What is the first thing to do when isolating a DPT from the process using 5 way manifold valves? Anybody can help me out of this. Thank you ahead...
Re: Procedure for 5 way Manifold Valves in DPT
11/12/2010 2:28 PM
Good Day
The first thing you do is equalize the pressure. This is usually the middle valve. Open this valve. Then close the two root valves. These are the ones connected to your process. Now with the pressure equalized and the process isolated you can relieve the pressure with the other two valves. The transmitter can now be pulled and serviced. Installation is the reverse of this procedure , except prior to closing the equalizing valve you will usually find bleeders on each side of the transmitter. Open these a small amount to get the air out of the system. Some cheapie transmitters won't have bleeders. But most that connect to a five valve manifold do. It might be a good idea to blow down the root lines as they collect lots of contamination after a while. But this also depends on what your process might be. If your disassembling the transmitter from the manifold don't forget to replace the teflon or buna o rings.
Good Luck
Mike
11/12/2010 11:38 PM
Thank you poor_grape_farmer for your kind and informative response to my query. i rated u good answer.
Good Answers: 176
11/13/2010 2:47 PM
The transmitter should be isolated from the process before the equalizing valve is opened.
A five valve manifold is shown below:
If the equalizing valve is opened before the process in (blocking) valves are closed (isolating the transmitter from the process), then whatever differential pressure that the process develops will create a process flow from the high side, through the equalizing valve and back to the process through the low side.
The (blue) valve added to the diagram below only shows the equalizing function, a connection from high side to low side, but the absence of the blocking valves applies to the issue; the red arrows show the wet leg draining through an opened equalizing valve in a level application.
Likewise, the diagram below shows the effect of steam flowing through an open equalizing valve on a 3 valve manifold. The absence of the vent valves on a 5 valve manifold does not alter the effect of steam flow when the process is not blocked before the equalizing valve is opened:
Good Answers: 19
11/15/2010 9:48 PM
A steam transmitter could really boil itself to death with live steam flowing through the impulse lines!
11/16/2010 6:22 AM
If all else fails, read the instructions.