Electrical Device Rating Question

07/27/2010 11:37 PM

Why the electric devices are rated to 230V even though our voltage supply is 240V (415/1.732) ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#1

Re: 230V

07/27/2010 11:41 PM

I too have the same doubt because it is said that 10% rise in voltage reduce life of a bulb to half of its actual duration.

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: 230V

07/27/2010 11:52 PM

Our voltage is rated at 240V with + 15% due to our voltage frequency from 50 to 55 hz.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: 230V

07/27/2010 11:59 PM

On a 240v network, there will typically be some voltage drop from the service through the wiring to the motor, which will then receive ~230v, and is rated accordingly.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Electrical Device Rating Question

07/28/2010 2:04 AM

In any distribution network, the voltage will rise and fall within a tolerance band. As far as any particular device is concerned, 230V and 240V are in the same tolerance band, so the absolute rating of the device doesn't matter; it won't blow up if the voltage now is 230.0001V!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#5

Re: Electrical Device Rating Question

07/28/2010 4:39 AM

Most electrical equipment can operate satisfactorily within a range of supply voltages, usually wider than plus or minus five percent about its nominal utilization voltage. But the fact that equipment will fuction over a particalur range of voltage does not mean that it will function well at the extreme ends of that range.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: Electrical Device Rating Question

07/28/2010 5:16 AM

A transformer's name plate voltage is 433V (i.e.) it is its open circuit voltage. But, when you load the transformer to its rated capacity, there will be some voltage drop inside the transformer (in the transformer secondary windings). Now, you will get only around 415V at the transformer terminals itself. Add to this, the voltage drop in the cables from the transformer to the distribution boards and from the distribution boards to the loads (under rated load conditions). The single phase voltage would not go beyond 230V under normal circumstances. That's why single phase equipments/devices are rated at 230V.