How do i restore a s7-400 siemen plc to run state. the run led blink about 3 times and stop.
Good Answers: 29
Re: plc
07/12/2010 9:53 AM
Consult your operation manual. Look for a section detailing error codes.
Re: plc
07/12/2010 9:55 AM
....or telephone Siemens directly for assistance.
Re: PLC
07/12/2010 10:57 PM
check for some errors in your program, as experienced, there are conflicting blocks added in your program, or some short circuit from your inputs/outputs.
Re: PLC
07/13/2010 5:26 AM
Have you made any modifications to the PLC code or the wiring? Is there a ProfiBus or ASi bus connectd?
Re: PLC
07/13/2010 10:03 AM
No modification made, the entire plant was shutdown for maintanance two weeks ago only for the Plc not running when restarted. There is a profiBus connected.
Re: PLC
07/13/2010 5:42 PM
Hello, if your machine was running properly prior to the shut down then it is very likely that you have lost the program. If you have S7 software then you can go online and look for the error codes and correct. if you do not have the software then you will have to contact the machine manufacturer. In any case check and or replace the battery.
Good Luck!
repeat problems can not be solved by the same way of thinking ( A. Einstein)
Re: PLC
07/13/2010 8:10 PM
i agree with dthomas16, this happens when your CPU is at fault (at the very rare occasion) or the memory card. try replacing the CPU and download the back-up program (if you have ) and when the fault still exist, then the problem lies within your inputs/output i.e sensors, vfd's etc.
Re: PLC
07/14/2010 2:31 AM
Do you have the ability to go online? It is, as others said, possibly a case of the battery not maintaining the program. However this would only be the case if you do not have an EEPROM/ memory card installed.
Re: PLC
07/23/2010 10:43 AM
Reset it properly less chance of problem with main program. follow guidelines plc trouble shooting.