3P 115A Contactor Coil Power Consumption

11/13/2010 8:59 AM

I am using 460/120V AC 150VA stepdown transformer for controling the circuit.i want to know about what is the power consumption of 120 vac coil to start the motor.

thanks

suthakaran

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: 3P 115A CONTACTOR COIL POWER CONSUMPTION

11/13/2010 9:46 AM

You're kidding us. This has to be a joke. You're installing a three phase to single phase transformer that's power limited to only 150VA and you want to know the power handling of a starter solenoid.

Well lean your head against the computer screen so my crystal ball can tell me what parts you've acquired.

A little closer now.

It's starting to come clear to me.

Lower your shoulder just a bit.

That's it. Now I get a clear picture.

Hold still while I snap a clear picture.

<click>

I'm sorry to say but the prognosis is not so good. You see I didn't find anything in there. I normally would tell somebody here that they should not try to do what they are doing. In your case though you have two reasons that you might want to continue with your efforts. First, where there's no sense there's no feeling. It probably won't hurt. Second, the Darwin awards do achieve a greater social purpose.

I don't know if this will be helpful but I thought you should see what I found:

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2010
Location: St Louis MO USA
Posts: 224
Good Answers: 7
#5
In reply to #1

Re: 3P 115A CONTACTOR COIL POWER CONSUMPTION

11/14/2010 11:30 AM

GA Redfred.... for making me laugh....... many times in here (CR4) I have been helped by your thoughtful and precise answers. Thanks, Ray

__________________
klearzen
Register to Reply
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#2

Re: 3P 115A Contactor Coil Power Consumption

11/13/2010 1:45 PM

If you check the website of the manufacturer of your contactor, you should find a downloadable catalogue that will give you the information that you seek.

__________________
paulusgnome
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: 3P 115A Contactor Coil Power Consumption

11/13/2010 3:44 PM

It depends on the manufacturer. To pick one example, An Allen-Bradley Size 4 starter with a 120v coil requires 69va to hold the coil in, with 1224va inrush. If your starter is comparable, the 150va transformer should be able to handle it plus a couple pilot lights or so.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: 3P 115A Contactor Coil Power Consumption

11/13/2010 8:43 PM

You actually have two issues (assuming only 1 contactor and no other loads):

  1. The Inrush VA of the contactor coil. This can be obtained from the contactor manufacturer and only the specific data for the product you use will be valid. Coil designs vary widely among manufacturers so if you look at the data for one it may not match what another brand will take. For example a Siemens 120V coil for a 120A contactor is 270VA inrush, 22VA sealed. For a similar contactor from ABB, the Inrush is 880VA, the sealed is 44VA. There is too much variation there to make assumptions.
  2. The Inrush capacity of the control power transformer. Regardless of the VA rating of the transformer, some designs offer better inrush capabilities than others. You can make some generalization but only in a very conservative manner. For example a Sola SBE Series 150VA transformer is capable of 969VA of inrush at 40% PF, an Acme 150VA transformer is only capable of 800VA inrush.

So either 150VA transformer would work for the Siemens contactor in my example, but if you had an ABB contactor, only the Sold transformer would work, or you would have to have a larger Acme transformer. The point is, you cannot make generalizations, you must do the research.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Anonymous Poster
#6
In reply to #4

Re: 3P 115A Contactor Coil Power Consumption

11/22/2010 12:36 AM

hi dear friend,

that is a good answer and help me to do some research.Selected Transformer is METTO ELECTRONIC 150 VA 480/120V 60 Hz and Schneider electric 115A contactor coil power consumtion 300VA inrush,22VA sealed)

Thanks and regards

suthakaran

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #6

Re: 3P 115A Contactor Coil Power Consumption

11/22/2010 1:38 AM

Well, you will have to contact them to see if there is any inrush capability in that transformer, the website doesn't say anything useful. But if it was not designed as a control power transformer, it may not have any reserve capacity and the coil inrush is over loading it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Off Topic (Score 5)
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JRaef (2); klearzen (1); Paulusgnome (1); redfred (1); Tornado (1)

Previous in Forum: Asking for Formula and Working Details as a Beginner Electrical Engineer   Next in Forum: Sizing of Drop Out Fuse

Advertisement