Why Fuse is Not Placed in Neutral Wire

05/13/2010 2:35 PM

Hi All, I have read in the web that a fuse is never inserted in a Neutral wire. Can any one tell me the reason for this? What will be the consequences if it is inserted?

__________________
The important thing is not to stop questioning.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Why Fuse is Not Placed in Neutral Wire

05/13/2010 2:49 PM

Gross generalizations:

A) No amount current in the Neutral could be there unless it came from the phases (or Hot). So in effect, if you have fusing n the phases, you have protection of the neutral.

B) If a fuse was put in the neutral of a 3 phase Wye / Star system and it opened, you phase voltages would be floating, not good. If you have a North American single phase system, an open neutral would not be as bad, but t is a waste.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Why Fuse is Not Placed in Neutral Wire

05/13/2010 7:22 PM

The most reason is there is a major safety concern to this.

Simply think a single lighting circuit where you have fuse in neutral and if it is blown and you see the light is off. You thought there is no power supply (STOP: there is power supply) and carelessly try to repair it. Think about the case may happen to you.

For the same reason, it is not allowed to use disconnect switch in the neutral line.

Hope it is clear now.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Why Fuse is Not Placed in Neutral Wire

05/13/2010 7:33 PM

D'oh!

That too!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5
In reply to #1

Re: Why Fuse is Not Placed in Neutral Wire

05/14/2010 8:40 AM

I may have an exception to this:

Portable equipment on plastic casters with no part touching any grounding surfaces and fed by a three phase source with no neutral. (think 208VAC in USA with standard 4 wire plug as installed on portable equipment) The equipment has a control panel with the ground conductor connected to the panel and back plane. A meter is installed in the control panel that operates only on 120VAC. You do not want to use ground as a neutral in this case, since, if ground is ever broken in the cord feeding the panel, the 120VAC is connected to the equipment body. Therefore, you use a stepdown transformer to 120VAC, but the leg that would be neutral and connected to ground, must float, and therefore should also be fused. Isn't this essentially a "fused neutral"?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Anonymous Poster
#7
In reply to #1

Re: Why Fuse is Not Placed in Neutral Wire

05/21/2010 9:59 PM

Thanks for your answer. It helps me.

Register to Reply
Anonymous Poster
#4

Re: Why Fuse is Not Placed in Neutral Wire

05/14/2010 1:59 AM

hi Madhusudan,

Let me tell you that why fuse is not placed in neutral wire. It is so because if due to voltage drop or sudden high voltage if fuse wire trips which was placed in neutral then the equipment connected to the phase wire remains connected and flow of current will remain passing through it and we may get shock though the circuit is incomplete and in such case only neutral wire will get cut off the circuit but if we place fuse in phase wire then if fuse wire trips then we will not get shock. we will be safe.

Thats the main reason why fuse wires are not placed in neutral and are placed in phase wires. I hope you might have got it cleared.

Regards,

Mani Mohan Chhibber

Larsen & Toubro Ltd.

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Why Fuse is Not Placed in Neutral Wire

05/18/2010 9:32 AM

It's contrary to British Standard 7671.

Were it to be there and to be removed for, oh, say, the replacement of an Edison-screwed lamp, although the lamp would be off the circuit would still be connected to the live conductor, and a shock remains possible.

Don't fuse neutrals!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); JRaef (2); msamad (1); Phys (1); PWSlack (1)

Previous in Forum: Capacitor Current   Next in Forum: Motor on SD-Starter Trips Breaker on Startup

Advertisement