Hairline Cracks in RC Slab

03/25/2007 10:45 AM

I have a 28cm thk. solid rc slab with spans of around 8meter. I have noticed that there some hairline cracks appearing in the bottom of the slabs running straight in the middle of the span. I had just casted the slabs 4 months ago and still having its own weight as a load. The slabs is intended for two floor basment. I Have this cracks investigated by coring and had found out some of them are around 10cm deep inside. I had checked the strength of my concrete and is satisfactory at around 28mpa. Made some loading test also at its design loadings of around 1500kg/sq.M and had past the maximum deflection (4mm against 6.75mm ) as per ACI Code criteria although the deflection recovery came at around 70% only less 5 % of the code criteria. Anyhow it is waived as per the code says. I was still monitoring if this cracks will propagate and fortunately not until now. My question is what are the possible causes of this cracks? Is it dangerous structurally?

thanks for your replies.

ramil

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Hairline Cracks in RC Slab

03/25/2007 10:46 PM

You have not stated width of slabs or what reo you have used.and if there are any strenthening beams.

as for the concrete I would have used 40 mpa, what you have stated is what we use as driveways in Australia

Alf Arnold Be Mba.

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#2

Re: Hairline Cracks in RC Slab

03/25/2007 11:05 PM

Is it dangerous structurally?

Not at all. You are carrying a 28cm RC slab x8m span.

ITS SELF WEIGHT IS 700kGF/m2 already!

Fine Cracks at bottom centre only means that the steel is almost at the kink of the (yield point)--linear Stress-Strain Curve.

You still can go to double the loading upstairs on this slab with live/dead loads.

Register to Reply
Guru
Canada - Member - Toronto, Ontario (South Parkdale On The Lakeshore) Engineering Fields - Marine Engineering - Great Lakes School Of Marine Technology (Owen Sound and Port Colbourne) Technical Fields - Architecture - Private Practice 1976-1990 Technical Fields - Education - Toronto Teachers' College 1971 Technical Fields - Marketing/Advertising - Founding Member Hobbies - Hunting - Founding Member Hobbies - Target Shooting - Founding Member

Join Date: Mar 2006
Location: Toronto Ontario Canada
Posts: 1265
Good Answers: 14
#3

Re: Hairline Cracks in RC Slab

03/26/2007 5:15 AM

Ramil

The structural danger is obviously related to the bearing surfaces and styles of support being provided to the floors between the cracks. You may have to calculate for additional columns and support members if the slabs are off-ground. Mesh is not a support consideration, only a strengthening strategy.

Cracking is a universal problem caused by shrinkage during the curing process, and usually avoided by pouring in smaller contained and supported surfaces. Large surfaces are sometimes saved from cracking by the addition of CO2 during the curing process, I'm told. Also check out the sites of various pozzolan provider companies to see what's new in that area.

When I laid a large concrete surface on ground, I had it deliberately cut into smaller areas, and the cuts sealed with epoxy to provide a smooth surface and expansion joints. The cuts did not go all the way through the floor, since it was expected to crack along the lines of the cuts as the places of least resistance anyway.

Mark

Register to Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#6
In reply to #3

Re: Hairline Cracks in RC Slab

03/26/2007 3:15 PM

Cracks way be formed when the curing process happens too quickly. It is more likely to happen with a higher ambient temperature. Generally any temperature above 75 deg F or 22 deg C would benefit with cooling to slow the curing process. While building bridges, above these temperatures, we would typically hose down (cover with water) the concrete every hour for the first 48 hours after it has set.

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Anonymous Poster
#4

Re: Hairline Cracks in RC Slab

03/26/2007 9:59 AM

What's the width of the slab? Is the crack running in the main rebars direction or along the secondary bars? Probably the temporary formwork support was removed before the concrete achieved its required strength for self support. Another possibility is the position of the bottom bars may be too high i.e too much concrete cover. All this need to be checked.

Anyway, you have to seal the 10cm deep cracks with epoxy resin injection to prevent corrosion to the rebars.

Whether it is safe or not should be determined by a professional Engineer after evaluating all the design parameters. Of interest would be whether the rebars was designed correctly, and then, was it placed accordingly. Make sure to check position of the rebars as it affects the slab capacity tremendously, especially the bottom bars. Then look into the concrete strength. You mention that the strength is around 28mpa. I am not sure how that value was obtained. Is it insitu strength i.e. from core samples or is it based on the cube test records during the construction stage? If it is from the cube test samples, then you will still need to take core samples for compressive strength testing to determine the insitu strength. After getting all this datas, then only you can evaluate whether the slab is safe or not.

Cheers.

Register to Reply
Power-User

Join Date: Nov 2005
Posts: 101
Good Answers: 9
#5

Re: Hairline Cracks in RC Slab

03/26/2007 10:15 AM

You need to provide reinforcement information. If the reinforcement is properly designed there may not be any concerns at all.

Register to Reply
Anonymous Poster
#7

Re: Hairline Cracks in RC Slab

06/04/2007 5:33 AM

leneiar cracks are indicative of structural defects but there are other reasons which can cause this it can be due to exothermic reaction due to imbibed quick setting chemicals or any other additives in concrete also if calcium content is more the reinforcemts can also contribute to this if they are corroded which may not be the case with you (reinforcement can swell due to corrosion and can cause cracks when concrete is in green or grey stage) last and least thing to think is due to bending movement

remedy can be cut a v groove of about 2 inch and pour only epoxy resin and top it with 100 mesh sewed sand and allow it to be like that ofcourse you can clad it later with flooring materials

Register to Reply