Motor Connection

08/27/2010 12:57 PM

Hi friends, suppose i have a motor which has no tag on wire ends, how can i make it proper delta connection when i dont know the starting end or ending end of each winding, plz give me optionns

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Motor Connection

08/27/2010 1:32 PM

You might not be able to do this. If you know that you have a three phase induction motor, then you can make a reasonable assumption from ohmmeter measurements which wires are for which coil. But if you actually have a synchronous motor, a stepping motor, a DC servo motor or a universal motor then you may not be capable of wiring this motor in a delta configuration.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Motor Connection

08/27/2010 1:33 PM

Why did you post this in feedback? Were you looking to get feedback?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Associate

Join Date: Dec 2006
Location: Doha Qatar
Posts: 43
#3

Re: Motor Connection

08/27/2010 1:54 PM

if u have 6 ends of 3 widings you can identify with the help of multimeter by measuring resistance

__________________
Please save the power for Next Generation- Do ur bit
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Motor Connection

08/27/2010 2:33 PM

The ohmmeter gets you part of the way there, but you also need to determine that the windings are wired in the same direction. (Or more yet, which ones are in series or in parallel with each other in the case of a dual-voltage motor.) I think there are some battery-and-magnet tricks for this, but I don't recall them.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Feb 2009
Location: TORONTO, CANADA
Posts: 134
#5

Re: Motor Connection

08/28/2010 12:34 AM

Depends on the number of leads you have coming out. Three leads no problem hook them up and see what the rotation is. six leads (double delta or star delta) the phase of the leads is important and a little hard to figure). 9 leads (dual voltage with some leads terminated in the motor) 12 leads (dual voltage all leads for all windings out--facilitates star delta starting). Some times if it is not a large motor or a critacle appilcation you may just hook it up and "let-er fly" wrong phasing will show.

Unfortunatly it is difficult to determim which "hand"
the winding is wound on which determines the phasing of the winding. ie: CW or CCW.

__________________
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
Register to Reply
Commentator

Join Date: Jul 2010
Location: North West Province, South Africa
Posts: 67
Good Answers: 18
#6

Re: Motor Connection

08/28/2010 3:43 AM

Hi Ammarkhan,

I have been faced with this problem before with a 3 phase 380vac squirel cage motor where I received the motor back from the winders with just the six wires coming out and I had to fit the terminal block. You can solve the problem in a couple of easy steps.

1. Identify the three seperate windings with the aid of your multi-meter on the ohms range.

2. Once you have identified the windings mark the tails of each winding as follows :- winding 1 - U1 & U2 winding 2 - V1 & V2 winding 3 - W1 & W2

3. Now connect the three windings in series i.e. wire U2 to wire V1 and wire V2 to W1.

4. Connect a single phase supply (220vac) to the windings i.e. Live to wire U1 and Neutral to wire W2.

5. Switch on the single phase power to the windings and with your multi-meter measure the volt drop across the following U1 & U2, V1 & V2, W1 & W2. You will be able to see that two windings have the same volt drop and the third is different. Reverse the connections of the winding with the different reading and re-test. All three windings should now have the same volt drop.

6. Switch off the 220v power and now re-mark the coil ends from the start of the series connection you have made as U1 start & U1 finish, V1 start & V1 finish, W1 start & W1 finish.

7. Now first disconnect the three coils and then connect the windings as follows :-

U1 finish connect to V1 start

V1 finish connect to W1 start

W1 finish connect to U1 start

The windings are now connected in Delta

8. With your multi-meter on ohms check the resistance between each of the three wires marked start (U1 to V1, U1 to W1 & V1 to W1). The resistance read should be equal.

9. You are now ready to run the motor by connecting your three phase supply to U1 start, V1 start & W1 start.

10. Check the current on each of the three supply lines to the motor - they should be equal. If they aren't there is a problem and you need to recheck.

I hope this helps you out of your predicament.

__________________
A little knowledge that acts is worth infinitely more than much knowledge which is idle! Khalil Gibran
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #6

Re: Motor Connection

08/28/2010 1:59 PM

Now that's a cute technique. GA, and welcome to CR4.

I take it that the two like-directional windings induce a different voltage in the "backward" one, as shown in the voltage drop readings.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: May 2006
Posts: 142
Good Answers: 3
#7

Re: Motor Connection

08/28/2010 9:28 AM

Why not do what I do, call the manufacturer, seems that they all have techs with a cad screen in front of them.

Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

CONWAYMECH (1); Keith Grewar (1); MIKE L. (1); msmir116 (1); redfred (2); Tornado (2)

Previous in Forum: Yet Another Rating Scheme   Next in Forum: Looking for Pre-Set Timed Vibrator

Advertisement