Cooling and Humidity Control

10/07/2010 12:42 PM

We have installed DX unit unit for air conditioning of the laboratory. The units need to cool the GC lab with 100% fresh air. Cold air is exhausted due to hydrocarbon contamination. During summer, the humidity in the outside air is 85 to 90%. We are able to achive temperature as low as 14 Deg C and we are unable to bring the humidity inside to 50% which is required.

Kindly advise what is wrong with the units.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: Cooling and Humidity Control

10/07/2010 1:40 PM

DX unit unit

What's this?

Check with the manufacturer for the dehumidification specs of the unit unit under the loads you demand. You may have to upgrade or add some additional equipment.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#2

Re: Cooling and Humidity Control

10/07/2010 7:58 PM

Are you using a heat exchanger to cool the incoming air with the outgoing air? Give the incoming air more contact time with the heat exchanger, and the dehumidifier, slow down the flow.

__________________
mike k
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Cooling and Humidity Control

10/08/2010 10:33 AM

It sounds as though the equipment is being asked to do something it is not rated to do.

14degC is legally too cold for a UK workplace where people are seated for any length of time, for instance. Try turning the required room temperature up a bit: 18-19degC, perhaps? The product air RH will certainly be lower at these higher temperatures with no additional dehumidification, and as a bonus the electricity bill will be lower and the occupants more comfortable.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#4

Re: Cooling and Humidity Control

10/10/2010 9:31 AM

I think this is a case of oversizing the unit for the volume of air. Perhaps increasing blower speed would have some favorable results, but maybe not.

If your condensing unit will permit, you might consider raising the suction pressure with an EPR valve. However, then you might experience destructive higher discharge temperatures or compressor short cycling on the pressure control. In that case post evaporator refrigerant liquid injection might be necessary.

Such modifications would surely void any warranties and would have to be done by a mechanical contractor on a time and materials bases because it would be pretty much experimental.

In any case a psychometric study will reveal the solution, money will cure the problem.

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote