Use of IS Barrier for Intrinsically Safe Instruments

07/13/2010 2:55 AM

I am using Instrically safe feild equipment of Zone 1 IIA/IIB T6 for a lube oil refinary. Do I still need IS barriers in PLC panels?

Please refer me any litrature ilustrating use of IS Barriers.

Register to Reply
Pathfinder Tags: IS Barrier
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#1

Re: Use of IS Barrier for Intrinsically Safe Instruments

07/13/2010 7:10 AM

Yes.

The barrier prevents electrical faults in the safe area from getting into the hazardous area.

Barrier absolutely required. Yes. Yes.

Register to Reply
Anonymous Poster
#2

Re: Use of IS Barrier for Intrinsically Safe Instruments

07/13/2010 10:37 AM

Our friend Iris is correct, one need to protect IS barrier although fieild instruments are of selected based on particular Group / Zone. For instance the instruments are usually powered through 24V DC supply but what about load. For any unforeseen reason if any mishap occurs then how sure that this load is insufficient to get a spark or flame or static charging. More over, you stated that it is a lube oil refinery hence safe design first.

We see very poor practice of people using ATEX field instruments but the most danger zone which is neglected is the control panel and it's lead wires in and out of control panel.

Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#3
In reply to #2

Re: Use of IS Barrier for Intrinsically Safe Instruments

07/13/2010 1:05 PM

The factory supplied wiring diagrams for hazardous areas are very explicit about barrier or isolator protection.

Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#4

Re: Use of IS Barrier for Intrinsically Safe Instruments

07/13/2010 11:16 PM

You need not think at all about this point.

Just follow, whatever is specified in ATEX / FM certificate. There, you will find that the certificate not only asks for using external barrier, but also will specify the entity parameters of the barrier to be used.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Use of IS Barrier for Intrinsically Safe Instruments

07/14/2010 4:28 AM

Intrinsic safety is a method of protection where the voltage and current levels in the hazardous area are too low for an incendive spark capable of igniting a potentially explosive atmosphere to occur.

Therefore some method of preventing higher voltage/current levels from outside the hazardous area getting into the hazardous area is required.

The PLC is outside the hazardous area and the instrument is inside the hazardous area.

Therfore a barrier device is needed between the PLC and the field instrument, and the instrument manufacturer's instructions may even state the parameters of the barrier that is required.

Is the selected interconnecting cable correct?

DO NOT SELECT, INSTALL OR TEST HAZARDOUS AREA EQUIPMENT WITHOUT HAVING RECEIVED AN APPROPRIATE LEVEL OF TRAINING!

Risk of

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#6

Re: Use of IS Barrier for Intrinsically Safe Instruments

07/14/2010 11:50 AM

Intrinsically safe field equipment is only approved for use in Zone 1 environments when used with approved intrinsically safe barriers (ISBs).

As others in this forum have stated, the device itself can not garuntee that current through the conductors would be limited in the event of a short circuit or damage to the device, thus all conductors that feed IS devices must be completely isolated from non-IS wiring (even within panels) and supplied by ISBs.

ISBs do not have to be located in the PLC panel; they can be located anywhere you want to put them, if you follow the installation guidelines correctly.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!