Reverse Power

04/17/2010 7:47 AM

What causes reverse power in parallelling? Thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Reverse Power

04/17/2010 10:11 PM

Among the conditions that can do this are:

Poor fuel delivery to a generator (clogged filter, air leaks, etc.)

Wrong governor adjustment (or malfunctioning governor) to a generator

Incorrect voltage regulation (wrong setting or bad regulator) to a generator

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
Engineering Fields - Power Engineering - New Member

Join Date: Feb 2009
Location: Tamil Nadu
Posts: 66
#2
In reply to #1

Re: Reverse Power

04/18/2010 6:10 AM

rapid increase in bus frequency faster than governor response could give transient reverse power.especially if in parallel with mains or with larger machines.

__________________
Better not count the cent if the risk is many many dollars.
Register to Reply
Active Contributor

Join Date: Mar 2010
Posts: 22
#3
In reply to #1

Re: Reverse Power

04/20/2010 8:24 AM

THANKS TO ALL.