DG Set with 0.95 Power Factor

06/22/2010 4:27 AM

Can i asked for a DG set with 0.95 power factor

Register to Reply
Pathfinder Tags: united
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: DG Set with 0.95 Power Factor

06/22/2010 7:58 AM

Yes! Very much! But ensure that the Engine is suitbaly sized for the HP.

Register to Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: DG Set with 0.95 Power Factor

06/22/2010 3:42 PM

The power factor is determined by the nature of the loads, not by that of the generator. The PF specification on a genset tells what conditions it can handle, not what it produces.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 2)