Induction Motor On No Load

09/24/2010 3:27 AM

What will happen if an induction motor drawing water from a tank is emptied and motor still runs? will it burn?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Induction motor on no load

09/24/2010 3:31 AM

It shouldn't bother the motor, but there may be unbalanced or shock loads to the pump impeller and shaft when it starts drawing a mixture of liquid and air (or vapor).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Induction Motor On No Load

09/24/2010 7:37 AM

The motor doesn't draw water from a tank. The motor provides power to a pump, which draws water from a tank.

Depending on the type of pump, the seals may be damaged.

I haven't read the FAQ's lately. Is there a requirement there that original posts be only one sentence long and provide no useful information?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Induction Motor On No Load

09/24/2010 10:50 AM

Yes there is. Rule #75. Didn't you get the update?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Induction Motor On No Load

09/24/2010 11:24 AM

That seems to be the only rule religiously adhered to by every new poster we see.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#5

Re: Induction Motor On No Load

09/24/2010 11:33 AM

As far as just the induction motor only, the motor will continue to draw the same amount of current. The phase angle of this current will significantly change because the motor will no longer be doing significant mechanical work. As far as burning up the motor, it depends on how the motor gets cooled. If the drawn water was the primary cooling agent (a submersible pump) and there are no thermal cutoffs in the design then prolonged dry pumping can burn up a motor. A good engineer will anticipate likely scenarios and prevent a cascade of failures from happening.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Associate

Join Date: Sep 2010
Location: East Coast
Posts: 49
Good Answers: 1
#6
In reply to #5

Re: Induction Motor On No Load

09/24/2010 12:08 PM

Wont the motor draw less current if it slips less due to no load? Thanks.

__________________
Never use a superalitve when a diminutive would suffice
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#7
In reply to #6

Re: Induction Motor On No Load

09/24/2010 1:13 PM

There will be a slight reduction in the current draw, but not as much as most people think. Many people think of a motor in DC operation. Baldor has a nice white paper on induction motors. From that paper the actual and equivalent circuit diagram.

The variable resistance in (b) increases as one approaches zero slip. What most people focus on is this curve from the same paper.

Particularly the curve to the left and that there's a steep drop in current as one approaches synchronous speed. But there are always additional drags on a motor from internal and external bearings and wind-age that are always mechanically present. So unless the motor has a prime mover driving the shaft to overcome these drags, rarely does a free spinning motor reach the corner of these curves to get the sharp drop in current.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Member

Join Date: Sep 2010
Posts: 7
#12
In reply to #7

Re: Induction Motor On No Load

09/25/2010 1:32 AM

That is an excellent coverage on the motor part of the system. But the reply to the question comes from analysis of the motor & the load, the load in this case being a pump.

There are a number of cases of motor burnout due to long duration dry running. When the pump is dry,

  • initial period (15 mins to 45 min depending on various factors related to type of pump & quality of water) the water lubricated parts are still lubricated & the motor runs on 'no-load' with a very slight reduction in current & a low power factor.
  • in the next period, the water lubrication effects vanish & the parts such as seals or glands start getting overheated and get damaged. In this phase apart from the damage to the pump components, the motor faces progressively increasing load as a result of increasing friction and at the same time reduced cooling if its cooling system is related to the water pumped - as in submersible pumps. This invariably leads to the motor damage due to overheating.
  • The increase in friction in pump can be enormous and very fast if the water being pumped has sand content in it. This happens mostly in tube well submersible pumps.
  • Sand or some or the other solid material is always there in most of the pump installations. As such it is always desirable to build in a protection to avoid dry running of a pump, even though the motor technically may not be heading for a a damage by itself.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #6

Re: Induction Motor On No Load

09/24/2010 2:19 PM

No, current INCREASES with slip, so if it slips less, it draws less current.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#9
In reply to #8

Re: Induction Motor On No Load

09/24/2010 3:12 PM

Yep, my mental lysdexia is showing again.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10

Re: Induction Motor On No Load

09/24/2010 3:37 PM

Due to bearing friction, windage, possible cooliing fan losses, and reactive power at light loads, the "no-load" current can be about 30% of full-load current.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#11

Re: Induction Motor On No Load

09/25/2010 12:12 AM

Basically the question is meaningless. To many unknown parameters.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#13

Re: Induction Motor On No Load

09/25/2010 8:25 AM

Simple answer:

If the motor-Pump is left to run dry for a long enough time, the pump seals will fail, the cooling by the water of the seal area will fail due to the remaining water getting hot and steaming, ---> possible motor shaft seasing and heat transfer to the motor casing if directly coupled with a flange fitting... definitely the motor will eventually burn out for these reasons.

Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#14

Re: Induction Motor On No Load

09/25/2010 12:35 PM

The question leaves many unknowns.

From experience I have noticed the following with centrifugal or fan type pumps:

1) The AC current drops off partially as the discharge stops. No work is being done. However the magnetizing current is still present. Smaller fractional HP motors appear to have a larger % no load current.

2) A submersible pump needs to be submersed for cooling. If it is not submersed it over heats due to lack of cooling.

3) Without water the seals in the pump rapidly dry out and over heat and are damaged. (Even the ceramic ones. The faces are OK but the rubber seal behind gets cooked.)

4) I had one example of a blocked outlet and the pump was left running overnight. It was a 1 HP pump (not submersible). It boiled the water in the pump chamber under about 30 psi pressure. Unfortunately the plumbing was plastic and things started to melt and eventually the plastic pipe at the pump swelled and burst. (That ended the heating effect!)

Register to Reply
Anonymous Poster
#15

Re: Induction Motor On No Load

09/25/2010 9:33 PM

Suction cavitation

Suction cavitation occurs when the pump suction is under a low-pressure/high-vacuum condition where the liquid turns into a vapor at the eye of the pump impeller. This vapor is carried over to the discharge side of the pump, where it no longer sees vacuum and is compressed back into a liquid by the discharge pressure. This imploding action occurs violently and attacks the face of the impeller. An impeller that has been operating under a suction cavitation condition can have large chunks of material removed from its face or very small bits of material removed, causing the impeller to look spongelike. Both cases will cause premature failure of the pump, often due to bearing failure. Suction cavitation is often identified by a sound like gravel or marbles in the pump casing.

When the Bearings fail, motor will draw heavy current and burn itself.

For more information go to Wikepedia and type Cavitation. There is wealth of information to learn.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#16

Re: Induction Motor On No Load

09/26/2010 7:04 AM

wouldn't it be great if the OP of ANY question included ALL the important facts so the question could be answered WITHOUT trying to guess the important points and exactly what it is the OP is trying to find.

Would the motor burn?

Whats missing here?

__________________
The square root of nothing is what you make it!
Register to Reply
Member

Join Date: Sep 2010
Posts: 7
#17

Re: Induction Motor On No Load

09/26/2010 11:53 PM

For more clarification i can say that motor is sub merged nad there is no separate pump is there. There is only a suction - Discharge type of arrangement with motor. Sorry for late reply !!!!!

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#18
In reply to #17

Re: Induction Motor On No Load

09/27/2010 12:02 AM

This will require a new rule. Rule #75 does not cover totally useless and misleading information.

I think this statement, " i can say that motor is sub merged nad there is no separate pump" demands a new rule.

I suggest, "ignorance is bliss" be the name of the latest rule.

That should make the OP happy, if not ecstatic.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#19

Re: Induction Motor On No Load

09/27/2010 12:09 AM

Well, that more or less destroys my earlier reply. I work mostly with nonsubmersible pumps, and my reply matched those. As several others have pointed out, running out of liquid will soon burn out a typical submersible pump motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20

Re: Induction Motor On No Load

09/27/2010 1:20 AM

The motor won't burn if it has an overload protection device installed and the device is set to the motor's full load current as stated on its rating plate. If the tank is empty, though, the current will drop as the motor is no longer doing any work.

The pump impeller and the seals might suffer, though.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#21
In reply to #20

Re: Induction Motor On No Load

09/27/2010 2:20 AM

If it is a self protected motor, one that has O/L protection that senses the actual motor temperature then it has a chance. External O/L's that only sense line current will not protect the motor from cooling loss. This is true for both submersible and separately ventilated motors (or self ventilated with blocked cooling openings). No matter what, if you remove the cooling, external O/L protection is useless.

(I am an advocate of industrial motors wound with RTD temperature feedback!)

Register to Reply
Member

Join Date: Jun 2010
Posts: 7
#22

Re: Induction Motor On No Load

09/27/2010 9:34 AM

Commonly in submersible pumps they are designed to work at certain load against the water pressure and running freely in air it is working over and above its design load which is known as pump cavitation which will cause the pump to cavitate in other words cause damage to controls and instrumentation.

Ronald Naidoo

Electrical Engineer

Register to Reply Score 2 for Off Topic
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#23
In reply to #22

Re: Induction Motor On No Load

09/27/2010 10:55 AM

Running freely in air it cannot cavitate!

Register to Reply
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#24
In reply to #22

Re: Induction Motor On No Load

09/27/2010 12:22 PM

Gentlemen

Yet another master class in submersible pumps.

first, ESP's (electrical submersible pumps) of any type and design rely on the fluid they are pumping to keep the motor cool by the velocity of the fluid passing over the outside of said motor.. The velocity is determined by the lift (not suction)(centrifugal pumps CANNOT suck) of the pump and the diameter of the well casing. A motor/pump with a OD of 5.4inch would be placed into a well casing of no more than 7inch, any bigger then a shroud would be used (another lesson).

How do we know that the motor is being kept cool (no therocouples installed).. by the rate of flow at surface and the motor running current (RC).

The motor MUST be protected not only with a overload, but an UNDERLOAD trip as well.

The purpose of the underload trip to to prevent the motor from running while not lifting fluid to surface. Any drop in the RC depictes a drop in fluid production and drop in velocity of fluid over the motor and a reduction in cooling.

Now you might say.. well if the motor is not working hard (idling) then its NOT going to get hot. WRONG!

If you say that then you've never seen a ESP motor. A submersible motor has no fan and no fins to increase the surface area, and you've never put your hand on a surface motor while running... Even under a low load a surface motor kicks out a huge amount of heat.

So cavitation.. forget it.. way to complex and answer for this OP.... seals burning out.. Na... damage to impellers..yes can happen! Thats called downthrust!! (another lesson)

but if you have no load you want to STOP the motor before you cause damage.. hence the underload.

Typically the U/L is set at 80% of RC and the O/L at 115% of RC. Any less than 80% then you might be setting the U/L at idle amps for the motor then you will not protect your motor, pump and cable.

so to recap.. low RC means low or no fluid production, means low or no cooling of the motor. The result I am sure you all can work out

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#25
In reply to #24

Re: Induction Motor On No Load

09/27/2010 1:00 PM

GA

Nicely done.

I would only add "centrifugal pumps don't suck much". If they CANNOT suck at all, how does the water enter the impeller?

One more thing; If the application is a sewage lift station tank (again, MORE INFORMATION FROM THE OP WOULD HAVE BEEN NICE), some submersibles for that purpose, Flygt pumps for example, are designed not to sustain significant damage from running dry. These are not the same as ESPs mentioned above.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#30
In reply to #25

Re: Induction Motor On No Load

09/27/2010 11:20 PM

the clue is the word "submersible"

ESP's are in the fluid, the design will keep the dymanic fluid level at approx 1000ft ABOVE the intake.. therefore keeping the pump "submerged"

Dymanic fluid level.. the level the fluid reaches when the production rate of flow from the pump matches the inflow from the well.

Static fluid level.. the level the fluid reaches when the pump is not working.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#26
In reply to #24

Re: Induction Motor On No Load

09/27/2010 1:15 PM

GA

The only things I wish to add is that both an underload and an overload condition will not instantly (milliseconds) cause damage to the motor and pump. Also one must consider that briefly both current conditions will normally occur in the operation of the pump. Overcurrent will happen during startup and undercurrent will happen prior to operation and with a large bubble. So care and consideration should be used in deciding how to respond to both of these failure modes and how quickly one should respond to them. One should also consider the possible risk from a restart. It might be tempting to use a PTC resettable fuse to handle both trip conditions but this can easily become worse than nothing. The PTC will work perfectly for a motor that has a shorted winding, but think about what can happen with running a pump dry. A pump that continuously cycles on and off will not really be protected.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#27
In reply to #26

Re: Induction Motor On No Load

09/27/2010 2:38 PM

All this is great.

But if this is the cheap 1/4 Hp off the shelf submersible sump pump all the extra protection far exceeds the cost of the pump.

Those $90 pumps don't last long anyways. Water leaks in and ground faults, bearings wear out, plastic impeller seperates from shaft, casing rusts out, etc.

There is a reason for a one year limited warranty.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#28
In reply to #27

Re: Induction Motor On No Load

09/27/2010 2:49 PM

Very good, another important critical factor in deciding if protection is needed. But in making this cost/benefit calculation you shouldn't only worry about the cost of the pump replacement. One should also consider the possible cost to what is getting flooded and the possible down time.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#29
In reply to #28

Re: Induction Motor On No Load

09/27/2010 7:10 PM

2 pumps and float switches!

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#31
In reply to #26

Re: Induction Motor On No Load

10/23/2010 6:40 AM

Hi Redfred

You are right, the U/L will not occur immediately, that would depend on the time delay set on the motor controller. However the O/L will trip immediatly if the timer settings are set to do so.

To explain: A submersible pump motor controller (MC) is not like anything in use anywhere else, it has so many functions, all to protect the motor. The typical functions are under & over loads plus the time delays on those functions, the over & under voltage plus time delays, Hz trips, automatic starts, restart timers, cumulative restart timers, lock out settings, back spin timers and lock outs, plus digital and analog inputs, plus a host of other functions that would make this reply way to long to read.

With a ESP if it trips, it may not be a failure, under-loads are caused by gas, blocked intake, NOT cavitation (lets not go there please) and several other things. Over load trips:.... heavy oils thro pump, sand, grit, stones, temporary drop in volts, and a host more.

Typically I set both trips to operate after a few seconds, however in the case of O/L's then the controllers measures the O/L and dependent on the value will either ignore the value until the timer has expired or if its over a preset higher value it then trips. Same for start-up (inrush current), it also has a short circuit value.

Underload trips can be restarted automatically by the controller if programmed. Typical restart is 30minutes after the shutdown (to allow motor cooling) and providing the pump/motor is not back spinning. That is measured by what we call a, "Back spin relay". Motor rotating in reverse generates a small current, this device detects this and and prevents the MC from starting.... don't want to brake shafts or couplings!

The auto restart, again all programmable, for a underload trip this will only happen three times with a time interval of minimum 30 mins between starts, then the MC locks out, never to start until the technician investigate the problem.

Over loads... a one time only trip that requires technical intervention

So not all trips are failures, just something the MC does not like happening down-hole, as for pump cycling.. not a good idea, reduces the "run life" of the pump. A re-design should be considered if consistent cycling is happening

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Register to Reply 31 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: