Previous in Forum: Np2 Automatic Controller For Emergency And Standby Power System   Next in Forum: Forced Guide Contact Relays
Fault Level
09/01/2010 3:19 AM
how to calculate fault level of alternator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member Popular Science - Genetics - New Member Technical Fields - Technical Writing - New Member Safety - ESD - New Member Engineering Fields - Power Engineering - New Member
Re: Fault Level
09/01/2010 4:29 AM
based on the Xd'', Xd' and Xd of the generator
Correct Me If Iam Wrong, Suggestions/Recommendations needs to be verified before implementation
Re: Fault Level
09/01/2010 4:40 AM
Please can you give the formula of same?
Re: Fault Level
09/01/2010 5:18 AM
Epressions for SC are;
I" = E/X"d, Where X"d is the apparant reactance of the stator winding just at the instant of SC (during the first few cycles, it causes heavy current to flow)and E is the phase voltage.
I' = E/X'd, Where X'd is the transient reactance which takes into account the armature and leakage reactance.
I' = E/Xd, Where Xd is synchronous reactance (used primarily for relay settings)
Knowledge sharing is a WIN-WIN situation
Good Answers: 170
Re: Fault Level
09/01/2010 9:43 AM
If I can modify a bit:
I"k = E"/X"d
I'k = E'/X'd
Ik = E/Xd
Not to ignore the time constants, T"d & T'd
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member
Re: Fault Level
09/05/2010 1:53 AM
Fault level of alternator (in MVA) =
Capacity(in MVA) of alternator / Sub-transient impedance (Xd") of alternator
nvmani