Anonymous Poster

Changes Required in Switchgear When Load Increased

06/04/2010 5:05 PM

Could anyone please help me on my below question?

We need to replace the motor of 160KW with 260KW, currently the CTs connected are of rating is 400/1 Amps. Should it be remain same or replacement is required? and anyother changes required in switchgear?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Changes Required in Switchgear When Load Increased

06/04/2010 5:41 PM

need to determine the full load amps of the motor. What is the voltage?

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Changes Required in Switchgear When Load Increased

06/04/2010 7:50 PM

Casual investigation says that unless the voltage is over 500, you will need to change them.

Not enough information.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Changes Required in Switchgear When Load Increased

06/04/2010 10:43 PM

Clearly there is not enough information here. I would expect that at these enormous electric motor ratings of 200 and 350 horse power motors respectively, that this kind of a job is beyond the scope of your training. I say this because this is not a minor power change. Whatever power distribution capability your previous motor had, it will most likely not be capable of providing this power. Either the voltage or the current handling capability of the wiring, disconnects, fusing, contactor and maybe even transformer feeds will have to be changed. If you knew what these changes were, you'd know if this CT could handle the job without it being upgraded too. Talk to your electrician or contractor about this CT.

Maybe your quest for more power is because your 200 hp motor is under fed already. Wouldn't be the first time that somebody trying to be frugal, didn't get all the power they thought they should get.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Anonymous Poster
#4

Re: Changes Required in Switchgear When Load Increased

06/04/2010 11:09 PM

Since you didnt provide enough information, i suggest you replace now the new motor and run it. Once your new motor starts, you will come to know what are the changes are required.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Changes Required in Switchgear When Load Increased

06/04/2010 11:36 PM

You might have to upsize any or all of the following:

1. CT ratio to about 600:1.

2. Ammeter dial plate to match the new ratio.

3. Wiring to the motor.

4. Circuit breaker to the motor.

5. Motor starter one or two frame sizes up.

6. Main breaker and bus bars in the switchgear.

7. Transformer that feeds this system.

8. Primary wiring from the grid to the transformer.

9. Various similar items in the grid (for instance if it is rural and/or marginal).

If some of these things have already been designed to account for future expansion, there may be fewer needed changes. Someone should survey all of this in light of these factors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#6
In reply to #5

Re: Changes Required in Switchgear When Load Increased

06/05/2010 6:59 AM

10. The generator in the power house. that is the first thing to replace.

Reply
Anonymous Poster
#7
In reply to #5

Re: Changes Required in Switchgear When Load Increased

06/05/2010 2:29 PM

Thanks Sir.

Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#8

Re: Changes Required in Switchgear When Load Increased

06/07/2010 4:16 AM

Not nearly enough info. Unless your previous motor had vastly oversized switchgear, everything from the motor cables to the master CB's and perhaps even the transformer may have to be upgraded.

__________________
Always learning
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Changes Required in Switchgear When Load Increased

06/07/2010 5:06 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#10

Re: Changes Required in Switchgear When Load Increased

06/07/2010 11:05 AM

Of the various replies to your question, the one from Tornado on 06/04/2010 11:36 PM (reply # 5); is the most accurate and highlights the extent of the issues that are involved. HOWEVER, I would strongly suggest that a registered professional engineer in electrical POWER engineering (with a current license in your state) look into your problem and recommend possible solutions. Replacing a motor with a larger HP motor is a non-trivial exercise. Power (voltage, amperage, and power frequency) are only the starting point. Motor load, type / kind of motor starter, wiring to the motor, (as outlined by Tornado) all play into possible solutions. In addition, electric power costs SHOULD also be considered, since motor changes can also change your electric energy costs. FYI: You pay for kVA not kW, so changes in motors could also change your power factor (kVAR) and trigger power factor penalties on your electric bill. An electric POWER engineer should be able to look at all of these issues for your installation and determine the 'true cost' of the motor change. Todd Jones, P.E. A Registered Professional Engineer

Reply
Anonymous Poster
#11

Re: Changes Required in Switchgear When Load Increased

06/08/2010 2:25 AM

In addition to above, i missed to say, voltage licence from other states will be enough.

NB:- I am not Tornado.

Reply