10/27/2010 6:10 AM

What is the best way to join copper and aluminum busbar ?

Is just tinning the copper busbar sufficient?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#1

Re: CU to AL

10/27/2010 6:17 AM

Bi metalic shrims

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: CU to AL

10/27/2010 7:24 AM

Tin the copper first.

Smear "Densal" jointing paste on each face before joining.

__________________
The reports of my death are greatly exaggerated.
Reply
Active Contributor

Join Date: Jul 2008
Location: Malawi
Posts: 20
#3

Re: CU to AL

10/27/2010 9:11 AM

Hi thanks

I wasnt logged in when I asked the question. Im in Malawi (wheres that? east central africa, where madonna buys her babies) we dont have bi metal shims or copper grease or pretty much anything readly avail. I can get solder, is it good enough?

Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: CU to AL

10/27/2010 1:15 PM

It's been done; It's not recommended, especially outdoors where it's exposed to weather. If you are joining the busbars directly, tinning (solder) is a good idea - don't know how well it will work on the aluminum, but at least on the copper. Stainless steel hardware is best if you can get it.

See the following article that seems to agree with this:

http://ecmweb.com/images/archive/1000_bolted_joints.pdf

Practice at my company when we have to connect copper to aluminum conductors is to use bronze connectors on the copper cables, with Penetrox joint compound. We also try to put the aluminum so it's above the copper. This is so that the copper oxides don't get washed down onto the aluminum and cause corrosion. Check this out:

http://fourseasonsroofingandsiding.com/mixmetals.htm

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: CU to AL

10/27/2010 8:58 PM

Don't try tinning aluminium, just tin the copper.
If you can't get jointing compound use Vaseline.

__________________
The reports of my death are greatly exaggerated.
Reply
Active Contributor

Join Date: Jul 2008
Location: Malawi
Posts: 20
#6

Re: CU to AL

10/28/2010 3:32 AM

Thanks Guys.

Its a new 2000 amp incommer to an indoor panel. I will just tin the copper busbar.

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7
In reply to #6

Re: CU to AL

10/28/2010 5:52 AM

Please make sure you use something to stop the aluminium oxidising / corroding. Vaseline must be available.

Under no circumstances use copper grease it will corrode within hours. I found out the hard way!

__________________
The reports of my death are greatly exaggerated.