Cooling Tower

09/02/2010 8:00 AM

Dear Sir,

The cooling tower was selected / sized base on the following data

1) water entering temperature is 36 degree C

2) water leaving temperature is 31 degree C

3) ambient wet bulb temperature is 28 degree C

4) water circulating is 417 m3/hr

My question is what will happen to water leaving temperature if the ambient wet bulb temperature is 26 degree C and the value of water leaving temperature & water circulating is maintained.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Jun 2006
Location: Central America
Posts: 227
Good Answers: 1
#1

Re: Cooling Tower

09/02/2010 8:28 AM

The cooling capacity increases.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#2
In reply to #1

Re: Cooling Tower

09/02/2010 9:48 AM

... as long as the word "...and the value of water leaving temperature & water circulating is maintained." is a typographical error.

__________________
Semper Ubi Sub Ubi
Register to Reply
Power-User

Join Date: Jun 2006
Location: Central America
Posts: 227
Good Answers: 1
#3
In reply to #2

Re: Cooling Tower

09/02/2010 10:04 AM

Agreed. Outlet water (water leaving) temperature can´t be maintained, it will be lower depending on ambient wet bulb temperature. .

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #3

Re: Cooling Tower

09/02/2010 1:48 PM

Quite.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jan 2009
Posts: 18
#4

Re: Cooling Tower

09/02/2010 10:36 AM

Sorry, the question is what will happen to water leaving temperature if the ambient wet bulb temperature is 26 degree C and the value of water entering & water circulating is maintained.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: Cooling Tower

09/02/2010 1:49 PM

Eh?

The water leaving temperature is a function of the wet bulb temperature. So response #1 et. seq. is correct.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Aug 2010
Location: UAE
Posts: 50
#9
In reply to #4

Re: Cooling Tower

09/03/2010 3:05 AM

it most like to lower 1 or 2 degree. Does when you want to maintain a water leaving temperature of 28C then your cooling capacity will increase, assuming other factors are the same.

Register to Reply
Commentator

Join Date: Aug 2010
Location: Austin, TX
Posts: 80
Good Answers: 8
#6

Re: Cooling Tower

09/02/2010 1:49 PM

Does your tower have a variable speed fan on it?

Does your Condenser water system have a variable position bypass valve?

__________________
Some standards are like the North Pole and some are like Mecca. People use both to get their sense of direction, however, only one is a preferred destination. - P.E. Scheibmeir
Register to Reply
2
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#8

Re: Cooling Tower

09/03/2010 12:50 AM

As indicated in Post 1, your cooling capacity will LIKELY increase. It will attempt to follow the approach (31C vs 28C) but- as the WB of the air falls, the capacity of the machine to follow that apparent higher cooling capacity will fall off- there is only so much "work" that a basic design can support. You did not provide the entering DB of the air at the rating point, but it is likely very near 36C. Using the WB value of your post, it is very likely that the leaving water will be very close to 29C (maintaining the 3C approach) assuming that the DB of the air is also about 2C cooler DB- 34C.

Also- as the WB falls, the total amount of cooling that can be done by the tower- even if the entering temperature of the water is also falling- will be reduced because the amount of evaporated water that the air can "hold" will also fall as the air temperature falls.

It takes less water per kg of air to reach saturation when the entering air is 25C DB or WB than when the air is 31C DB , and even less yet when the air is 15C DB than when it is 25C DB. Since the evaporation of water is what provides the cooling effect, less available evaporation means less cooling capacity.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10

Re: Cooling Tower

12/26/2010 12:11 PM

Dear bwchoo,

The Water leaving the Cooling Tower will be more cool on account of Drop in the Wet-Bulb Temp is changing from 28 Deg.C to 26 Deg.C

The air at 26 Deg.C Wet-Bulb temp has more capacity to absorb heat from the hot water than air lat 28 Deg.C Wet-Bulb Temp.

Hence air will absorb more hveat/vapour to get saturated, in this process about 0.56 K.Cal of Heat/Kg. of air passing through the Cooling Tower will be absorbed theoritically from the Hot Water, resulting in further cooliing of water.

Total heat transfer taking place will be Weight of air/Hr. x 0.56 = Weight of Water circulated/Hr.x T(out) and we can find out theoritical drop in outlet water.

Thanks,

DHAYANANDHAN.S,

CR4 MEMBER.

Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

bwchoo (1); coffeebean (2); dhayanandhan (1); Doorman (1); energygod (1); erlo (1); MrGeneRall (1); PWSlack (2)

Previous in Forum: Butterfly Valve   Next in Forum: Mech Seal Failure

Advertisement