Running an Induction Motor in Delta Connection Instead of Star

10/02/2010 9:44 PM

Hi Forum,

I am a newcomer arriving here by googling. Am a vibration specialist with mechanical background and have recently monitored a 2 pole motor which I find unusual. (guess is 15 kW) We have 50 hz line frequency and the unit is running at 2900 rpm instead of normal 2985 rpm or thereabouts. In my nearly 20 years of vibration work I have never seen a fixed speed motor run this far below synchronous speed. Some small motors might get as low as 2950 or 2960 rpm but larger ones never seem to go lower than 2980 - 2985 rpm.

I have asked the on site electrical people and they advise it is not a VFD. I read somewhere (can't remember where) that if a motor which is intended for star connection is connected in delta (or vice versa) it can run at considerably lower speed.

Can anyone shed light on this?? Any help much appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2009
Posts: 227
Good Answers: 11
#1

Re: Running an induction motor in delta connection instead of star.

10/02/2010 10:05 PM

It could be that the motor is working too hard. The bearings might have bad lubrication or the load is a bit too much for the motor. Is it a two-pole wound rotor with 3-phase stator?

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#28
In reply to #1

Re: Running an induction motor in delta connection instead of star.

10/08/2010 9:25 AM

GA

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Running an induction motor in delta connection instead of star.

10/03/2010 12:25 AM

AC motor speed is related to the applied frequency and the number of poles in the design. It is then further delineated by design characteristics that determine the "slip speed" of the motor, i.e. how much the actual running speed differs from the synchronous speed. Factors that determine slip are rotor resistance and load. As you increase load, slip increases and the motor pulls more current as it tries to "catch up". But if you are observing different slip speeds on identical loads, then the difference is probably rotor resistance, in other words the motor was made that way. This may have been on purpose, it may also just be a quirk of that particular motor. Most likely it was on purpose, you may have ben observing a "high slip" motor design, what we in North America would call a "Design D" motor. They have their purpose but are not common.

This article explains it in more detail.

PS: The issue of suing a different motor connection has to do with a false notion that changing it will save energy and people do it with surprising regularity. It's not true, but that doesn't stop them. What it does is change the torque capacity of the motor, which if the load is the same, allows for higher slip. But if the load is the same, it also risks stalling.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Running an induction motor in delta connection instead of star.

10/03/2010 3:53 AM

This may come as a silly question, but did you look at the manufactures rating plate. You may be chasing a problem that doesn't exist.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Oct 2010
Posts: 2
#4

Re: Running an Induction Motor in Delta Connection Instead of Star

10/03/2010 7:10 PM

Hi All,

Thanks for all the responses.

From vibration point of view bearing lubrication is OK. This can be gleaned from the spectra. Load could be an issue.

I haven't looked at the nameplate and will do so next I am on site. I don't expect it to show a speed this low though. In my vibration work I constantly check the exact speed motors run and never found any this far below the speed they should do given poles and LF.

So from JRaef's reply it would seem possible that if it were connected opposite the intended it changes torque capacity allowing for higher slip for a given load. Then it would seem it's a matter of how much extra slip.

I will run this by the site's electrical people when I am there in a months time. Thanks again to all responses. rgds

Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#16
In reply to #4

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 5:23 PM

Factors that will hinder ur attaining synchronious speed are as follows:

1) System voltage as compaired to ur motor rated voltage.

2) System frequency as compaired to ur motor rated frequency.

3) If the PF of ur motor is low, the slip will be more.

If the above are in place with ur system requirement, it could be a design spesification if the motor is not runing hot and have not been rewound in error. Bearing faults and unballanced winding could led to severe vibration that will further increase the slip speed.

Motors that are consiquently connected have very high slip than motors with normal pole connections. Since no consequent pole connection will produce a two pole connection, ur answer will not be far from the previous and present answers.

Dickson.

__________________
There is peace in silence and achievement in plans.
Register to Reply
Associate

Join Date: Jan 2010
Location: India
Posts: 42
#5

Re: Running an Induction Motor in Delta Connection Instead of Star

10/03/2010 11:11 PM

Let us calculate, ASSUMING the motor you are talking about is a 3-phase INDUCTION MOTOR with squirrel cage construction.

N (RPM) = 120 x f / p ; substituting f = 50 Hz and p = 2

N (RPM) = 120 x 50 / 2 = 3000 RPM

On no-load condition, for INDUCTION MOTOR the slip is 3% and hence ROTOR speed reduces by that much.

Therefore, Shaft RPM = 3000 * (1 - 0.03) = 2910 RPM. The slip could be slightly less on latest EFF-1 and EFF-2 type or special motors.

Having said that, speed is directly proportional frequency. So, check the motor RPM in NO-LOAD condition, if possible without any connection to its shaft. Measure FREQUENCY and compare.

If all are fine, the motor could be mechanically restricted from rotating or is being overloaded. But then if this condition exists, motor's OVERLOAD protection must trip.

Also, speed reduces if the gap between ROTOR and STATOR is more. This might happen if motor is rewound too many times.

Trust this starts some thinking process !!!

www.maintenancecircle.com

__________________
Writer Anand
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6
In reply to #5

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 12:14 AM

Also, speed reduces if the gap between ROTOR and STATOR is more. This might happen if motor is rewound too many times.

would you explain this statement please?

Thanks

__________________
The square root of nothing is what you make it!
Register to Reply
Associate

Join Date: Jan 2010
Location: India
Posts: 42
#7
In reply to #6

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 12:21 AM

During re-winding, if slotted stampings are re-assembled or replaced the gap could widen. Typically, on induction motors, the gap is between 0.2 to 0.5mm radially. Increased gap reduces transfer of electro-magnetic field from stator to rotor due to increased air gap. Closer the rotor and stator, better.

www.maintenancecircle.com

__________________
Writer Anand
Register to Reply Off Topic (Score 3)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10
In reply to #7

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 12:57 AM

During re-winding, if slotted stampings are re-assembled or replaced the gap could widen.

I guess you mean that the slotted stator laminations in which the windings are placed are removed?

I have NEVER seen the stator laminations removed for a rewind and I've been in the electrical business for over 30 years, unless this is something new or its something you've seen done.

The remainder of your comment is a given, however if you are sending the motor for rewind then you would hope that the rewind company would have the technical knowledge NOT to increase the air gap and if they are your regular re-winders, then they will have the tech specs including dimensions of the motor on record. The purpose of the re-wind is to repair/refurbish the motor so it is returned to you "as new", and NOT technically deficient and less efficient then when it was in service before it required a rewind.

I served my time in (at the time) one of the largest steel works in Europe and they would rewind motors in house (without any loss of efficiency) of any size from 1/4HP to 2000HP... never heard/seen/assisted in the removing of laminations as part of the rewind process or rewinds affecting the air gap and the efficiency.

anyone else heard of this?

Now, if the laminations have damage from the rotor touching while rotating or from a failed bearing/bearings, then severity of the damage will dictate your next action, to either press out ALL the laminations & replace like for like, or smooth down the damage on the stator, or inspect and attend to the damage, if any, to the rotor..a judgement call really. But again a GOOD re-wind shop will know what they are doing and will take EVERY precaution NOT to increase the air gap

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 4)
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#13
In reply to #10

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 7:10 AM

"But again a GOOD re-wind shop will know what they are doing and will take EVERY precaution NOT to increase the air gap."

Just to throw something else into the discussion, with my local RSES chapter I toured a motor rewind shop. I had heard of the importance of a proper baking (to remove the lacquer coatings), and was able to ask about it. Apparently significant harm can be done to a motor by not baking off the lacquer.

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#14
In reply to #13

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 7:38 AM

Exactly...

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#17
In reply to #7

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 8:39 PM

If it gets to the stage of replacing laminations it's usually more cost effective to replace the motor.

I've seen laminations replaced just the once in 39 years, but that was a special case. Your not going to be able to phone your supplier for a 100MW combined motor generator and get one off the shelf. The stator was rebuilt in situ from a bare shell.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#8

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 12:33 AM

This is a slip of just over 3%, perfectly normal if the motor is operating at full load.

Cheers

Martin

Register to Reply
Associate

Join Date: Jan 2010
Location: India
Posts: 42
#9
In reply to #8

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 12:52 AM

Correct.

__________________
Writer Anand
Register to Reply
2
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#11

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 2:56 AM

This is typical of a "3000" rpm motor after a rewind. A number of other anomalies may also reduce motor speed, like the incoming voltage may fluctuate slightly from the normal rated 380 or whatever voltage applies. Most times we found that this voltage, in our region at least, the voltage is higher (525v rated but 540v supplied). You may need to check a few more specs than you are used to, or have done up to now. Since you state there is no VFD, i believe your answer lies in the rewind history (motor efficiency can drop by up to 12%) or the incoming supply.

__________________
Always learning
Register to Reply Good Answer (Score 2)
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#12

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 3:07 AM

I have seen some motors used in process plants, where designed with 6 wire for Star/Delta. The applied voltage and current consumption is varied in the connection but not the Speed. As said earlier connection does not relate to speed of the motor.

Register to Reply
Participant

Join Date: Sep 2010
Location: Germany
Posts: 2
#15

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 8:03 AM

Hello, thank you very much for the support.

Register to Reply
Anonymous Poster
#18

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 8:47 PM

Is the induction motor is also called synchronous motor ?

Register to Reply
Power-User

Join Date: Jan 2009
Posts: 227
Good Answers: 11
#19
In reply to #18

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 10:25 PM

No. Synchronous motors, as the name implies, run in synchrony with the AC line frequency. A two-pole synchronous motor will run at 3000 rpm at 50 Hz. or 3600 rpm at 60 Hz. What happens under load is that the armature drops a bit behind the position it holds in the rotating magnetic field under no-load conditions. If it is unable to keep up with the field, it generally stalls. Synchronous motors are preferred for motor-generator sets with AC in and out, and for VFD systems where precise speed control is important.

An induction motor, on the other hand, slips constantly when it is loaded, so its speed can be and generally is less than the synchronous speed. Induction motors are also generally cheaper to build than synchronous motors except for very low power applications such as electromechanical clocks and timers.

Register to Reply
Anonymous Poster
#30
In reply to #19

Re: Running an Induction Motor in Delta Connection Instead of Star

10/12/2010 8:23 PM

Please read this from other thread:

18 power thyristor module are used for controlling 6.6 Kv Synchronous motor's Rotor with Exciting Voltage of 60 Vdc, and 375 Exciting Current

Is that mean the speed of synchronous motor can be changed by using thyristors to control the motor's exciting ?

Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#31
In reply to #30

Re: Running an Induction Motor in Delta Connection Instead of Star

10/12/2010 9:29 PM

No, the thyristor module is used to implement a variable frequency drive, the motor remains "synchronous" to this variable frequency; slip in a synchronous motor is usually a very bad thing.

Register to Reply
Power-User

Join Date: Oct 2008
Location: Thousand Islands, Ontario, Canada
Posts: 187
Good Answers: 9
#20
In reply to #18

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 10:52 PM

No.

Register to Reply
Associate

Join Date: Jan 2010
Location: India
Posts: 42
#21
In reply to #18

Re: Running an Induction Motor in Delta Connection Instead of Star

10/04/2010 11:04 PM

No. An induction motor is an ASYNCHRONOUS type of motor wherein the ROTOR is always trying to CATCH UP with Stator but will not reach and the difference is called SLIP which is typically 3% under no-load conditions.

__________________
Writer Anand
Register to Reply
Anonymous Poster
#22
In reply to #21

Re: Running an Induction Motor in Delta Connection Instead of Star

10/05/2010 10:45 AM

Is that means, the Induction motor can run with slip but synchronous motor not ?

Thanks for help.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#23
In reply to #22

Re: Running an Induction Motor in Delta Connection Instead of Star

10/05/2010 12:39 PM

Yes. If a Synchronous motor "slips", it slips an entire pole, usually with dire consequences.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#24
In reply to #23

Re: Running an Induction Motor in Delta Connection Instead of Star

10/05/2010 12:49 PM

Thanks for your answer.

I have another question, now i understand that both synchronous and induction motors are supposed to run with fixed speed,is that mean we can't make variable speed control for those motors ?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#25
In reply to #24

Re: Running an Induction Motor in Delta Connection Instead of Star

10/05/2010 7:56 PM

Not without varying the voltage AND the frequency proportionally.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jan 2009
Posts: 227
Good Answers: 11
#26
In reply to #24

Re: Running an Induction Motor in Delta Connection Instead of Star

10/05/2010 9:49 PM

That's the purpose of a VFD (Variable Frequency Drive).

Register to Reply
Anonymous Poster
#27
In reply to #26

Re: Running an Induction Motor in Delta Connection Instead of Star

10/05/2010 10:55 PM

Thanks for your reply,but i can see many commercial AC motors with SCR (phase control)to control the speed ?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#29
In reply to #27

Re: Running an Induction Motor in Delta Connection Instead of Star

10/08/2010 1:22 PM

Only a couple of specific types of single phase AC motors can be speed-controlled with SCR voltage controllers.

  1. Shaded Pole motors, which are usually small light duty applications like ceiling fans and aquarium pumps. The "speed" is actually not directly controlled, but the lower voltage reduces the torque and the lower torque allows the load to increase the slip severely, but a Shaded Pole motor can run fine at high slip without damage.
  2. "Universal" motors which are actually an AC/DC hybrid like motor, usually found in portable power tools and small appliances.

Sometimes people use SCR voltage control on what are called "vibrator motors" which are 3 phase high slip designs, i.e. 10% or more, for vibratory feeders because the application is narrowly specific and at lower 'speeds" (really lower torque again) the idea is that the feeder will be doing less work, similar to a centrifugal load.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#32

Re: Running an Induction Motor in Delta Connection Instead of Star

10/19/2010 8:46 AM

Speed of the motor is dependent on supply frequency, no. of poles and rotor resistance also. If the bearings and lubrications are O.K.,the speed of motor may decrease with overload condition whereas motor current will increase w.r.t. F.L.A..If the motor is rewinded, with replacement of rotor copper bars, and if the used copper bars have different resistance ( due use of different sizes of copper bars/different quality of copper conductors etc.), the rotor resistance will differ w.r.t. to original design value and hence speed can drop ( or slip can increase)

__________________
Manindra
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#33

Re: Running an Induction Motor in Delta Connection Instead of Star

10/20/2010 2:55 PM

Hi

Got another answer for you to consider

Have you checked for Harmonics?

Negitive sequence harmonics, 5th, 11th, 17th etc, will cause heating (additional) in the motor because they try to run the motor slower than its designed speed, because negitive Harmonics create a reverse rotating magentic field within the motor.

Positive harmonics, 7th, 13th, 19th etc still cause heating but have the opposite effect.

This information I obtained from Fluke, makers of Power Quality Analysers

__________________
The square root of nothing is what you make it!
Register to Reply
Register to Reply 33 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amarnath.sn (1); Andy Germany (1); Anonymous Poster (5); baxterm (3); brich (4); Coldspot (1); Dickson (1); JRaef (4); jvrj (1); maintenanceanand (4); manindra (1); MNIce (3); romanpehl (1); TonyS (2); VibrationGuy (1)

Previous in Forum: AC Generator AVR Schamatic Diagram   Next in Forum: Armature Core in Electrical Generator
You might be interested in: Vibration Instruments, Vibration Sensors

Advertisement