L1, L2, L3 and N Main Busbar Arrangement in LV Switchboard

04/29/2010 9:10 AM

Can somebody please guide me that if there is any standards governing the main busbar arrangement in a LV Switchboard?

From front to the back, should it be L1, L2, L3 & N or N, L3, L2 & L1? Which configuration is more preferred? Any standards saying so?

Thanks!!!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Member

Join Date: Mar 2010
Posts: 6
#1

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 9:50 AM

N:nearest

L3:near

L2:middle

L1:far

Register to Reply
Anonymous Poster
#4
In reply to #1

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 10:13 AM

Dear Gradually,

Any write up or technical notes or technical specs or whatsover reference to this arrangement?

Register to Reply
Member

Join Date: Mar 2010
Posts: 6
#5
In reply to #4

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 10:36 AM

from chinese standard(国标)

Register to Reply
Participant

Join Date: Dec 2007
Posts: 3
#6
In reply to #5

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 10:40 AM

Do you know any big brands of Switchboard (like ABB, Siemens, Schneider, etc...) is following this standard way of doing their busbar arrangement?

Actually i need some written documents to convince one of my clients.

Appreciate!!!

Register to Reply
Member

Join Date: Mar 2010
Posts: 6
#7
In reply to #6

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 10:58 AM

some of ABB, Siemens.N,L1,L2,L3(from inside to outside)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #6

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 11:52 AM

What does the Client want?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Dec 2007
Posts: 3
#10
In reply to #9

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 1:09 PM

the client wants L1, L2, L3 & N from front to rear. i am trying to convince him that our practice of the reverse way is also ok and need to support my statement perhaps with reference to some big names... that will be much more convincing

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/30/2010 3:00 AM

Provide the Client with what he/she is prepared to pay for, subject to its being safe.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 9:57 AM

Busbar arrangement:

A, B, C (or 1, 2, 3) from left to right, front to back, top to bottom as viewed from front side.

Reference Standard:

ANSI C37.20.1 Section 7.1.1.1

NEC 430.97 (B)

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster
#3
In reply to #2

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 10:11 AM

Dear Sir,

I found this statement also in the internet, but my case is with neutral unlike what happen in the most MCC

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#8
In reply to #2

Re: L1, L2, L3 and N main busbar arrangement in LV Switchboard

04/29/2010 11:14 AM

In addition to the above, other arrangement is also permitted by both of the standards but each phase shall be clearly marked. So, in regards to neutral, you can place it any suitable location (say A, B, C, N or 1, 2, 3, N) and clearly mark it.

Quote from the standards:

ANSI C37.20.1, Section 7.1.1.1: " …. Certain types of equipment may require other phasing arrangements and a neutral conductor. In these cases the phasing shall be suitably indicated."

NEC 430.97 (B): "…….Other busbar arrangements shall be permitted for additions to existing installations and shall be marked."

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#12

Re: L1, L2, L3 and N Main Busbar Arrangement in LV Switchboard

04/30/2010 9:42 AM

Phasing is often driven by the switchgear chosen, e.g. using an ABB or Schneider 4 pole Air Circuit Breaker, N will be on left (looking from front) i.e. N, L1, L2, L3. Terasaki ACB will be L1, L2, L3, N again looking from front. Your choice, both are correct, if marked, as stated above.

__________________
rogerggbr
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".