Surge Supressor Clamps in 85 Picoseconds

11/07/2010 11:05 PM

Can a company save 20% or more on Electrical bills by installing surge supressors that clamp nearly instantaneously at 85 picoseconds on every circuit breaker panel, sub-panel, and equipment disconnect not attached to a breaker panel?

There is a company that claims that 90% of power surges can come from within a facility, and these small transient surges occur as often as 400,000 times daily, and they can provide a 20% savings, guaranteed in writing, for every business by doing this installation and stopping said surges.

Can anyone explain to me why this is, or more likely, is not possible?

__________________
All we want are the facts, ma’am.” Sgt Joe Friday, "Dragnet"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Surge Supressor Clamps in 85 Picoseconds.

11/07/2010 11:16 PM

All we want are the facts, ma'am

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Surge Supressor Clamps in 85 Picoseconds.

11/08/2010 12:12 AM

Sounds like Mission Improbable to me.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
4
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#3

Re: Surge Supressor Clamps in 85 Picoseconds.

11/08/2010 6:50 AM

Yes, spikes are everywhere, mostly from inductive flyback currents when switches are opened to motors, etc. There is no power savings to be had by clamping spikes, but they can be damaging to other equipment, hence the motivation to install surge suppressors. You commonly see suppressors in protected AC outlet strips. These use transient-voltage-suppressor (TVS) components called metal-oxide varistors, which act instantaneously when a breakdown voltage is exceeded at the MOV's electrodes. The MOV pictured is a 20-cent 130V 14mm V130LA10AP type. Follow the two links and read all about it.

The key to evaluating speed is to realize that AC wiring, motors and solenoids, etc., has inductance and capacitance that limits the spike risetimes to much longer than 5 to 50ns, which means that a 1ns suppressor will be faster than the spikes. Forget talking about 85 picoseconds, that's meaningless in this context.

To get more specific, look at the V130 component leads in the picture. Measured right at the body with a fast oscilloscope a clamping response of faster than 1ns would be observed. But measured at the end of the leads a slower say 5ns response to a high-current surge would be observed, simply from the inductance of the leads. For example, say the inductance is 20nH and suppose we have a 10A 5ns current spike. We can calculate a voltage of V = L dI/dt = 40 volts developing across the short leads. Our MOV can clamp at its body, but we can measure un-clamped voltages at the ends of the leads. Now consider lengthy AC-line house wiring with much higher inductances, in the uH region. This example should illustrate why it doesn't make sense to talk about picosecond response times in the context of TVS boxes and circuits.

Here's a rough draft of the circuit of a typical inexpensive multiple-outlet surge suppressor, taken from the section on AC-line protection in the upcoming 3rd edition of The Art of Electronics. It's useful to open up one of these units for yourself and examine all the parts. You'll note the circuit has two fuses, which serve the very important function of disconnecting the TVS components in the event of one failing in the line of duty, to help prevent starting a fire. After a fuse blows the neon light will go out, indicating that you no longer have surge protection.

As for installing masses of suppressors all over, it's interesting to observe that a surge suppressor in one spot, such as in a computer at the end of a power cord, works to help protect items in nearby "unprotected" locations.

__________________
Thanks, Win
Register to Reply Good Answer (Score 4)
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Surge Supressor Clamps in 85 Picoseconds.

11/08/2010 8:51 AM

20% or more on Electrical bills can probably be saved by going round regularly switching things off that are not being used, which actually requires no capital investment at all. Consider also the building occupancy - by shifting working hours to use available daylight better, are there lights that would not need to be used <rhetorical question>?

Investment in high efficiency lighting should be the next step, followed by time-switches and occupancy detectors. If the building is electrically heated (!), door closers and draught excluder equipment achieve a high rate-of-return on investment, followed by bulking-up the building's insulation wherever possible to the point where it achieves or exceeds the current Building Regulations' requirements for a new-build.

On a peak demand electrical tariff there is more money to be saved by putting soft-starts on the biggest motors first, and then working downwards through the size ranges across the facility.

Don't neglect those 500W high-bay floodlights, either. There are a number of LED-based replacements available these days, which give the same lumens for a lot less hotts watts.

Can the waste water heat be recovered by counter-current heat exchange with cold mains intended for hot water usage <rhetorical question>? One factory site that neglected the site energy balance in that regard is currently undergoing divestment and redundancies in an effort to save money elsewhere.

As for snake oil, forget it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
3
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#5

Re: Surge Supressor Clamps in 85 Picoseconds

11/08/2010 1:20 PM

NOT POSSIBLE.

Surge suppressors are typically TransZorbs, Metal Oxide Varistors (MOVs) or gas tubes. TransZorbs and MOVs short the high voltage to a reference (typically ground or neutral) and the spike is converted to heat in the TransZorb or MOV. A gas tube shorts the high voltage and the gas tube and the resistance of the building's wire will convert the spike to heat. None of these devices will result in the power not being brought into the building through the power meter. Therefore, no drop in your power bill.

Surge suppressors are a VERY GOOD idea to reduce expensive equipment damage and reduce the expenses of equipment down time.

Think about their claim "There is a company that claims that 90% of power surges can come from within a facility". The surge energy is already past the power meter per claims of "The Company". Surge suppressors don't prevent surges, they redirect the energy in a manner that will hopefully not harm any equipment. This redirection results in the electrical surge energy being converted to heat. There is no mechanism to prevent the power meter from turning. Claims false.

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Register to Reply Good Answer (Score 3)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: Surge Suppressor Clamps in 85 Picoseconds

11/08/2010 1:31 PM

Electricity power quality products and services are a dime a dozen (in that there are many). However, from exactly how you have explained the claims the company in question is a fraud and the claims a scam.

If I read between the lines (a lot) the claims could just be misinterpreted as a hopeless misunderstanding and marketing by power quality and protection salespeople.

Do you have a website link, this is quite different from most other power scams I have come across (if what you say is true). Perhaps you (or the company) meant to say 20% savings through increased equipment life (reduced equipment failure) due to clamping of voltage transients at the main switchboards.

Can you please provide a link to the company's website as we are genuinely interested in more information and clarification regarding these claims (well I certainly am).

__________________
jack of all trades
Register to Reply
Power-User

Join Date: May 2008
Posts: 166
Good Answers: 5
#7
In reply to #6

Re: Surge Suppressor Clamps in 85 Picoseconds

11/08/2010 9:34 PM

http://www.utiliguard.com/ is the company website for Diversified Facility Solutions, LLC here is the page with their guarantee of energy savings http://www.utiliguard.com/documents/guarantee.pdf and finally here are approx 300 plus companies' websites that provide their service for them across the country: http://www.google.com/search?q=link%3Autiliguard.com&ie=utf-8&oe=utf-8&aq=t&client=firefox-a&rlz=1R1GGLL_en___US366#sclient=psy&hl=en&client=firefox-a&hs=Wke&rlz=1R1GGLL_en___US366&source=hp&q=link:+utiliguard.com&aq=f&aqi=&aql=&oq=&gs_rfai=&pbx=1&fp=64371607d2fffabb

Cheers!

__________________
All we want are the facts, ma’am.” Sgt Joe Friday, "Dragnet"
Register to Reply
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #7

Re: Surge Suppressor Clamps in 85 Picoseconds

11/08/2010 10:18 PM

Thanks for the link, it helps a lot.

I am always very dubious of websites that mention the triple triangle of trouble - bold contradictory claims, distributor opportunities and testimonials.

Lots of buzz words and claims bordering on the bizarre and false are made (including contradictory claims of reduced plant energy usage), in the end it just seems like overzealous marketing of what effectively is just a simple run-of-the-mill surge protector product (rather than an actual scam), although some of the claims appear to be crossing the line between real world fact and fantasy.

Would I buy it? No, partly because there are better products in the market (such as quality individual point of protection surge protectors for sensitive products such as computers) and partly because the company paints the (US) power grid in such a poor light that people would think after reading the companies statements that they were living the poorest part of some third world country 50 years ago!

Oh and the fact that the website's "Contact Us" icon takes you straight to the "Distributor Request Form".

My advice is to AVOID!

__________________
jack of all trades
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #7

Re: Surge Suppressor Clamps in 85 Picoseconds

11/30/2010 3:23 PM

So what?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: BANGALORE, INDIA
Posts: 248
Good Answers: 5
#9

Re: Surge Suppressor Clamps in 85 Picoseconds

11/08/2010 11:54 PM

I am interested to know whether these MOVs etc at the main input side really help protect MOSFETS in electronic circuits down stream.

For example let us say we have a electronic gadget operating from 240V AC, 50 Hz. What should be the rating of MOV to be used at the input. I have seen may using MOVs marked 275 or 305 being used and these have breakover voltage of over 600 V or more and then if we use MOSFETs rated 500V, how can it protect? So the voltage marking and breakover voltage rating are too far apart & confusing!!! Manufacturers of MOV like devices need to explain.

What about failure of MOV itself - also means replacement costs. So does anyone use further MOV protection components upstream before MOV on mains side? Any experience advice on this?

__________________
"Perplexity is the beginning of knowledge." -- Kahlil Gibran
Register to Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#13
In reply to #9

Re: Surge Suppressor Clamps in 85 Picoseconds

11/30/2010 9:09 PM

I'm sorry no one has responded to your questions, they are good ones, and certainly relevant to the topic. You are correct about the elevated clamp voltages of MOVs that are defending against rare incoming high-voltage incoming spikes. But consider, a transient spike's energy is proportional to V2, and by clamping a say 3kV spike at 600V, the MOV has absorbed 96% of the spike's peak energy (0.62 / 32 = 0.04). That's a rather significant piece of protection.

As for a 500V offline MOSFET, presented with an attenuated spike, it has it's own protective measures during a breakdown event. First, the mosfet isn't generally sitting right across the AC line. Being in a switching supply, it's on the other side of a common-mode choke, which has a series leakage inductance. Furthermore, the AC-line wiring has series inductance, e.g., dI/dt = V / L. Small mosfets also have a fairly high internal breakdown resistance. All these serve to limit the maximum current that can flow during an over-voltage event.

Let's think about spikes. There are two "standard" spikes, the most intense pulse has a 8us risetime and lasts 20us to the 50% decay point, the other pulse type has a 10us risetime and lasts for 1000us. So we're talking about more or less strong 25us and weaker 1.5ms single-event clamped current pulses into our mosfet. How's a poor little mosfet going to deal with these over-voltage pulses?

On the left we have a portion of a typical mosfet datasheet. This one is fairly-wimpy part, a Fairchild FQP4N50, rated at 500V and only 70 watts. Mouser sells this little mosfet for $0.34 qty 250.

OK, if you can read it, check out the spec called EAS (fifth from the top). That's the part's single-pulse avalanche-energy rating, and the value shown is 260mJ. Crudely-speaking, as long as we keep the total energy below EAS during the avalanche-breakdown event, our mosfet will be fine. Its semiconductor junction will heat up, yes, but it won't fail. This spec means that the part can absorb a power level of P = E/t during the pulse. That works out to 10kW of power-handling capability for 25us, and173W for 1.5ms of breakdown duration. Keep in mind the mosfet only has to handle the left-over 4% of the pulse energy that the MOV failed to absorb itself.

This has not been a detailed analysis, but it should serve to show that our mosfet isn't going to immediately fail if a nearby protective MOV fails to clamp the transient-event voltage to under 500V. In fact, the 600V clamping is what will save our 500V mosfet.

__________________
Thanks, Win
Register to Reply Score 1 for Good Answer
Anonymous Poster
#10

Re: Surge Supressor Clamps in 85 Picoseconds

11/09/2010 1:02 AM

What's not often known is that MOV's have a finite life. Check the manufacturers specs.

They only dissipate a certain amount of energy then they're useless. That's OK if they're replaced, but we all know that rarely happens. A MOV mounted on a circuit board is a bit of a con job (fisher & paykel are you listening). Ffej

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#11
In reply to #10

Re: Surge Suppressor Clamps in 85 Picoseconds

11/09/2010 4:52 AM

While you cannot visually tell if a MOV has gone open, you can definitely tell if it fails catastrophically.A fuse in series with the MOV provides protection from a melt down, and a lamp across the MOV indicates an open(normal)condition.If the lamp is off, this indicates a catastrophic failure has occurred, and the MOV should be replaced.

This is not foolproof, as the MOV can be destroyed without blowing the fuse,but it is better than no monitoring of the condition.

This implementation is used frequently on main panels for sensitive equipment, with the indicator lamp (usually Neon) mounted on the outside of the panel.

When I repair circuit boards (a lost art nowadays) that show signs of spike damage, I replace any MOV's present, and add appropriate ones when possible for future protection.They do work,and have saved me many service calls, as well as building my company's reputation for reliable repairs.

The telephone companies use spark gap protection,where a small air gap is created between signal and ground. An overvoltage condition will arc to ground. Usually 300 volts at building, 600 volts at cable service box.They also use a carbon-arc air gap device at the building at the entry point.These are being phased out in favor of gas type.

Perhaps as technology matures, there will be MOV's with intrinsic indicators,such as (color change) to indicate their condition.

Insofar as saving money on utility bills? Deja Moo! (I've heard that bull before).

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#14

Re: Surge Suppressors Clamps in 85 Picoseconds

12/01/2010 7:16 PM

Transient voltages on the power line are only one source of voltage spikes on electronic components.EMP from nearby lightning strikes are another,and induce voltage almost instantaneously as the magnetic field passes thru a conductor,and is such a high frequency and voltage that it rides the skin of the conductor.MOV's have proven very effective at suppressing this type of surge also, as well as static electricity discharge from improperly grounded circuity or equipment.

An old TV repairman showed me his method of surge suppression,back before MOV's were available: He tied several knots in the 2 conductor cord of the TV,In effect, creating a choke,and he swore by it.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

a+x=z (1); Anonymous Poster (1); BruceFlorida (1); HiTekRedNek (2); jack of all trades (2); PWSlack (2); sbruel (1); TonyS (1); Tornado (1); Winfield Hill (2)