Motor Overloading

08/04/2010 9:38 PM

Hi all,

Somebody told me that a DC motor (linear actuator) will never have overloading condition, thus overloading protection (or breaker) is not required. Only AC motor will have overloading protection. Is this true?

Can any help to explain a little the difference between AC and DC motor in terms of overloading senario, and overloading protection?

Thsnk in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#1

Re: Motor Overloading

08/05/2010 2:02 AM

No.

Any motor can be overloaded. It all depends on the design of the motor and motor driver and how well it was designed for a particular application.

A linear actuator delivering peanuts will work fine until an elephant climbs aboard, then problems start occurring. e.g. too much mass.

__________________
Charlie don't surf.
Register to Reply
Associate

Join Date: Dec 2006
Location: Doha Qatar
Posts: 43
#2

Re: Motor Overloading

08/05/2010 2:05 AM

dats right

any motor can be heated or overloaded if u dont monitor ur input voltage and ur load ie maximum current it should drwa at full load

__________________
Please save the power for Next Generation- Do ur bit
Register to Reply Score 1 for Off Topic
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: Motor Overloading

08/05/2010 2:21 AM

That is rubbish.

Motors, either DC or AC can have and will have an overloading condition due to increase of load, during voltage drop due to faults in the control system, faults in the distribution line, efficiency of the motor decrease, aging of the motor copper winding coil, faults in the load that the DC motor is connected and e.t.c.

Whether it is an AC motor or a DC motor it required some forms of protection relays such as overload relay, Fuse protection, over current protection and breakers.

For example:

In most of the rolling mills, especially for steel mills, AC and DC motors are used especially for the rolling rollers. DC motor is used due to the constant speed and constant torque are needed and it is a one of the most importance parameters in the rolling section.

During rolling of the billets down size from 120mm to 5mm size, with smooth rolling, the current for the DC motor are at the normal running operating current. But if the rollers miss rolled and the steel bar stuck inside the rollers, the DC current will increase up to a point where the Inverter will trip the DC motor as to protect the DC motor overheated.

Any motors either AC or DC will have an overloading and the overloading will cause motors to be overheated due to excessive of the current passing thru the motor coil winding. Heat will generate due to the magnetic flux in the core.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Motor Overloading

08/05/2010 2:23 AM

<...That is rubbish....>

Beware the disapproving Guest!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Motor Overloading

08/05/2010 2:36 AM

There are various types of motors, such as torque motors, that can be stalled without overloading. This includes AC for sure, and I would guess that there are DC types that would also work.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#10
In reply to #5

Re: Motor Overloading

08/06/2010 5:05 AM

I was thinking at the same type of motor. A torque motor used to strech paper in a printing machine.

This type of motor has a very high resistance and a good cooling. It will warm up, but not as high that is will burn.

So no overload is possible.

I have seen a similar application in an automatic door close system. There were no limit switches to stop the motor, it just applied a certain torque to hold the door closed.

Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 12
#6

Re: Motor Overloading

08/05/2010 6:23 AM

ha.. thsnk guys !

i had been debating this ( i said we need some overloading protection on the motors in our design ), but my boss said that DC motors do need that protection coz it will never happen.

Debated for 1 hr.... he still insists... ha ~

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7
In reply to #6

Re: Motor Overloading

08/05/2010 10:27 PM

If you are still having problems convincing your boss (protection IS necessary for this type of DC motor by the way) you could actually prove it to him with an example using a linear actuator, a power supply and an ammeter.

Sometimes it takes something visual and hands-on to prove a valid point that if ignored can potentially cause a lot of grief and expense further on down the track.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8
In reply to #6

Re: Motor Overloading

08/06/2010 12:35 AM

then your boss is a fool.... in charge and out of touch!

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#9
In reply to #6

Re: Motor Overloading

08/06/2010 4:36 AM

Normally, a dc motor is supplied and controlled from a dc inverter. Within this unit there is a current limiting setting to be adjusted by the user. Also, there are fuses etc.

Therefore, maybe your boss is referring to this fact (without knowing exactly...?) and therefore he could be right in saying that you do not need an extra protection device downstream from the dc inverter driving the dc motor. the protection will be before the dc driving board to protect against failure of this board. Don't forget that the board has a bridge rectifier (controlled with SCRs) and if these fail, then a short circuit will appear on the supply to the board (there should be some fuses inside the board, but a set of fuses should also protect the supply...).

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#11

Re: Motor Overloading

08/06/2010 8:09 AM

There is more than one way to protect a motor or other load based on limiting the input. The problem becomes one of controlling the amount of damage you are willing to incur. If your power supply or source is only capable of delivering the voltage and current that matches the specifications of the motor then you will reduce the possibility of an overload, but the motor performance will suffer.

Putting all of your faith on the motor manufacturer or the installer or the application may be acceptable for a quick test, but it would be foolish for the long term.

If you perform a "failure mode & effects analysis" (FMEA) you can start to see what I am talking about. Consider the locked rotor current at full voltage. Because there is no rotation in a locked rotor, there is no cooling. Consequently the heat will build up until insulation starts to melt. Shortly after that you will have short circuits between the loops of wire and it will just get hotter, faster. Then you will draw all the current the supply can deliver to the new lower impedance circuit. At this point, you are definitely in an overload condition.

Or some DC motors use brushes rubbing against commutators and they slowly turn into conductive dust covering all parts of the guts of the motor. Most of the time that is not a big problem. But consider the brave electrician who has no concept of safety and installs the motor while the electricity is still on. One little slip and he has a disaster in front of him.

In short, you should consider the effects of a dead short inside the motor. If you think that never happens, you should talk to one of the many firms that re-wind motors as their business.

The point is this: If you are prepared for a disaster, then you can mitigate the consequences. Otherwise a component failure inside the motor will propagate toward the power source until something burns up and stops the disaster. So, how much burning are you willing to tolerate? After all, most equipment runs until something fails, and an open circuit is not always the failure mode.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Score 1 for Good Answer
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#12
In reply to #11

Re: Motor Overloading

08/06/2010 9:00 AM

It's good to point out the possibility of a direct short in the motor, but that is not the same as an over load condition. The OP did not specifically say that the motor is not to have any type of current limiting devices such as fuses, which would act in the case of shorted windings.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#13
In reply to #12

Re: Motor Overloading

08/06/2010 10:04 AM

The term "overload" is a very general description of what can happen. But if the motor is expensive I would definitely want something to intervene in case there was a condition where the mechanical load (connected to the rotor) suddenly seized up. Chains or belts can break or even get hung up in the machinery causing the motor to stall. When that happens, it causes an overload condition.

I don't think I have ever seen a motor that costs less than the chain or belt to connect it to some other device. Consequently, I would choose to protect the expensive stuff first. I would also want to prevent damage to the wiring because that kind of damage can escalate very quickly.

Try not to fall into the trap of assuming that the motor has been properly sized for the job to be performed. It is an expensive and potentially dangerous set of conditions where the motor is so oversized that can not stall.

That being said, there are other forms of protection such as a clutch or shear pin but as an electrical engineer I admit to being biased on using good design techniques rather than relying on some mechanical device to cover my butt.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#14

Re: Motor Overloading

08/06/2010 12:42 PM

For the novice motor overload protector like myself?

What would constitute a 'level' of protection?

fuses?.. resettable fuses? circuitry? thermal cut off switch? PLC?

____________________________________

..for the linear actuator.. I assume this must be an argument on whether or not to provide this in the design for an OEM product rather than to add protection to a single unit.

A boss that believes he's right when he's not? ...unheard of

__________________
High Tolerance is Beautiful
Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 12
#15

Re: Motor Overloading

08/10/2010 1:58 AM

thsnk a lot guys !

appreaciate advices from all of u ~

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

brich (1); EElectrician (1); jack of all trades (1); JE in Chicago (1); LAA_Lucke (1); msmir116 (1); NotUrOrdinaryJoe (2); PWSlack (1); rudy.leurs (1); Simon Wan (1); skygon (2); stevem (1); Tornado (1)