MCCB Ith & Ir Acronym Meaning

05/02/2010 9:16 AM

We are planning to replace our Chiller with bigger capacity.

The motor rating of old chiller is 375 kw whhle the new one is 570 kw, all at 380 volts, 3phase , 60 hz. The suppllier required us to a circuit breaker with minimum ampacity of 911 amps.

our existing Circuit Breaker is SACE ABB, Iu =1250, Ue =660 Volts, 3 poles. Their is a rating of Ith @ 45 deg C of 800 Amps maximum and Ir = 6300 max. My questions are:1. What is the Ith & Ir means. 2. Can i use ourold MCCB with the rating of 1250 Amps Iu?

Please all extert here help me.

My best regards to all.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: What is the Ith & Ir at MCCB stand for?

05/02/2010 2:42 PM

Ith is the thermal current rating of the breaker. The more the motor current exceeds this, the quicker the breaker will trip. I'm unsure of the other abbreviations, but they may represent the magnetic trip rating, which is nominally instantaneous.

If the motor requires 911 A, it is likely to trip this breaker either 1) right away if the starting current exceeds 6300 A, or 2) in a short time if the running current exceeds 800 A. So I don't think this combination will work.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: Nov 2009
Posts: 42
#2
In reply to #1

Re: What is the Ith & Ir at MCCB stand for?

05/02/2010 2:59 PM

Thanks, but how about the Iu (1250 Amps) which i believed is the nominal current rating. Our MCCB rating Iu = 1250 Amps & Ue is 660 volts. then their is anothr rating which is Ith = 800 max @ 45 Deg C. any idea on this Sir?

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: What is the Ith & Ir at MCCB stand for?

05/02/2010 4:15 PM

My idea on that is exactly as before. If the thermal rating Ith of 800 A is exceeded by the 911 A motor, the breaker will trip (sooner or later).

However, if the ambient temperature at the breaker is less than 45°C, the Ith will be somewhat higher. This may get you by, but it looks really borderline. Reduced-voltage and unloaded starting will also help.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#5
In reply to #2

Re: What is the Ith & Ir at MCCB stand for?

05/03/2010 5:16 AM

ASK ABB for their catalogue on MCCBs select yourself you will find all inputs required you could download the catalogue from ABB web site.

good luck

murali

Ex power user

Reply
Associate

Join Date: Nov 2009
Posts: 42
#6
In reply to #5

Re: What is the Ith & Ir at MCCB stand for?

05/03/2010 8:46 AM

thanks. this an old model MCCB from ABB. SACE SN1250 model. Installed last 1986 by the German Contractors here in KSA.

All I want to know is if could still use this MCCB. But i think the best solution now is to buy a new MCCB.

Rgards to all.

Reply
5
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: What is the Ith & Ir at MCCB stand for?

05/02/2010 7:01 PM

Extract form appendix K of standard IEC 60947 -2

Voltage

  • Ue = Rated operational voltage
  • Ui = Rated insulation voltage
  • Uimp = Rated impulse withstand voltage

Current

  • In = Rated current
  • Ith = Conventional free –air thermal current
  • Ithe = Conventional enclosed thermal current

Short -Circuit

  • Icm = Rated short circuit making capacity
  • Icu = Rated ultimate short circuit breaking capacity
  • Ics = Rated service short circuit breaking capacity
  • Icw = Rated short time withstand current

Trip unit

  • Ir = Adjustable overload setting current
  • 1.05xIr = Conventional non –tripping current
  • 1.30xIr = Conventional tripping current
  • Isd = Short time delay tripping setting current
  • Ii = Instantaneous tripping setting current
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 5)
Anonymous Poster #1
#7
In reply to #4

Re: What is the Ith & Ir at MCCB stand for?

06/14/2018 3:20 PM

I have Schneider 800A mccb how to set 800a to 400a???

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: What is the Ith & Ir at MCCB stand for?

08/22/2024 7:20 AM
  • Start with the instruction manual that came with it, and a mk.1 eyeball with which to read it.
  • If that fails, get on the 'phone to <...Schneider...> and ask.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".