TN-C-S in Need of Earth?

08/18/2010 1:12 PM

Hi,

I currently live abroad in Thailand and I am told the system here is TN-C-S which means afaik that the Earth is bonded to the Neutral. Now when I look in my fuse box, they have earth wires, but they have also linked the Neutral to the Earth actually in the fuse box itself.

I am sure this is unsafe, and there is NO RCD/RCCB protecting the system. The incoming power is 3 phase into a switch and the box is done by Square D. There is a "test" button on the switch (model EZD100H). But since no neutral runs through it, I am sure it is not of a 30mA RCD but just a MCB like switch.

Please can someone confirm for me, that this should have a seperate earthing system and that binding the Neutral and Earth inside the Box is wrong.

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: TN-C-S in Need of Earth?

08/18/2010 7:31 PM

If you were using the "NEC as your code reference, you would be required to have the neutral and the grounding electrode conductor bonded in the main panel at the first over current device just as you have at your location. If you are required to have a GFI(ground fault indicator) it is necessary that the phase conductor and the neutral pass thru the GFI for it to operate properly. Check this link for you information.

http://hyperphysics.phy-astr.gsu.edu/hbase/electric/gfi.html

Register to Reply Score 1 for Good Answer
Participant

Join Date: Aug 2010
Posts: 4
#2
In reply to #1

Re: TN-C-S in Need of Earth?

08/18/2010 10:36 PM

OK, so from what you say- GFI is what we would call an RCD or RCCB.

But what would be the consequences if any, if you separated the N and E in the consumer box without a GFI type device?

I can only see it being safer by having it separate anyway.

All input is welcome.

Thank you for your comment.

TB

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: TN-C-S in Need of Earth?

08/19/2010 5:04 AM

<...But what would be the consequences if any, if you separated the N and E in the consumer box without a GFI type device?...>

The E must to be bonded to the N upstream of the GFI/RCD/RCCB and not downstream of it, otherwise the device won't operate in the event of a fault thereby placing the user at greater risk during the fault event.

If in doubt, consult a qualified electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Aug 2010
Posts: 4
#5
In reply to #4

Re: TN-C-S in Need of Earth?

08/19/2010 7:27 AM

If there is NO GFI type device, then removing the link that is in the box between the N and E would have what effect?

I plan to install a 4pole RCD (as it is 3 phase + neutral) so that the whole system would be safe.

I don't want the Ground and Neutral connected at all, because I was never taught that this was a good thing.

So what I plan is -

Earth Rod 2m deep, direct to Consumer unit. Remove link between N and E which is in the consumer unit. Move the 3phase +N to go direct into a 4pole 30mA RCD then back into the Consumer Unit. There are just the 4 wires in, so the N must connected to the E before I get a chance to even split it afterwards.

Does this sound ok?

Thanks for the responses so far.

TB

Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#3

Re: TN-C-S in Need of Earth?

08/19/2010 2:34 AM

I think what you have is what we call MEN System (multiple earth neutral) this system is used in most countries around the world and has proved its self to be most reliable. RC-D's (residual current devices) are a relatively new player on the market, I suppose here in New Zealand they have to be installed in new installations for the past 10 years or so. But i don't think that there has been are requirement to upgrade existing installations unless work is done within the sw bd or a new appliance outlet is installed.

I am sure that what you have is the MEN system and it has not been upgraded, and i would expect that in Thailand. It is still a reasonably safe system, the only reason that we have RC-D's now is that the technology is available and they don't cost a fortune for a bit more additional safety.

Register to Reply
Participant

Join Date: Aug 2010
Posts: 4
#6
In reply to #3

Re: TN-C-S in Need of Earth?

08/19/2010 10:08 AM

How would I know if it was a MEN system?

The house is about 5 years old. I know they are way behind modern electrics here but it was supposedly built by a German Thai company, using quality electrics. Looking at them now, I somehow believe they didn't have much of an idea of what they are doing. The Consumer box is made up from all the colours of the rainbow in cable form....

White, Black, Red, Blue and green. Really weird to look at a system like that, but that is how they do it here. Atrocious.

TB

Register to Reply
Register to Reply 6 comments