I'm a consulting engineer overseeing modifications to existing 26" refrigerant line and a contractor has installed a 24" Butterfly Valve in this line using a 24" weld neck flange slid inside the 26" pipe and welded on the exterior only. Since concerns were raised they have proposed filling the void between the inner pipe wall and weld neck's end that was intended for a butt weld connection. See drawing below.

I have rejected this installation but was told from the contractor that this is, in their opinion, the best way to install the valve. It is really the reducer or method of reduction that I object to, although the valve was specified and shown on drawings as 26" installed with 26" slip-on flanges.
The installation specification is ASME B31.1, although this is not a pressure vessel or pressure piping. The service is R22, under vacuum is what has been claimed since it is on the suction side of the compressor.
I am interested in other opinions from experienced piping designers and engineers. Would anyone else except this installation? Is there a way I can have pipe stress calculations done, welds inspected and documented, etc that would meet the requirements of a ASME B31.1 installation?
I know, B31.5 might be a more appropriate spec for this service but it was spec'd as a B31.1 installation.