Had an interesting situation yesterday that I would appreciate some expert opinions on :
The site is a printing factory where a compressor driven by a 30KW 3-phase induction motor is being installed. The motor is started with a star-delta starter. Motor FLA is 57A, and the thermal overload relay is set to 30A (note overload wires inside the delta in a S-D starter setup). The feeder from the switchboard is about 30m long, feeder protection is a 50-63A MCCB with the magnetic trip factory set to 504A.
When the Start button is pressed, the motor starts to spin up for about 2-3 seconds, and then the MCCB trips. A clamp meter around one of the phases reads 350A while the attempted startup is in progress.
My comment to the contractor was that the startup current is too high for a 57A FLA motor starting in star mode, it should be lower than this, around 200A. I suggested that either the unloader valve on the compressor is not working (motor starting under heavy load), or the starter is incorrectly starting in delta.
The contractor is going to install another MCCB today, this one with adjustable thermal and magnetic trips. He believes that if he can stop the breaker tripping, he will have solved the problem.
I think that if he does this, he will be back on site before long to either repair the starter or replace the motor, but he don't need no stinkin' advice from some upstart engineer so all I can do is watch and see what happens.
Thoughts, anyone?