Inverted Blower Fan

11/12/2010 10:54 PM

Three (3) weeks ago (Oct. 08, 2010 to be exact) I supplied a 350 KVA Dry type Step-up Transformer to a client here in the Philippines with 230 Primary Volt. and 460 Secondary Volts equipped with a 1/2 HP Blower fan on top of its NEMA enclosure. We tested it with my clients 2 machines on its load last Oct. 26 and it proved to be excellent. The Japanese engineering company has even declared that the 350 KVA Step-up transformer is too big for the 2 machines intended for it. The scheduled operation of the unit will still be on Dec. 15, 2010. But to my surprise, yesterday Nov. 12, 2010, I found out that the blower fan on top of the transformer has been tampered with and installed up-side down, making it an exhaust fan, instead of a blower fan. Please advise the effect of this changes on the transformer especially on its temperature since they will be adding another machine (though another light machine) on its load once fully operational.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Inverted blower fan

11/13/2010 12:03 AM

Are you sure it was supposed to be a blower fan? Natural convection would be upward, and if the fan is on top it would seem natural for it to be exhausting.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#2
In reply to #1

Re: Inverted blower fan

11/13/2010 12:45 AM

Yes, it is supposed to be a blower fan. Considering the temperature here in the Philippines, the transformer manufacturer designs only blower type fan directed at the silicone core of the transformer to prevent it from heating up profusely. What I want to know is the difference before and after the invertion of the fan? Can you give me your comments on this?

Register to Reply
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#3

Re: Inverted Blower Fan

11/13/2010 10:12 AM

Who is the manufacturer? Did you contact them? Since hot air naturally rises, I agree with the first comment. It would not make sense to install a fan to blow air into the unit. You generally would want to work with nature, not against it.

Most of these applications I have been involved in have had the fan(s) installed on the bottom of the unit, directing the air into the coils.

__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 262
Good Answers: 1
#4

Re: Inverted Blower Fan

11/13/2010 11:51 AM

Maybe the transformer has been installed upside down ? Then the blower fan at the bottom of it would make sense.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#5

Re: Inverted Blower Fan

11/13/2010 1:39 PM

Quote "the transformer manufacturer designs only blower type fan directed at the silicone core of the transformer to prevent it from heating up profusely. "

Reygay

I would check with the MFG but according to you post, the fan is supposed to BLOW air at the silicone core. You will not get the same air flow across this area using a circulation fan. Suggest you check and see who made the change and why.

Register to Reply
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#6

Re: Inverted Blower Fan

11/14/2010 10:36 AM

Heat rises and when the cooling fan is placed on top of the transformer enclosure, it is supposed to accelerate the removal of heat generated by the transformer, away and out of the cabinet. Due to the normal ambient temperature existing in your area, surrounding outside air were already pre-warmed or preheated, and Blowing in pre-warmed air into the cabinet will not only block the rising heat generated by the transformer, it will also further accelerate the temperature rise of your unit. As long as the lower portion or bottom end of your transformer enclosure are not blocked where fresh and much cooler air exist, then using it as an exhaust fan makes more sense..

__________________
vsar
Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#7
In reply to #6

Re: Inverted Blower Fan

11/14/2010 5:58 PM

I agree, but I forgot to inform you that the enclosure has 8" x 14" ventilation windows on all four (4) sides plus the bottom end of the transformer is open and that's where the cables go thru from the transformer. Please help me by giving your opinion on these matter.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Inverted Blower Fan

11/14/2010 6:09 PM

Have you asked the manufacturer about this? If not, why not?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#9
In reply to #8

Re: Inverted Blower Fan

11/14/2010 11:26 PM

I have'nt asked the manufacturer about this. I just want to gather scientific opinions on this so that I would know what to ask the manufacturer and what to do about this, since this is already tampering on the part of my client.

Register to Reply
Associate
Netherlands - Member - New Member Canada - Member - New Member

Join Date: Oct 2010
Location: Canada
Posts: 41
Good Answers: 2
#10
In reply to #9

Re: Inverted Blower Fan

11/15/2010 8:09 AM

I would suggest you talk to the manufacturer, ask him how he designed the fan to be installed. If indeed the fan is supposed to be blowing into the transformer enclosure from the top, then tell your customer to correct the installation.

As I mentioned before, I am used to seeing fans direct the air upwards through the coils, but if you manufacturer tells you that that is his design intent and he will vouch for it, so be it.

No matter what we say here, I would not direct a manufacturer to change his design unless I specifically requested a particular feature in my specifications, or you will be taking the liability for it.

__________________
I do not feel obliged to believe that the same God who has endowed us with sense, reason, and intellect has intended us to forgo their use. Galileo Galilei
Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#11
In reply to #10

Re: Inverted Blower Fan

11/15/2010 8:41 AM

That's the problem. This Japanese client has lots of transformers being used in their various machineries but all of them has exhaust fans on their transformers. That's the reason they inverted the fan installed on the transformer I delivered. Its either they just want uniformity on their transformers or they really believe that exhaust fans are really better than a blower. I also noticed that other transformer manufacturers here uses exhaust fan instead of the blower. Now that I have given you the complete picture of the said transformer, I hope you could give me your wise opinion or comparison of both fans.

Register to Reply
Associate

Join Date: Aug 2010
Location: Umdorman ,Sudan
Posts: 28
#12
In reply to #11

Re: Inverted Blower Fan

11/16/2010 6:29 PM

As Tornado said it is an exhaust fan not a blower fan because its location is on the top of the transformer.

I know the Japanese are very accurate,impossible to do an error like this as you think.