Alternators

07/11/2010 10:57 AM

Can two alternators of unequal capacity be run in parallel ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#1

Re: Alternators

07/11/2010 11:18 AM

yes, the following conditions should be taken in consideration for paralleling 2 or more

1- RMS line voltages must be equal
2- The generator to be paralled must have the same phase sequence. If the phase sequence is different, then even though one pair of voltages is in phase the other two pairs of voltages are 120 degree out of phase. If the generators were connected in this manner there would be no problem with phase a but huge currents would flow in phases b and c damaging both machines.
3- Generator output phase angles must be the same
4- The oncoming generator must have a slightly higher operating frequency as compared to the system frequency. This is done so that the phase angles of the incoming machine will change slowly with respect to the phase angles of the running system.

Reasons for operating in parallel
1- handling larger loads
2- maintenance can be done without power disruption
3- Increasing system reliablility
4- Increased efficiency

Register to Reply Good Answer (Score 2)
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#4
In reply to #1

Re: Alternators

07/12/2010 2:12 AM

Hi All

In addition to Mr Hameedullah Ekhlas Comments -

Two unqual rating of the Alternators / Gensets can be synchronised easily.

Synchronising has two parts -

1. Paralleling the Gensets

2. Load Sharing

Paralleling has been beautifully explained by Mr Hameedullah Ekhlas.

Loas Sharing - Thumb Rule - the Load on the genset should be equal % of their Ratings. e.g if you have 2 Gensets of 1000 kw , 750 kW & the Load is 1400 KW, Means your Requirement is 80 % of the total Generating Capacity, Hence both the Gensets should be loaded to 80 % of their Capacity viz - 800 kW & 600 kw respectively.

Thanks

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5
In reply to #1

Re: Alternators

07/12/2010 2:52 AM

GA for a good answer.

The only thing that I would add is that "doing it wrong" can throw one or both alternators out of the building. Someone could get hurt, you REALLY have to know what you are doing.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Member

Join Date: Jul 2010
Posts: 9
#8
In reply to #1

Re: Alternators

07/15/2010 10:15 AM

Thank u sir ... it is a good answer :)

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Alternators

07/11/2010 3:12 PM

Possibly, it depends on the application and size of the alternators. Can you please provide more information, is this for car alternators on a 12V DC common bus within a vehicle or something else?

__________________
jack of all trades
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Alternators

07/11/2010 7:12 PM

You can run them parallel only if you are able to synchronize them. But there are some conditions for generators (or other utility power) to synchronize. See the thread http://cr4.globalspec.com/thread/43318 for detail of the conditions.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Alternators

07/12/2010 3:31 AM

Yes, provided steps are taken to ensure that voltage and phase angle criteria are met.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: Alternators

07/12/2010 4:32 AM

Parallelling of 2 Genset has been explained by others...

Your question: Unequal capacities? Yes they can be paralleled but you must have a Load sharing Capability (usually standard nowadays with the parallelling panels). this load sharing operation must be done by a qualified person who knows the equipment being used. It consists of adjusting what is called the DROOP on each governor so the load is shared according to each generator's capacity. Ex: if A = 1000KVA and B = 500KVA, and the load is 1000KVA, then A will share 2/3 of 1000 = 666.66 while B will share 333.33 making the total of 1000 kVA.

The setting of the sharing process differes a little from one make to the other but the principle is the same. You Must Know What You Are Doing (Capital for warning not shouting!). Otherwise, One genset might take more load than its fair share (Proportional to its capacity) and be overloaded ... tripping or else.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Hameedullah Ekhlas (1); jack of all trades (1); LAA_Lucke (1); msamad (1); Partho Bhowmick (1); PWSlack (1); vishram lele (1)

Previous in Forum: Transformer Rating   Next in Forum: Generator Bus Duct

Advertisement