Sizing of Drop Out Fuse

11/13/2010 9:49 AM

I have a 100kVA 11kV/0.4kV Dyn11 type transformer. I want to connect a 20kW HydroPower plant to this 11 kV grid with this transformer. So, how can I calculate the size of Drop out fuse to connect HV side transformer to 11 kV grid? Or shoud I use MCCB??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Sizing of Drop Out Fuse

11/13/2010 2:07 PM

you are trying to tie the existing 11 kv circuit to the the 20 kw plant thru the 100 kva transformer. The max output of the 20 kw at 11 kv = 1.05 amps and 29 amps a 0.4 kv. The max load at 11 kv on the 100 kva transformer = 5.25 amps. You need to more concerned with protecting the hydro plant as it can only deliver 1 amps to the 11 kv system. Not sure what you are trying to accomplish but 1 amp is not much of an improvement.

Reply
Anonymous Poster
#2

Re: Sizing of Drop Out Fuse

11/13/2010 8:46 PM

Thank you for your answer. But I want to utilize the existing transformer to inject excess power to the grid when the isolated load is less than 20kW.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Sizing of Drop Out Fuse

11/13/2010 10:17 PM

This seems like an odd match, with the transformer four times as large as necessary.

What provisions ensure that the hydro will be in synch when putting it onto the grid?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Sizing of Drop Out Fuse

11/13/2010 11:06 PM

Guest quote "Thank you for your answer. But I want to utilize the existing transformer to inject excess power to the grid when the isolated load is less than 20kW."

You want to inject excess power to the grid but the max is only 20 kw. That is a very small amount of power. What kind of load are you trying to help by doing this?

Reply
Anonymous Poster
#5

Re: Sizing of Drop Out Fuse

11/14/2010 7:44 AM

From this transformer other villages are electrified. But I donot know exactly the villages load. I want to connect 20kW to this transformer. This 20kW Plant also supply power to the villages but during night, there is no load and the whole 20kW can be injected into the grid via this transformer. So I want to know about the sizing of drop out fuse.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6

Re: Sizing of Drop Out Fuse

11/14/2010 1:34 PM

Think about it like this. The max load that you can supply thru the 100 kva transformer is 20 kw. As previously posted that amounts to 20kw/(0.4x1.73) = 29 amps fed from the hydro plant. So to protect the plant you need to install a 30 amp breaker on the 400 volt side of the transformer. This will allow you a max of 20.7 kw thru to the 11 kv grid. Is this the only source to the grid? You need to try to keep the load balanced as close as possible. Does this answer you question? Where are you located?

Reply
Anonymous Poster
#7
In reply to #6

Re: Sizing of Drop Out Fuse

11/14/2010 2:01 PM

Thank you. Then it will be 1.5 Amp breaker for 11kV side right?? Should not I consider power factor 0.8 (however it is a synchronous generator) to calculate capacity of breaker? Or it implies only for asynchronous generator? It is from one of the village of Nepal.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#8
In reply to #7

Re: Sizing of Drop Out Fuse

11/14/2010 5:47 PM

1.5 amp should work. I would not worry about the PF. What kind of load do you have? Is it just lights and small appliances? How many houses are connected?

Reply
Anonymous Poster
#9
In reply to #8

Re: Sizing of Drop Out Fuse

11/15/2010 5:51 AM

143 Households with around 100 watt per house, 5 computers only at day time and 1 saw machine only at day time and its capacity is 2.2kW. Load is inductive.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#10

Re: Sizing of Drop Out Fuse

11/15/2010 1:58 PM

You should be ok. If the length of the 400 volt cable from the power plant is long you need a breaker at the plant to protect in case of a cable fault. That is why I suggested a 30 amp breaker in post 6. What is your background in this type of work? Do you have many of these projects? Just curious? Send your email to me via this forum and I will respond.

Reply
Anonymous Poster
#11
In reply to #10

Re: Sizing of Drop Out Fuse

11/16/2010 5:45 AM

Oh! I am the Master of Science in Power Engineering Student in Germany originally from Nepal (Kathmandu). This is my Master Thesis about the Grid connection of 20kW MHP without Interrupting isolated load. Thank you very much for your quick response.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Sizing of Drop Out Fuse

02/20/2024 7:20 AM

As the purpose of the <...Drop out fuse...MCCB...> circuit protection device is to protect the cabling installation, information on which has been withheld, the question is unanswerable.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 12 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); PWSlack (1); Tornado (1); wareagle (5)

Previous in Forum: 3P 115A Contactor Coil Power Consumption   Next in Forum: Noise Reduction for AV installation

Advertisement