We are having 440V 32Amps ,3 Phase Welding machine , which is having R Y B phase supply, Currents in R,Y,B , Phases are32A,16A,16A,.Can i use ELCB for these welding machine.
Good Answers: 181
Re: "is it Possible to use ELCB for three phase Welding machine"
09/24/2010 1:44 AM
A 3 or 4 pole RCCD (ELCB) will work fine.
I'd recommend it given the abuse most welding sets receive.
09/24/2010 2:29 AM
How does it, Plz give connection diagram
01/22/2021 5:08 AM
<...Plz give connection diagram...>
That description comes on the instruction leaflet supplied with it.
If in doubt, consult a locally qualified Electrician.
09/24/2010 2:52 AM
ITS A PERFECT SOLUTION FOR A SAFE ELECTRICAL OPERATION OF WELDING SETS AND ONLY THING YOU HAVE TO SELECT THE MAX ALLOWABLE LEAKAGE CURRENT PERMISSIBLE.
TO MY KNOWLEDGE FOR A HEALTHY EQUIPMENT CONNECTED TO A DEDICATED 32AMPS TPN 415VOLT WELDING SET 63mA CURRENT IS OK.
IN FACT THIS PRACTICE IS FOLLOWED IN REFINERIES WORLDWIDE FOR GIVING POWER SUPPLY TO WELDING MACHINES.
PRIODICALLY U HAVE TO CHECK THE HEALTHINESS OF THIS ELCB IN EVERYMONTH AS A SAFE/STANDARD ELECTRICAL ENGINEERING PRACTICE.
S BHATTACHARYA
Good Answers: 181
09/24/2010 4:18 AM
STOP SHOUTING!
TURN CAPS LOCK OFF
Good Answers: 804
01/26/2021 1:26 PM
Rest In Peace Tony S...
09/27/2010 1:21 AM
Shhhhhhhhhhhhhhhhhhhhhhhhhhhhhh!
Re: Is it Possible to Use ELCB for Three Phase Welding Machine?
09/25/2010 12:06 AM
You must use long delay CBs due to the heavy start surges in welding machines of the transformer type. Otherwise you will have nuisance tripping.
A 75 Amp 3 phase incoming supply would have been better for your machine.
09/26/2010 4:38 PM
Yes you can use an ELCB we run them on all our welders, use motor start or d curve breakers this deals with incidental tripping due to high inrush current when starting the weld.
09/27/2010 9:26 AM
Yes this is a compulsory statutory requirement to have welding on EL Protection for fire requirements (300mA)