CV Calculations for Emergency Shutdown Valve

08/17/2010 12:55 AM

Do we really have to carry out Cv calculations for Emergency shutdown valves ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: CV Calculations for Emergency Shutdown Valve

08/17/2010 3:25 AM

For any on/off valve, the Cv calculation is not usually necessary. Of what use is it (rhetorical question)?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member Hobbies - CNC - New Member

Join Date: Aug 2006
Location: Western Australia
Posts: 767
Good Answers: 58
#2

Re: CV Calculations for Emergency Shutdown Valve

08/17/2010 4:38 AM

You would want to know the Cv of valves in order to know the pressure drop across them. This affects the economics of your valve choice - that is, what is acceptable to the process against the cost of the valve.

The Cv and the Gain (delta flow/delta valve travel) and the closing time can be very important factors in determining the suitability of emergency shutdown valves in process systems. For example, will tripping of the Emergency valve shut the system down faster than the anti surge valves on the compressor recycle can open resulting in serious surge of say an axial compressor.

So to answer your question - probably yes, but maybe not.