Anonymous Poster

5HP Motor Starter

09/01/2010 9:55 AM

I have a 5HP water submersible pump. It keeps burning cause I do not have enough protection for the motor. I would like to get a good circuit diagram for a motor starter with detailed protective devices. Any idea of a location or site that has such circuit diagram and device specifications?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
5
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: 5hp motor starter.

09/01/2010 10:05 AM

I would start with the manufacturer's web site. If you Google the manufacturer's name and model number I suspect that you will get a lot of useful information. They'll be able to tell you what starter circuitry you should have and any over current protection you should have. They will also be able to tell you what the maximum size of debris the impeller can handle so you will know what screen size should be used.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 5)
Anonymous Poster
#3
In reply to #1

Re: 5hp motor starter.

09/01/2010 3:20 PM

Is it the right way to get 2 GA marks is to get rid of my question by transferring me to Google,i need direct clear answer sir.

Reply
Active Contributor

Join Date: Aug 2010
Posts: 17
#4
In reply to #3

Re: 5hp motor starter.

09/01/2010 3:46 PM

I believer that Mr.redfred should give back your money.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #4

Re: 5hp motor starter.

09/01/2010 3:57 PM

If he brings me the receipt, I'll refund him double the amount I charged.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
4
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #3

Re: 5hp motor starter.

09/01/2010 3:55 PM

If you really want a direct clear answer then you have to give us direct clear information. I will not play 20 questions with you. I only know a few pieces of information to possibly help you, you have a 5hp motor (not enormous but not tiny either), this is a submersible pump (probably water but anything from yogurt to petroleum to god knows what it could be in) and that how you are using this pump it burns up often. I do know that you think that your problem is the starter wiring, but I don't know how you've wired it. I don't even know if you have an electric motor. You might have an electric start 5hp Briggs and Stratton motor here. Now had you provided some additional information, I might have helped you further, but not now.

Good Bye

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 4)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #5

Re: 5hp motor starter.

09/01/2010 8:47 PM

20 questions? Is that all? I think you are grossly underestimating the possibilities here.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster
#20
In reply to #5

Re: 5hp motor starter.

09/02/2010 5:57 PM

I with you! If he has to ask for the kind of details his is asking, there is a real danger to him self and others. He may need the yellow pages under electricians instead! - JHF

Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#9
In reply to #3

Re: 5hp motor starter.

09/01/2010 11:10 PM

Guest-

In order to get "i need direct clear answer sir." one must provide sufficient information within one's question. Google is often a good place to begin one's search for information, but definitely not the source of unquestionable perfect answers. For example, give me the numerical answer for "y" in the equation x2 -y + r = 0. Impossible to find the numerical value for "y" since not enough information is given in the question. An answer can only be as good as the question! Lousy question results in lousy answer!

Also, don't forget that you get what you pay for.

Also, how can you judge the accuracy of answers obtained from a forum open to anybody? That answer could kill you if you think it is correct and it really isn't. (not referencing anyone who has submitted a reply to the original question).

If you want a better answer than what you are paying for, find a mechanical/electrical engineer with much experience in the installation/use/troubleshooting of pumps who you trust and pay him to solve your problem. Be prepared to either give him much more information or to pay him to obtain that information so he can accurately solve your problem.

Incidentally, I have that experience but I am now retired. That means I charge a lot of USA dollars and require a very large travel expense account. Don't bother contacting me.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #9

Re: 5hp motor starter.

09/02/2010 1:18 AM

Have gun; will travel.

$10,000 minimum.

Wire Paladin, San Francisco.

Fax 415-555-1212

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13
In reply to #11

Re: 5hp motor starter.

09/02/2010 1:58 AM

You having an end of season sale?

You've dropped your price!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #3

Re: 5hp motor starter.

09/02/2010 5:20 AM

It was free of charge!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
2
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 5HP Motor Starter

09/01/2010 2:05 PM

This may be the type of submersible pump that actually requires submersion in order to cool the motor. If so, you need a level control switch that shuts off the pump when the water level is too low. This is in addition to a motor overload cutout, which is needed if the pump bogs down on stringy material.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #2

Re: 5HP Motor Starter

09/01/2010 9:14 PM

Quite likely. In India, there are usually two more situations requiring protection :

1. Dry run - no water, so no cooling. Electronic relays are available to stop the motor in such a situation.

2. Restart after momentary power outage - when power fails, the tall water column spins the pump shaft in the opposite direction. If power comes on now, the shaft can shear. This is prevented by a timer which prevents the motor being restarted until all the water has had time to drain away.

If the OP is in India, there are special pump controller manufacturers who include all these.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#17
In reply to #8

Re: 5HP Motor Starter

09/02/2010 8:16 AM

GA from me.

Normally, submersible pumps are fitted with a non return valve at their outlet.

To protect the submersible pump against dry running:

1) Use a Flow switch/Timer/Low Pressure Combination device which has a small pressure vessel incorporated. These are widely available nowadays. They have an electronic circuit with flow detection, a timer set at 15sec and a low pressure switching. Add the Overload and a phase failure if 3 phase motor.

2) If the flow switch combination device is not available or you cannot get a suitable sized one, then Install a pressure vessel + Pressure Switch + Flow switch (Honneywell...) in series on your pipe work coming out of the well. Add a timer set 10-15 sec in the panel. Wire the main switch + Phase failure Relay + Overload in series, then Flow switch N.O. & Pressure switch (Closing on pressure dropping below ~ 1 bar) & Timer (N.C. to open after delay) in parallel, then the control relay/motor contactor. The timer coil wired strait after the overload contact (above) and before the 3 parallel contacts.

3) Understand the circuit: P.Sw will open when pressure > 1bar (or minimum required pressure). T opens after 10-15s. F.Sw closes if water is flowing and remains as long as there is a flow. When flow stops, the F.Sw drops open and [C] releases, stopping the pump. The pressure in the vessel will initiate a flow next time there is a water demand....

It all depends on how you want to use the pump etc

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#22
In reply to #17

Re: 5HP Motor Starter

09/27/2010 12:17 AM

Very interesting.Can you give a circuit incorporating a lockout contactor with reset button to prevent chattering of contactor/starter?.Such a problem was encountered in Saudi when contactor and timer were used instead of a PCB.

__________________
pnaban
Reply
Member

Join Date: Jul 2010
Posts: 7
#19
In reply to #8

Re: 5HP Motor Starter

09/02/2010 12:11 PM

Also can use level electrode for dry run protection

Reply
Associate

Join Date: Jun 2008
Location: India,Pune
Posts: 46
Good Answers: 1
#10

Re: 5HP Motor Starter

09/02/2010 12:57 AM

Sir,

There are two protections you can use.

1) over current relay. to be installed on to your contactor.

2) One Single phasing prevention device by Minilec (An Indian co) They can give you a starter with all these facility)

3) In series You may put one more sensor for no flow condition for water on air vessel .

kiran nawathe

__________________
if you are a managment professional or youth who wants to start business contact for free help for your project including financial assistance through NGO in and around Pune India
Reply
Active Contributor

Join Date: Aug 2010
Posts: 13
#12

Re: 5HP Motor Starter

09/02/2010 1:30 AM

Normally a thermal overload relay will be sufficient for protecting motor from overload caused problems.

For submersible pumps it is absolutely essential to provide run dry protection (a simple form of float switch), as the fluid that is getting pumped flows through outside the winding casing to provide cooling to copper windings.

Basically the fluid level of a submersible pump cannot be allowed to drop below 2/3 of it's height (or even 3/4 by some manufacturers) Google FLYGT submersible pumps, their website is a minefield of information.

Cheers

Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#14

Re: 5HP Motor Starter

09/02/2010 4:05 AM

When I worked in Agricultural engineering department 3 decades ago in India I faced similar type of problems. Some of of causes of failure of submersible pump are dry run,Over heating of motor,Improper connection of cable from motor-pump to control panel,Voltage fluctuations,mal functioning of starter and safety devices. You have to check one by by one and take remedial measures to avoid failures in future.

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#15

Re: 5HP Motor Starter

09/02/2010 4:28 AM

In India, here is a link to a comprehensive pump-motor protection relay, mainly targeted at the agricultural market. Conditions in the remote areas being : Low voltage, single phasing, occasional phase interchange by utility personnel when repairing lines which are down, frequent power outage, dry run, overload due to clogging....

Please check this out : minilec SPG D2

Usual disclaimer.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#18

Re: 5HP Motor Starter

09/02/2010 9:23 AM

Good submersible pump controllers can be obtained from Franklin Electric. Check out the Pump-Tec Plus for single or three phase I am not sure of the motor manufacturer of your pump. The Franklin controls work on the Franklin motor. If you are using Chinese or Grundfos motors, the Franklin controls still may work but check first before purchasing. The Pump-tec retails at about $350.00.

The Pump-Tec controls many conditions; voltage fluctuations (generators), dry and auto restart, thermal overload, clogged pumps, etc. They even indicate why the pump was shut down for diagnostic evaluations.motors. They work very well (*) with minimal problems. We have installed such controls on landfill site application pumps and they have operated for >10 years. The pumps referred in the above are applicable to 4 inch submersible pumps for water.

Submersible sump pumps have a large variety of options including; float control, ultrasonic, proximity etc. Call your manufacturer for best recommendations for your situation.

__________________
If they want holy water, tell them to boil the hell out of it.
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#21

Re: 5HP Motor Starter

09/26/2010 7:56 AM

For submersible pumps the following protections are required: 1)over current/over load 2)short circuit 3)winding temp alarm/trip 4)dry running protection(low water level) 5)no flow protection 6)Under voltage/Over voltage/phase reversal/single phasing/phase reversal- protection 7)Cooling media around motor stator(oil/water) You should also check cable size, voltage drop, contacts in starter, chattering etc If the rating of the pump is small it may not be economical to employ all the above. If you are not competent enough to trace the cause contact manufacturer or an engineer experienced in the relevant field

__________________
pnaban
Reply
Reply to Forum Thread 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); JRaef (1); kevinm (1); kirannawathe (1); kvsridhar (2); LAA_Lucke (1); mrswamy (1); mwadym (1); old salt (1); pnaban (2); PWSlack (1); redfred (3); Sabeet123 (1); TonyS (1); Tornado (2); wheel (1)

Previous in Forum: Capacitor Bank Protection   Next in Forum: Improving High Voltage Op Amp's Slew Rate

Advertisement