Transducer Output Why 4 to 20 Ma

11/23/2010 6:32 AM

Hi, All

transducer output why 4~20mA why not 0~20mA

regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: transducer output why 4 to 20 mA

11/23/2010 6:49 AM

Zero would give very poor noise immunity*. Also if you put zero current through a sensing resistor you get zero voltage drop which is difficult to amplify and may well cause problems as if you are working with a single supply of say 0-5v you would have no offset and some amplifiers don't like input or output going down to the negative supply level (0v).
But aside from that I have no idea.
Del

*Calculate 1uA noise current as a percentage of 0mA, then as a percentage of 4mA, that will demonstrate what I mean.

__________________
health warning: These posts may contain traces of nut.
Reply
3
Active Contributor

Join Date: May 2008
Location: Mumbai
Posts: 11
Good Answers: 1
#2

Re: Transducer Output Why 4 to 20 Ma

11/23/2010 9:14 AM

2 wire transducer utilizes 4mA for itself i.e. for powering the transducer/transmitter. Also in case of 0mA it is not possible to identify if there is some problem with transmitter/cable damage or power failure.

__________________
Nikunj Jain
Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#3

Re: Transducer Output Why 4 to 20 Ma

11/23/2010 11:10 AM

One reason was mentioned -supply current for the sensor and connected conditioner in 2 wires systems- there is a second. If the signal you get is outside the limits there is a fault either in the sensor or in the connections and this helps to determine where the failure is. from this point of view it is as for the voltage ranges from 0.5 to 4.5 V which is very usual.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Transducer Output Why 4 to 20 Ma

11/29/2010 1:07 PM

Because 0mA means "a wire has fallen off", or "there is a fault".

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#5

Re: Transducer Output Why 4 to 20 Ma

12/10/2010 12:00 AM

just an idea. zero current in signal transmission is somehow an open circuit and therefore it confuse the receiving end (controller) wether a fault occured or not. 4ma is logically a live zero because it represents zero variation on the measurement considering the transducer/transmitter is in service.

Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#6

Re: Transducer Output Why 4 to 20 Ma

04/02/2011 3:49 AM

If we are using a 0-20mA signal we have to supply power to our electronics in a similarway as to power a voltage signal using one or two extra power supply lines.With a 4-20mA signal we always have at least 4mA flowing in the loop. This means thatif we can power our electronics from the residual 4mA we can have our power supplyAND signal on the same pair of conductors. This technique simplifies installation,especially in large plants, as only a twisted pair is needed to transmit a signal from asensing device to a measuring or control instrument.An instrument which transmits a 4-20mA signal is usually referred to as a TRANSMITTER and if it derives its power from the 4mA residual current it is called a LOOP POWERED TRANSMITTER.The principle of operation is not however immediately obvious to engineers used todealing with voltage signals.The transmitter is a current sinking circuit, which means that it will attempt to draw acurrent from an external power supply. This is usually a 4-20mA signal powered from24V DC which is often an integral part of the measuring instrument to which the transmitter is connected. Unlike voltage transducers which are wired in parallel to measuring instruments, the current transmitter is wired in a series circuit.

__________________
Sure Answers Always
Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); nick name (1); nikunjjain (1); PWSlack (1); user-deleted-1105 (1); Vinu_Answers (1)

Previous in Forum: About ICSS (Information Control and Safety System)   Next in Forum: F&G Devices

Advertisement