3 Phase Overload Setting

07/23/2010 8:46 PM

We have a 3 phase 3 Kw 415v motor, FLC 5.7 amps, locked rotor 9 amps. When motor is running under load it draws 2,5 amps per phase should the overload be set at 7.5 amps.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: 3 phase overload setting

07/23/2010 9:52 PM

If the overload relay is built per

(a) IEC standard, the maximum allowable setting is not more than the motor FLC.

(b) NEC standard, the maximum allowable setting is not more than the motor 1.15 x FLC.

Your motor FLC is 5.7A, but it is drawing only 2.5A. So, it is freely allowed to keep the setting up to 5.7A. Even for NEC, there is no possibility of nuisance trip.

7.5A overload setting is much higher for this motor.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: 3 Phase Overload Setting

07/24/2010 1:04 AM

I think the nature of your question is, do you add the currents of the 3 phases? The answer is no. When we speak of current, we are referring to current in each phase only; there is no cumulative issue involved.

So as said, you set the OL to the motor nameplate FLC; 5.7A in your case. What it actually draws is irrelevant, the OL is a protection device to prevent damage from excessive current under abnormal conditions.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: 3 Phase Overload Setting

12/28/2025 5:51 AM

<...should...be set at 7.5 amps...>

Why?

If the <...overload...> were set at <...5.7 amps...> then the motor would be correctly protected.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

JRaef (1); msamad (1); PWSlack (1)

Previous in Forum: Electrical & Instrumentation   Next in Forum: Software for electrical design for buidings

Advertisement