have built a panel for a rotory pea drum that runs on hydraulics the motor runs the tank pump the motor is 10hp 7.5kw have put it on a single contactor with a 13amp to 19.5 amp overload the breaker is 25amp 3pole. Now getting to the point, the motor is wired up in star
as soon as it starts it stalls after 2 seconds tried in delta but because of the start load it trips breaker.
HELP.
Re: PlugPass Electrical Services, PAT Testing, Electician
06/13/2010 12:38 PM
install a valve at delivery side. before start the motor close the valve 90% then start the motor when motor reached its rpm i.e., motor connection shifted to delta slowly open the valve.
06/19/2010 3:55 PM
Thanks Folks for your replys to my email found that the motor was stalling because who ever put the motor in the pump had accidently
knocked the internal pump so it was sitting on the base of the tank and giving the motor a lot of work to start. Refitted new motor and pump and all is well
Thanks all kindly Peter T
yours truly Peter T
Good Answers: 97
06/13/2010 1:40 PM
Is the "Tank pump" motor the source (prime mover) for the hydraulics?
By "single contactor" do you mean a DOL (direct on line) method of control?
What is the stator connection (star or delta) for this motor at design voltage?
Is the breaker motor rated (thermal-magnetic, inverse time delay) to withstand inrush current?
Is the power supply sufficient to tolerate inrush current?
CRTL-Z
Good Answers: 18
06/14/2010 6:11 AM
Did you include a bypass valve in your hydraulic circuit design? The pump pressure will stall the motor until the drum reaches speed without one.
06/15/2010 2:27 AM
do the megggering for the Motor, cable, etc..... before starting... check the starting current in each phase, if they are all in phase then you have to increase the changeover time for star-delta starter and check........
06/15/2010 3:27 AM
What is the supply voltage?