I am using 460/120V AC 150VA stepdown transformer for controling the circuit.i want to know about what is the power consumption of 120 vac coil to start the motor.
You're kidding us. This has to be a joke. You're installing a three phase to single phase transformer that's power limited to only 150VA and you want to know the power handling of a starter solenoid.
Well lean your head against the computer screen so my crystal ball can tell me what parts you've acquired.
A little closer now.
It's starting to come clear to me.
Lower your shoulder just a bit.
That's it. Now I get a clear picture.
Hold still while I snap a clear picture.
<click>
I'm sorry to say but the prognosis is not so good. You see I didn't find anything in there. I normally would tell somebody here that they should not try to do what they are doing. In your case though you have two reasons that you might want to continue with your efforts. First, where there's no sense there's no feeling. It probably won't hurt. Second, the Darwin awards do achieve a greater social purpose.
I don't know if this will be helpful but I thought you should see what I found:
__________________
"Don't disturb my circles." translation of Archimedes last words
If you check the website of the manufacturer of your contactor, you should find a downloadable catalogue that will give you the information that you seek.
It depends on the manufacturer. To pick one example, An Allen-Bradley Size 4 starter with a 120v coil requires 69va to hold the coil in, with 1224va inrush. If your starter is comparable, the 150va transformer should be able to handle it plus a couple pilot lights or so.
__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
You actually have two issues (assuming only 1 contactor and no other loads):
The Inrush VA of the contactor coil. This can be obtained from the contactor manufacturer and only the specific data for the product you use will be valid. Coil designs vary widely among manufacturers so if you look at the data for one it may not match what another brand will take. For example a Siemens 120V coil for a 120A contactor is 270VA inrush, 22VA sealed. For a similar contactor from ABB, the Inrush is 880VA, the sealed is 44VA. There is too much variation there to make assumptions.
The Inrush capacity of the control power transformer. Regardless of the VA rating of the transformer, some designs offer better inrush capabilities than others. You can make some generalization but only in a very conservative manner. For example a Sola SBE Series 150VA transformer is capable of 969VA of inrush at 40% PF, an Acme 150VA transformer is only capable of 800VA inrush.
So either 150VA transformer would work for the Siemens contactor in my example, but if you had an ABB contactor, only the Sold transformer would work, or you would have to have a larger Acme transformer. The point is, you cannot make generalizations, you must do the research.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
that is a good answer and help me to do some research.Selected Transformer is METTO ELECTRONIC 150 VA 480/120V 60 Hz and Schneider electric 115A contactor coil power consumtion 300VA inrush,22VA sealed)
Well, you will have to contact them to see if there is any inrush capability in that transformer, the website doesn't say anything useful. But if it was not designed as a control power transformer, it may not have any reserve capacity and the coil inrush is over loading it.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Good Answers: