Anonymous Poster

Electrical & Instrumentation

07/23/2010 1:10 PM

Hi Gents.

I real need your help we want to connect some motors with power factor correction banks

1st motor has 500 Kw, 3.3 KV, 106 Amps

2nd motor has 280Kw,3.3 Kv, 60.9 Amps

3rd motor has 250 Kw, 3.3 Kv, 56.7 Amps

Please advice which capacitor size and type I must use on this different size of loads.

Thank you,

Lazaro.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Electrical & Instrumentation

07/23/2010 1:24 PM

This is what qualified electrical engineers get paid to do...

So either you are an unqualified electrical engineer or you are saying you don't want to pay for the service, you want someone to do it for free. Good luck with that.

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Electrical & Instrumentation

07/23/2010 7:44 PM

There are many threads available related to this topic in CR4. You can search and look into them. Here are some of them that I can remember:

http://cr4.globalspec.com/thread/54230

http://cr4.globalspec.com/thread/53560

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Anonymous Poster
#3

Re: Electrical & Instrumentation

07/23/2010 8:44 PM

Search for available resource in this forum i bet you will get it.

Reply
Commentator

Join Date: Aug 2009
Posts: 91
#4

Re: Electrical & Instrumentation

07/24/2010 5:01 AM

It is not just calculation for reactive power

1 Configuration of system

2 desired power factor calculation you can see schenider or GE ABB lit

3 proper selection according to temp harmonics protection -----

you can also use some power system sw to simulate the condition

__________________
Correct me if i am wrong i am learner
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Electrical & Instrumentation

07/25/2010 3:12 PM

Call a capacitor bank manufacturer/supplier to visit your site and study the set up.If necessary ask him to connect a digital power analyser which can record variation of I,V,pf,VAr,W.VA harmonics etc during the day and record these parameters and he will recommend a capacitor bank,filter,surge protector etc to you. Installing for individual motors may not be economical.

__________________
pnaban
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Electrical & Instrumentation

07/26/2010 3:01 AM

Yep. Get suppliers to do the work on the prospect of sales. Nothing wrong with that!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); ikhanuk (1); msamad (1); pnaban (1); PWSlack (1)

Previous in Forum: Generate Eectricity From Heat   Next in Forum: 3 Phase Overload Setting

Advertisement