main. The concrete encasement is an idea, but I don't want to create a point load on the storm drains, and cause further problems in the future. The RCP storm drains are already 25-years old.

__________________
You cannot escape the responsibility of tomorrow by evading it today - Abraham Lincoln
Register to Reply
Active Contributor

Join Date: Jan 2009
Location: Washington State, USA - the Soggy half
Posts: 15
Good Answers: 1
#3

Re: Has Anyone Ever Installed DIP Water Main in Contact With RCP Storm Drain?

04/16/2010 11:40 AM

We routinely run into similar situations. We place HDPE or rubber pads between the two lines creating at least a half inch gap. We also always center a full stick of pipe over the crossing to maximize the distance between the storm line and the water line joints to reduce potential cross contamination risk during water main failures. Finally we also usually encase the entire mess in concrete or CDF to further reduce the risk of cross contamination. According to our overseeing regulatory authority this is acceptable. If it was a higher risk crossing, say of a water line and a discharge line from a sewer lift station, we will use a 20 foot steel casing to run the water line through at the crossing.

Register to Reply
Commentator
Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: Mar 2010
Location: The most variable and beautiful State in the U.S. - And the worst managed and least livable one too.
Posts: 80
#4

Re: Has Anyone Ever Installed DIP Water Main in Contact With RCP Storm Drain?

04/16/2010 12:13 PM

As an consulting inspector I have seen these situations many times, involving many utility types.

The DIP needs to be sleeved, at least 5 ft. in either direction, as SCOTCHDRKR, suggested. The sleeving, using PVC or SDR type of pipe, will assist in the prevention of contact wear to either structure. Seal the ends!

The real reason for this, however, it to prevent local disturbance of one from the other should a rupture, of either, occur.

Then, ensure thorough compaction of the soil (such as base rock, NOT sand) used to cover both. A cement slurry mixture would actually be better, placed at least to the spring line of the sleeve. This will help stabilize the now disturbed soil around the SD. Continue adding/compacting to as much cover as is reasonable over the water main.

Assuming that final cover is an issue, leave the base 1' below final grade and pour a 3500 psi or better concrete with reinforcement on 12 in centers (both directions) 6 in. thick to 'bridge' the whole thing. Do this for the whole 10 ft. and full width of the trench or disturbed area. This spreds the load well above the pipes. This elevation can be adjusted up depending on the final grade finish. Leave enough for the required thickness of pavement to be placed atop the concrete or 6 in of topsoils.

__________________
Highly educated by life, books, and institutions. In that order. The Man denies me the big E title 'til I bow before him, cash in my outstretched hands and 'tests' sticking out my A%#. I bestow my own title: Engineering 'Technician' Extraordinaire!
Register to Reply Score 1 for Good Answer
Anonymous Poster
#5

Re: Has Anyone Ever Installed DIP Water Main in Contact With RCP Storm Drain?

04/25/2010 11:57 PM

Fyi while this close crossing proximity probably for multiple reasons flies in face of codes and standards recommendations, as many of you note stuff like this "happens" and I guess most folks would probably use ductile iron pipe and encase or partially encase the area where pipes are close together to provide uniform support to both structures (and minimize or eliminate point fulcrum loading etc.?) when they do this. About only other thing I could think of would be, as this is probably going to involve long established structures next to new excavation bedding/backfill, where there might be expected subsequent/relative movements/settlements etc., you might consider also providing a couple flexible joints (a "rocker pipe") near the boundaries of any concrete encasement with new excavation etc.

Register to Reply
Power-User
Engineering Fields - Civil Engineering - Member Engineering Fields - Construction Engineering - Member Engineering Fields - Mining Engineering - Member United States - Member - Member Popular Science - Weaponology - Member Hobbies - Target Shooting - Member Hobbies - Car Customizing - Member

Join Date: May 2008
Location: Cary, NC, USA
Posts: 131
Good Answers: 7
#6

Re: Has Anyone Ever Installed DIP Water Main in Contact With RCP Storm Drain?

04/26/2010 7:41 AM

All of your comments are exactly what I initially cam up with. However, there is not enough cover for the casing and the concrete. Also, to get a casing as strong as teh PC350 DIP, is quite expensive and no one stocks it. It appears the DIP manufacturer and the state would rather see the DIP installed with a rubber spacer between the twop pipes. I am going to remove the material down to the spring line of the stormdrains and fill it with concrete. Then encase the water main with concrete 1' outside and and above. Then once the concrete is set, install asphalt to grade.

__________________
You cannot escape the responsibility of tomorrow by evading it today - Abraham Lincoln
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Old Coal Man (2); RunsDownHill (1); scotchdrnkr (1); uncommon (1)

Previous in Forum: Support Beam Question   Next in Forum: Perimeter protection

Advertisement