Determination of Size of Conductor/Cable

05/31/2010 6:21 AM

How to determine the size of conductor or cable...i need the basic formula.. not a selection chart from different manufacture.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Participant

Join Date: Dec 2009
Posts: 2
#1

Re: determination of size of conductor/cable

05/31/2010 11:47 AM

The size of the conductor or cable may be determined by the current (amperage) and the voltage requirements. If you can find that information, you can check the National Electrical code table 301.16 and match the ampacity of the conductor to your requirements. Also, take in consideration the if the conductor will be copper or aluminum. Aluminum conductors will require a larger size in order to carry the same current.

If you need to determine the size in order to install the cable or conductor inside a raceway, the NEC also have tables that will provide that information.

The only formula I can think you can use in order to determine the size will requirer you to know the distance, ampacity and resistance per foot of the conductor you may want to select and see if it can carry the load to be connected. In this case you will need to have a manufacturer's table that will provide you wit this info.

Hope this helps.

Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2

Re: determination of size of conductor/cable

05/31/2010 12:47 PM

I guess you've forgotten the formula for converting conductance into conductivity. But don't forget you'll also have to include the heat dissipation per unit length of a resistance formula. Oh and since we're talking about heat you'll have to also include the effects of heat on the insulation. So you'll also need to calculate the electrostatic breakdown voltage over temperature to determine a catastrophic failure level and for just the change in resistivity of the insulation. Thinking about insulation, you'll also need to include a conditional clause for deciding to include the moisture permeability equations in case the wire will be direct buried. Another conditional clause on the insulation will be if ultra-violet radiation degradation of the insulation should be considered. You should also include a conditional analysis to see if the wire lengths will be long enough that transmission line calculations instead of lumped element calculations need to be done.

Now I could go into a little more depth and provide you these formulas and conditionals, but I've gone as far as I will without getting paid for my services.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6
In reply to #2

Re: determination of size of conductor/cable

06/01/2010 5:56 AM

Thanks! -- Saved me a lot of typing!

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Anonymous Poster
#3

Re: determination of size of conductor/cable

05/31/2010 2:05 PM

(a+b)(a-b) = a2-2ab+b2

Register to Reply Off Topic (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: determination of size of conductor/cable

05/31/2010 8:20 PM

Instead, try (a+b)(a-b) = a2-b2.

Or (a+b)(a+b) = a2+2ab+b2.

Or (a-b)(a-b) = a2-2ab+b2.

Your formula mixes up everything,

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Determination of Size of Conductor/Cable

06/01/2010 3:52 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: Determination of Size of Conductor/Cable

08/21/2010 11:42 AM

Your question is not clear.If you have a wire and if you want to know its size(cross section) you should measure the diameter,type(solid/flexible/stranded),material(copper/aluminium and properties)size of strands(if multi stranded) and refer tables provided by any reputed manufacturer.Calculating may not give accurate results.

__________________
pnaban
Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (1); jaimeloza (1); pnaban (1); PWSlack (1); redfred (1); Tornado (1)

Previous in Forum: Current Density of Electrolytic Aluminum Flats   Next in Forum: Substation Lightning Protection

Advertisement