Anonymous Poster

Backflow Prevention

11/14/2010 1:12 PM

Hi, we had a minor accident involving a corrosive chemical. It got past a check valve and into our nitrogen system destroying several brass fittings.

Any ideas on what would do a better job of preventing backflow? Could a pressure regulating valve work? The valve I am thinking about would sense a drop in pressure and close until that threshold is reached again.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Backflow Prevention

11/14/2010 4:28 PM

There are several types of backflow preventers, starting with a single check valve, then a double check valve, and finally an RPZ (reduced pressure zone) backflow preventer. I'm not sure what is available in stainless, but at least the downstream check and service valves need to be corrosion resistant.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Backflow Prevention

11/15/2010 9:32 AM

Double-block-and-bleed works well: two isolator valves with a third valve locked open to drain from a branch.

Spade-off between flanges downstream of the check valve works even better.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Aug 2010
Location: Austin, TX
Posts: 80
Good Answers: 8
#3

Re: Backflow Prevention

11/15/2010 1:55 PM

Sorry to hear of such a problem.

Kind of curious as to what kind of situtation would lead to such a scenerio.

Were you using N2 to drive a diaphragm pump? or for Oxygen displacement?

You may need to take two steps back and consider the current design of the system in question.

Can you provide any more details of the problem?

I would think that if the N2 pressure were greater than the system which introduced the corrosive chemical, the chance of a backflow could be mitigated.

Please provide more details if possible.

__________________
Some standards are like the North Pole and some are like Mecca. People use both to get their sense of direction, however, only one is a preferred destination. - P.E. Scheibmeir
Reply