Problem with Earth Leakage

12/06/2010 3:54 AM

We're trying to commission an MCC with about 20 motor starters and feeders, all with some form of earth leakage protection. Most of them were tested at the factory, and they worked fine. But now that the MCC is on site, the earth leakage protection doesn't work at all. When you press the "test" button on the relay, the breaker trips, but when you use an earth leakage tester, nothing happens.

We tested the test instrument, and it works.

There's no problem with the wiring. Like I said, in the factory it worked, and we even traced the wires again, just to make sure.

The only remaining possibility that we can think of is that the MCC isn't properly earthed. We will check that today.

Can anyone think of any other possible causes for this very frustrating pain in my behind?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Problem with earth leakage

12/06/2010 3:56 AM

There is no proper earthing.

Register to Reply
Active Contributor

Join Date: Nov 2009
Posts: 12
#2

Re: Problem with earth leakage

12/06/2010 5:02 AM

We're trying to commission an MCC with about 20 motor starters and feeders, all with some form of earth leakage protection. Most of them were tested at the factory, and they worked fine. But now that the MCC is on site, the earth leakage protection doesn't work at all. When you press the "test" button on the relay, the breaker trips, but when you use an earth leakage tester, nothing happens.

dear friend,

this may be due to improper earthing of the panel. please also check the phase sequence of the incoming supply.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Nov 2009
Posts: 12
#3

Re: Problem with earth leakage

12/06/2010 5:54 AM

dear friend,

it may happen due to improper earthing of the panel. please also check the phase sequence of the incoming supply.

Register to Reply
Participant

Join Date: Dec 2010
Posts: 2
#4

Re: Problem with Earth Leakage

12/06/2010 11:31 AM

Found the problem. The NER of the transformer wasn't connected. Somehow we failed to check that before energizing the transformer. Scary...

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Problem with Earth Leakage

12/06/2010 1:21 PM

Add the check to the test procedure, ready for next time, lest the next incumbent should forget as well.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#6
In reply to #4

Re: Problem with Earth Leakage

12/06/2010 1:40 PM

NER= Neutral Earthing Resistor??