Increasing Voltage

07/05/2010 2:50 PM

In one of my projects, voltage between earth and neutral is 0.01volt. When the load is given (ie when lights are in ON position), the voltage between earth and neutral is gradually increasing up to about 25-30volts. Kindly inform me what will be the reasons.

The other case is when neutral from the Main Supply and Residential Earthing is checked by continuity of the Multimeter, it shows some beep sound. It seems to be interconnected. What is the reason? Please inform my problems.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Contractor

07/05/2010 3:23 PM

Given your comments (and the words "contractor" and "project"), I would strongly advise leaving this work to a qualified electrician as you don't seem to understand the basics of the applicable electrical codes and bonded MEN (Multiple Earth Neutral) (or similar, as it varies from country to country) systems which are designed to have the earth and neutral connected at specific points for electrical safety.

Please bear in mind that if this is for a project or job, then your employer (and possibly you too) could be liable for any illegal works, property damage, loss of life (including yours!), etc if an untrained individual such as yourself tries to perform said electrical installation and/or testing.

Can you please provide more information on why you are asking this question (including your country as electrical standards, codes and systems vary from country to country). Alternatively this question has been answered previously on CR4 before (sorry I don't have the link).

__________________
jack of all trades
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #1

Re: Contractor

07/05/2010 10:18 PM

A very Good Answer Jack. Accurate and very diplomatic.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#2

Re: Contractor

07/05/2010 3:23 PM

From what I can understand your check of the earth/neutral bond with a "visual" beep is indicating continuity for a very small amount of current (the multimeter) where in reality there is a faulty earth/neutral bond.

__________________
CRTL-Z
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Contractor

07/05/2010 3:40 PM

In simple terms the continuity test feature of a multimeter injects a small amount of current and gives a corresponding single tone to indicate if there is a low resistance present.

A continuity test alone is not a conclusive test for testing a Neutral-Earth bond as it requires no other voltage potentials or flowing current to be present (which can effect the reading).

The fact the Neutral and Earth are bonded together leads me to believe the installation is likely MEN type (or similar) where the Neutral and Earth are intended to be bonded together at the switchboard (a system that is common throughout many parts of the world including New Zealand), however without knowing what country the installation is in this is purely an educated guess until the original poster provides more information.

__________________
jack of all trades
Register to Reply Off Topic (Score 4)
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#4
In reply to #3

Re: Contractor

07/05/2010 4:36 PM

I am in complete agreement with your recommendations and was trying to convey the principles of a multimeter continuity test (although I have not heard of a "visual" beep) and the misapplication.

My efforts to "dumb down" my reply has backfired, as your reply to me indicates.

Had I seen your post before I submitted mine I wouldn't have bothered posting.

__________________
CRTL-Z
Register to Reply Off Topic (Score 4)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5
In reply to #4

Re: Contractor

07/05/2010 5:44 PM

I thought that may have been the case half-way through writing my response but posted anyway as I thought the extra information may be of benefit for the original poster (especially the second paragraph).

__________________
jack of all trades
Register to Reply Off Topic (Score 4)
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#8
In reply to #3

Re: Contractor

07/06/2010 6:30 AM

Hi Jack off all trades,

I am in Auckland, Office in East Tamaki, I would like to catch up with you some time.

Cheers

Joe

Register to Reply Off Topic (Score 5)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9
In reply to #8

Re: Contractor

07/06/2010 3:14 PM

I am in Auckland, Office in East Tamaki

It is such a small world, so am I!

I would like to catch up with you some time

Sounds like a good plan, we can trade contact details via CR4's private message system.

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Increasing Voltage

07/06/2010 4:22 AM

The voltage between neutral and earth at any instand is a function of conductor size, distance from the supply location and the vector sum of the currents in the three (usually) phase conductors feeding other loads elewhere. Its actual value at any place at any moment is irrelevant.

Earth is there to operate the circuit protective device(s) in the event of a fault.

Please read the Wikipedia article on earthing systems.

If in doubt, consult a qualified electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #7

Re: Increasing Voltage

07/07/2010 5:44 AM

In fact, for this OP, the voltage he is checking (N to Earth) is function to the earth resistance. he is probably checking the earth at a connection point linked to the earth rod(or whatever...) and a neutral wire.

He is having some earth leaks and does not have a proper ELCB on the line or he has a mixed wiring problem whereby a grounding wire has been used as a neutral in his circuit...therefore, any load on the Live Ground will increase the voltage drop and he is checking that voltage drop. This is what I think is happening.... not enough info to guess more than that considering his lack of knowledge in the subject he will be lost unless a course and circuit drawings are involved..?

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

jack of all trades (4); Joe Sparky (1); LAA_Lucke (1); PWSlack (1); redfred (1); Unredundant (2)