HVAC Question - Water Cooled Chiller

05/10/2010 1:43 PM

friends another problem to solve.what is the advantage of installing water cooled chiller instead of air cooled chiller in industry.? .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: HVAC Question - Water Cooled Chiller

05/10/2010 1:54 PM

A LOT smaller size for for the same capacity.

Water has a higher heat transfer coefficient and higher heat capacity than air.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#2
In reply to #1

Re: HVAC Question - Water Cooled Chiller

05/10/2010 1:58 PM

Guest #1 cont'd

For example:

'h' the heat transfer coefficients can be 2 orders of magnitude different.

  • Air - 10 to 100 W/m2K
  • Water - 500 to 10 000 W/m2K
Register to Reply
Associate

Join Date: Dec 2009
Posts: 42
#3
In reply to #1

Re: HVAC Question - Water Cooled Chiller

05/10/2010 6:00 PM

Water has an even bigger advantage over air for use in cooling or heating thats never used as far as I can see. Water can be cooled by maintaining a low pressure boiler so the water boils at ~10C. The vapor can be compressed and condensed in the atmosphere thereby transporting heat out or evaporation can be done at the other end to move heat inside. Use of water is a much less costly way to transport heat in and out to heat or cool.

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: HVAC Question - Water Cooled Chiller

05/10/2010 11:40 PM

In a water/lithium bromide absorption chiller, water is used as the refrigerant and LiBr as the absorbent. The evaporating temperature of the water is approximately the 10°C you described. In a hot, dry climate it should be feasible to power the regenerator by focused solar heat. A black pipe solar collector might even be enough, or nearly so.

I suspect this scheme would be a prime subject for Salahuddin's investigation.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Apr 2014
Location: Redwood city ca, Taipei Taiwan, St. Louis mo.
Posts: 11
#11
In reply to #3

Re: HVAC Question - Water Cooled Chiller

07/09/2014 5:35 PM

I Worked in HVAC for 16 yrs. If you are familiar with how cooling towers work, they do use the cooling quality of water to enhance standard refrigerant systems. these systems are only seen on large commercial buildings but could be rigged up for your home. The huge systems run the hot compressed refrigerant through a small compact system within the building, the evaporator coil is inside the ductwork and works the same as any household system. The Condenser is inside a water jacket (water runs over the coils instead of air like a residential system) the hot water is pumped to the roof where it falls like rain into a huge cooling tower/house. the cooling tower has blowers that help cool the hot water and after it is chilled it is sent back down to cool the hot condenser coils. I have often thought this type of system could greatly reduce residential systems energy costs, but have never designed a system to do it. If anyone is interested in working on it I would love to collaborate on it. Thanx Harold

__________________
"Everyone has the ability to come up with crazy ideas. Genius is the ability to identify the useful ones " Haroldoftroy
Register to Reply
Associate

Join Date: Dec 2009
Posts: 42
#12
In reply to #11

Re: HVAC Question - Water Cooled Chiller

07/09/2014 10:45 PM

Hi Haroldoftroy, It has been a few years since any activity has occured on this topic. I am very interested in developing a well engineered heat moving device. The current state of art(as you well know)fails to move heat efficiently no matter what off the shelf machinery is chosen.

Register to Reply
Anonymous Poster
#5

Re: HVAC Question - Water Cooled Chiller

05/11/2010 8:16 AM

Energy requirements are less if a cooling tower is used instead of ambient air. A cooling tower produces water at around 85 degrees F, versus ambient air at 100 degrees F (+/-). Water has a much higher specific heat compared to air. The compressor simply sees a much lower condensing temperature and presssue on its discharge side (around 85 degrees F) compared to ambient air at 105 degrees F (I'm from Texas).

Register to Reply
Member

Join Date: May 2010
Location: Bristol CT
Posts: 5
#6

Re: HVAC Question - Water Cooled Chiller

05/11/2010 9:10 AM

The first thing to consider is, "do you have a cooling tower" If so I agree with everyone that water cooled is better. If you have to invest in a cooling tower, that will cost you more. The other question is, "what size chiller are we talking about 6 ton or 106 ton?" Makes a big difference when discussing water or air cooled.

__________________
CLaude Noiseux Technic Inc Equipment Division
Register to Reply
Associate

Join Date: Dec 2009
Posts: 42
#7

Re: HVAC Question - Water Cooled Chiller

05/11/2010 1:25 PM

A cooling tower still trafers heat to the atmosphere even if it does so at lower temps than an air cooled condenser. Its a trade off between energy and water so it all depends where the system is located. The low pressure boiler can be used in both air and water cooled condensers. Its just more efficient to move heat from ~10Cto50C using water but maybe better solar powered cooling can be developed that I don't know anything about. Are there links to useful(rather than useless) info about this? As for water cooled chillers, it seems a lot of engineering needs to be done to develop a really good system. Lots of details need to be worked on.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: HVAC Question - Water Cooled Chiller

05/11/2010 11:31 PM

The OP is rather unspecific.

A water-cooled shell/tube or plate/frame condenser can offer the advantages of compact size and lower refrigerant condensing temperature/pressure. This may save considerably on compressor power, and the water pump will likely also need a bit less power than the fans for an air-cooled condenser. Some disadvantages are that it needs a large supply of water; it warms up the water, which may not be environmentally acceptable; it may experience erosion from particulates in the water, etc.

An air-cooled condenser will be much larger, and especially in hot climates it will result in greater compressor power and higher condensing temperature. Except for perhaps some water cooling for the compressor, there may not be a need at all for water.

An evaporative condenser is somewhat in between the other two, in most respects.

***

On the evaporator side, a lithium bromide chiller is a perfect example of a low-pressure boiler. Whoever voted the earlier post as OT is remarkably ill-informed about refrigeration, and also lacks vision.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jan 2010
Location: Charleston, SC
Posts: 25
Good Answers: 1
#9

Re: HVAC Question - Water Cooled Chiller

05/12/2010 1:22 PM

Although you will certainly have better net efficiency, there are several disadvantages to consider for the water cooled chiller with cooling tower. First, it is more complicated. You have an extra pump to serve the condenser water to the cooling tower. This energy needs to be applied to your net efficiency. Next, cooling towers require a lot of maintenance and consideration. There is scaling, corrosion, rust, algae, sun damage, ugliness, high sound levels, freeze protection, health issues, and general maintenance. Cooling towers can use a lot more water than you think, based on the local wet bulb temperature. This cost should technically be be factored into the net efficiency. The owner of a cooling tower really needs a good maintenance person to look after it.

__________________
R. Turner, P.E.
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 142
Good Answers: 1
#10

Re: HVAC Question - Water Cooled Chiller

05/13/2010 4:11 PM

Good point on the additional cost on chemical treatment, the more water the more chemical, if you don't have a competent chemical treatment program you can virtually destroy the system and related equipment with in one year depending on the quality of available water. I have seen this happen in a process application.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); cnoiseux (1); greendog (3); Haroldoftroy (1); pipeit (1); Tornado (2); toughguy1 (1)