Purging Long Runs of Stainless Pipe

09/29/2010 2:15 PM

We are in the process of finalizing installation of about 2000' of 6" schedule 40 SS open butt pipe for JP8 fuel. We would like to reduce the amount of time it takes to purge, what we are considering is a pre-purge approach, if it makes since, using Nitrogen at a very high CFH (Let er rip Nitrogen is cheap)until Oxygen is out of the line and then introducing the Argon before doing the welding. This is a 100% X-ray job and to date we have had no failures, we've used the Dams etc in the fab shop those devices are not practical anymore for final connections. Any advice would be appreciated. Note: System is underground and its also a double wall, the carrier pipe is what I am referring to.

Thanks,

PI

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Purging Long runs of stainless pipe

09/29/2010 2:20 PM

How about pulling a vacuum on it and then introducing the argon?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 142
Good Answers: 1
#2

Re: Purging Long runs of stainless pipe

09/29/2010 2:24 PM

Actually we have already tried that in a crude sort of way shop vac, we haven't pulled it down to north of 29" can't imagine how long that might take.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Purging Long runs of stainless pipe

09/29/2010 2:36 PM

Interesting question. It would depend on how big a vacuum pump, but at least a gauge would tell when the line was sufficiently empty.

When purging with nitrogen, do you measure the gas composition emerging at the other end to be sure the oxygen is low enough? I wonder how long that would take in comparison.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 142
Good Answers: 1
#4
In reply to #3

Re: Purging Long runs of stainless pipe

09/29/2010 2:49 PM

Yes we would check the exit purge port for gas composition, we would run it at a very high CFM, we have actually been pressure checking all systems with Nitrogen this is above and beyond the NDE already required. This line gets buried and part of it is under a live railroad, the outer shell will have a monitoring charge on it. Thanks for your interest your serve. :)

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#5
In reply to #4

Re: Purging Long runs of stainless pipe

09/29/2010 11:30 PM

The process you adopt is OK. Blowing With high CFM nitrogen will definetely drive out oxygen sufficient enough to the requirement. If you consider evacuation by a vacuum pump, I suggest to do it after nitrogen purging (to drive out the moist air) and before introducing argon.

Register to Reply
Power-User
Hobbies - CNC - New Member

Join Date: Feb 2010
Location: Vallejo, CA
Posts: 127
Good Answers: 8
#6

Re: Purging Long Runs of Stainless Pipe

09/30/2010 12:38 AM

A possible alternative, which would require qualifying a welding procedure, would be Solar Flux. A paste with water or methanol forms an excellent interior purge. If the specifications allow, the quality might well be better than the purge achievable on 2000 feet of pipe with ~ 50 open butt joints, any or all of which can leak air. From an old retired Steamfitter weldor.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7

Re: Purging Long Runs of Stainless Pipe

09/30/2010 5:57 AM

Has the pipe already been used for JP8, giving an explosion risk if it's welded? If it's a new installation, why do you need to purge, can't you just pump the fuel through? Gas suppliers don't use inert gas on a new pipe, they purge the air out with gas.

I did a job where a biogas pipe needed aditional welded fittings. We blew the biogas out using the installed biogas booster, admitting air to the suction. After completing the job, we purged with biogas, and checked when it burnt. Took the discharged air/biogas via a hose under water in a bucket, to prevent flashback, but not much risk of that as could smell the gas before we tried lighting it. Worked fine, but most of the plant operators kept well away!

Cheers........Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Power-User

Join Date: Dec 2007
Posts: 142
Good Answers: 1
#8
In reply to #7

Re: Purging Long Runs of Stainless Pipe

09/30/2010 6:11 AM

This is a new line and all described method/procedures are required by end user, Thanks for your input and interest.

Regards,

PI

Register to Reply
Active Contributor
Popular Science - Cosmology - New Member

Join Date: Sep 2009
Posts: 16
Good Answers: 1
#9

Re: Purging Long Runs of Stainless Pipe

09/30/2010 9:48 AM

We routinely use nitrogen to purge fuel lines. You don't have to use extremely high flow rates. Nitrogen will mix with the existing air, decreasing the O2 content as it does so. Purge for an hour and sample. You should be below 100 ppm O2. Any residual O2 will be absorbed & diluted by the JP.

Register to Reply