Bus Duct Design

10/05/2010 7:43 AM

We want 4000a bus duct and we have selected aluminum bus bar 120 x 10 mm x 4 run per phase and 12 x 10 mm x 2 runs for neutral could any one tell us about housing or enclosure for the same

We have selected bus bar support finger type smc and distance betn support to support is 500 mm

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Bus Duct Design

10/05/2010 8:37 AM

Are you willing to pay for the information?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#2

Re: Bus Duct Design

10/05/2010 8:56 AM

Here's a short PDF that should send you in the right direction for FREE.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Bus Duct Design

10/05/2010 11:06 AM

Get a quotation from a reputed manufacturer and compare.

__________________
pnaban
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#4

Re: Bus Duct Design

10/05/2010 10:59 PM

For 4000 Amps Busbars selected is not adequate.

Busbar selection will depend on ambient temperature, temperature rise permitted and overall enclosure dimensions.

Distance between Supports depend on short circuit withstand capacity of the Busduct.

In my opinion for 4000 A LT Busduct,for temperature rise of 35 deg C over an ambient temperature of 50 deg C, the Aluminium busbar to be selected to be 4 runs of 200 x 10 mm per phase and 2 runs of 200 x 10 mm for neutral.

The Busbars and inside of the Enclosure to be matt black painted.

The Aluminium selected to be electrolytic E91E grade.

For any further clarifications/design details you may contact me privately

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Anonymous Poster
#8
In reply to #4

Re: Bus Duct Design

11/08/2010 9:17 AM

can i pls get the bus duct sizing for AL and Cu..pls send to my mail id...anitha.vellaiperumal@gmail.com

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5

Re: Bus Duct Design

10/05/2010 11:37 PM

As per B.S. 162-1961 following reference values are admissible for voltage upto 415v / 440v:

Minimum length of insulator = 19 mm (Direct length from the live metal to earth, regardless of shape).

Minimum clearance to earth = 16 mm.

Minimum clearance between phases or between connection of the same phase seperable electrically from each other = 19 mm.

Conventionally minimum 100 mm seperation is maintained between one bus bar to another (conductors) by the manufacturers to allow overlaps at the joints, to carry out nut bolting and for ease of fabrication.

Bus Bar support is in the form of readymade insulator or bakalite sheets cut-slot to accomodate the bars. `

Sheet metal Gauge size is 14 for the enclosure.

Since melting point of aluminium is low therefore copper is normally selected from the point of short circuit sustaining.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#6

Re: Bus Duct Design

10/05/2010 11:47 PM

Further the enclosure should be made out of Aluminium to avoid eddy current and thereby heating of enclosure.

If the Sheet steel enclosure is designed then there will be circulating eddy currents which will heat the enclosure.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Bus Duct Design

10/06/2010 3:38 AM

In a situation where there is the possibility of high fault current I would avoid aluminium. Twice I've had to sort out the mess when aluminium bus bars have buckled under stress.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!