Anonymous Poster

Per Unit Impedance of Transformer

06/11/2010 12:12 AM

Sir Please Tell me that what is per unit impedance & if we want to make parallel operation of following trf then what is per unit impedance & how we can calculate please tell me im very confused for this.

1)132/33 KV , 40/50 MVA trf & 16/20 MVA trf.

2) 132/33 KV ,16/20 MVA trf. & 14/20 MVA trf.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Per Unit Impedence of transformer.

06/11/2010 10:06 PM

Please study the name plate of the transformer. Per unit impedance or percentage impedance would definitely be mentioned on the transformer name plate. It is a very importnat parameter for any transformer. Please note the same and come back, we will discuss further.

Reply
Anonymous Poster
#2
In reply to #1

Re: Per Unit Impedence of transformer.

06/12/2010 3:31 AM

impedance is 6%.

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Per Unit Impedence of transformer.

06/13/2010 10:05 PM

For the transformer, the Per Unit Impedance (%) = Percentage Impedance Voltage = Percentage Impedance (%Z). As already mentioned, it must be mentioned in the transformer name plate data.

See also http://cr4.globalspec.com/thread/41265

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: Per Unit Impedence of transformer.

06/15/2010 3:10 AM

It implies that when you load the transformer to its rated capacity, the Voltage Drop in the transformer secondary windings would be 6% of its no-load secondary voltage, when rated primary voltage is applied to the primary.

It also implies that with the secondary short-ciruited, if you apply 6% of the primary volatge , full-load rated current would flow in the secondary.

Conversely, it gives the short-circuit current supply capability of the transformer for a three phase terminal short circuit on the secondary windings (i.e.) Short circuit current = Transformer Rated Seconadry Full load current / Per unit impedance of the transformer.

Reply