Power Factor and Induction Motor

07/07/2010 5:37 AM

if the power factor of the utility is low ,is it effect the performance of the induction motor ? What does means by the P.F mentioned on the nameplate of the motor. Is it constant or changes with load?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Power Factor and Induction Motor

07/07/2010 7:51 AM

i do not believe that there is a "utility power factor". You just get a voltage at your incomer. When you put loads on it - motors, lights, furnaces, etc, that decides your plant power factor. If it is too low, the utility may ask you to put some capacitors to improve it. In some areas, there may be penalties for low pf. The motor, once you connect it and start, will run at its inherent designed pf, nothing external will affect it. However, depending on the voltage and the load on it, pf will vary slightly. For more details, you can check out this thread:http://cr4.globalspec.com/thread/56346#newcomments

kind courtesy - msamad.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Associate

Join Date: May 2010
Posts: 31
Good Answers: 3
#2
In reply to #1

Re: Power Factor and Induction Motor

07/07/2010 11:09 AM

You are right. The graph shows the relation with respect to voltage variation. What my question is that

Yesterday our PFC was not working. Its shows the power factor 0.72 instead of 0.95. Now in that scenario this P.F 0.72 have what kind of influence on the performance of the induction motors in the area?

This Low P.F 0.72 does affect the P.F of the motor or not? Let a motor of 4 KW, 400 V, 50 Hz, 7.8A, P.F 0.87, 2850 RPM. Does its P.F (0.87) remain same or will change?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Power Factor and Induction Motor

07/07/2010 11:19 AM

Look at it this way ... the incoming voltage applied to the motor is seeing the impedance of the motor only, nothing else. So, the motor will draw whatever current it needs to deliver the mechanical power it is asked to deliver. If you measure only the motor's pf, it will be close to what the nameplate says. The plant pf is another story. It will take ALL your loads including the motor, and the meter will show that.

You seem to have some high-inductance loads..maybe an induction furnace? You wouldn't need a PFC otherwise. If it is not working, you may need to manually cut in some capacitors while watching the pf meter.

Please rest assured that the motor is unaffected. Even if you shut down everything else, it will work as usual

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: Power Factor and Induction Motor

07/07/2010 2:13 PM

Sort form;

The motor affects the plant power factor, but the plant power factor does not affect the motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".