Hi...
Can u please tell me how to select cables for pressure/level/magnetic/ultrasonic transmitters,control valves,shutdown valves.
Re: Selection Of Cables
09/21/2010 7:47 AM
Try to be more "specific" about the condition , it will help us to reply and you to understand as well.
Cable selection depends upon various things e.g., Length, type of control, temperature or environmental conditions, voltage grade,etc. etc,
“Reality leaves a lot to the imagination.”
Good Answers: 29
09/21/2010 8:45 AM
Cable selection depends on the xmtr tied to each particular device, the voltage or amperage of the signal, the distance, etc. The exception is the ultrasonic devices. These will need to be transmitted through coax cable with the proper impedence specified by the Mfr. As said above, more info please.
Good Answers: 176
09/21/2010 9:01 AM
FYI,
Siemens (formerly Milltronics ultrasonics) switched from coax to twisted pair for its ultrasonic level transducer-to-electronics box extension cabling about 3-4 years ago. A factory guy told me there had been significant improvements in the electronics to where signal-to-noise increased to the point where coax wasn't needed. I believe the transducers are still manufactured with a coax pigtail lead, but using TP for extended cabling is acceptable.
The Siemens Clamp-on ultrasonic flow transducers still use coax.
09/21/2010 11:10 AM
Application? -
  • Hazardous area or not?
  • Which industry?
  • Location - building interior? Inland plant? Offshore installation? Ship? Aircraft?
  • Direct buried or clipped to tray or run in conduit?
  • Indoors or out?
  • Low-smoke-and-fume?
  • Bending radius restrictions?
  • Etc.
10/12/2010 6:35 AM
Instrument Circuit Type
Circuit Example
Field Instrument To Junction Box
Field Junction Box To Marshaling Cabinet
24 VDC or less Discrete signals Solenoids, Alarms, Switches, Relays, limit switched, Secondary Motor Control 16 AWG, 300 V PLTC/ITC, single twisted pair or triad cable
ARMORED:
16 AWG, 300 V SWA, PLTC/ITC, twisted single pair or triad cable
18 AWG, 300 V PLTC/ITC Twisted, Multi-Pairs or Triads, Overall Shield
Analog Signals Frequency, Pulse, or Transmitter Digital Communication 4-20 mA DC, RTDs, Weigh Cells
Speed, Vibration, Turbine Meter, Smart digital Transmitter
16 AWG, 300 V PLTC/ITC, single twisted, shielded pair or triad cable
ARMORED:
16 AWG,300 V SWA, PLTC/ITC single twisted, shielded pair or triad cable
18 AWG, 300 V PLTC/ITC Twisted, Individually Shielded Multi-Pairs or Triads
Thermocouple Measurement Thermocouples 16 AWG, 300 V PLTC/ITC, single twisted, shielded, thermocouple extension pair cable
ARMORED:
16 AWG, 300 V PLTC/ITC, SWA, single twisted, shielded, thermocouple extension pair cable
18 AWG, 300 V PLTC/ITC, Twisted, Individually Shielded, thermocouple extension multi-pair cable
Data Links EIA-422A Data Links, High Speed Communication networks Follow System Manufacturer's Recommendation Follow System Manufacturer's Recommendation