Ingenious Isolation ! ! ! !

12/22/2010 7:15 AM

A while ago I posted a link to http://www.hts-homepage.de/Klingerpark/Klinger1.html I was having another look though it and spotted this.

What a way to isolate something, wooden wedges!

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Musician - New Member Australia - Member - Torn and breading Engineering Fields - Nanoengineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: Jun 2006
Location: Magnetic Island, Queensland, Australia
Posts: 3721
Good Answers: 74
#1

Re: Ingenious Isolation ! ! ! !

12/22/2010 7:24 AM

Horses for courses. Wonderful solution at the time.

GA= Good Alternative

__________________
The Twain Has Met
Register to Reply
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#2

Re: Ingenious Isolation ! ! ! !

12/22/2010 10:40 AM

How about throwing the switch in the trash and putting in a proper unit that meets current code before someone gets killed.

Register to Reply Score 2 for Off Topic
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#4
In reply to #2

Re: Ingenious Isolation ! ! ! !

12/22/2010 2:06 PM

No a better idea is to get the apprentices to polish off the verdegris, on that lovely brass..

Make it look real nice

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Ingenious Isolation ! ! ! !

12/22/2010 1:51 PM

....and at the perfect height for crawling toddlers.

__________________
jack of all trades
Register to Reply Score 1 for Off Topic
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#5

Re: Ingenious Isolation ! ! ! !

12/22/2010 3:04 PM

Much of the old designs and technologies relied far more on common sense and paying attention to whats around you than actual purpose built safety measures.

It was typically seen as if you where stupid or careless enough to grab onto the exposed wiring you where clearly in need of replacement anyway.

Clean up in isles 6,7,8, and 9! Waldo insisted on wearing his fashionably long scarf at work toady while attending the 1000 Hp open flywheel and gear drive engines.

Oh ya and put an ad in tomorrows paper that we need a new maintenance tech too.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #5

Re: Ingenious Isolation ! ! ! !

12/22/2010 3:21 PM

Hmm - like riding a horse! (thanks, Ky - post #1)

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7
In reply to #5

Re: Ingenious Isolation ! ! ! !

12/23/2010 3:40 AM

GA... when I started as an electrical apprentice in the local steel works, it was drummed into me.. keep you hands in your pockets until you need to work on something, then check its dead before you do!

I remember walking into a switchroom FULL of these knife isolators in the older parts of the steel works, and these were still in use right up until the day it was demolished.

All we needed was a sign.. LIVE EQUIPMENT.

That did it for me, and several decades later, I'm still here :)

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#8

Re: Ingenious Isolation ! ! ! !

12/23/2010 3:47 AM

anyone following this posting should click on the link from TonyS and take the tour... there are photos of equipment I've not seen for years, and if you can read German even better.

I'm sure there is a circuit diagram for a mercury arc rectifier. Not seen one of those since '82...

Ahh.. memories!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#9
In reply to #8

Re: Ingenious Isolation ! ! ! !

12/23/2010 4:02 AM

I saw this

which oddly enough is not unlike the latest multi-pole alternators in 'gearbox free' wind turbines.

Hey Tony - 'old ways' are worth understanding!

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#17
In reply to #9

Re: Ingenious Isolation ! ! ! !

12/23/2010 5:40 PM

There was one bit of kit we had while I was an apprentice I could never get my head around, the rorary converter. Starting it was a black art. You could run it up to speed two ways.
A/ starting with the pony motor and then switch to synconous followed by paraleling with the DC system.
B/ starting with DC and then synconising with the AC system.

Method A was the safest.
It was a wonderful bit of kit but it scared the life out of me. We also had MAR's feeding in to the same system, they facinated me.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#18
In reply to #17

Re: Ingenious Isolation ! ! ! !

12/23/2010 6:04 PM

There was a rotary converter that ran military radios and what not, in the days of valves (vacuum tubes), that gave the span of voltages out of 24 or 12 Vdc. "Neat" you would say back then, "only (about) 9" diameter and 20" long, and 50 lbs!"

Probably worth around 150W, but lots and lots of short circuit current available in a rotating mass. (insert fear emoticon here)

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#26
In reply to #18

Re: Ingenious Isolation ! ! ! !

12/23/2010 10:32 PM

Our 220V DC system had 100KW MAR's and 200KW rotary converters so a bit of a flash and bang if the sycronising was out.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#28
In reply to #17

Re: Ingenious Isolation ! ! ! !

12/24/2010 6:02 AM

At Westinghouse we had a 70kVA WWII 50/60Hz synchronous rotary converter in the test shop which kept the maintenance guys pretty busy. It had been updated with electronic controls for the exciter and when I was there they tried a soft start system - unsuccessfully. I had to investigate this.

The set drew approx 100A per phase under load, but as one would expect peaked at 900A starting off load. This peak did not blow the 100A rewireable fuses. The soft start was initially set low which just blew the fuses. Turning it up not only blew the fuses but partially melted the ceramic carriers as well. It turned out the set was so stiff that it could not me made to move with anything less than 300A, but it drew this current for so long it was damaging the installation. In the end we just gave it up as a bad job starting it with the fusebox switch, the 900A peak being the lesser evil.

Register to Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#10
In reply to #8

Re: Ingenious Isolation ! ! ! !

12/23/2010 6:45 AM

Mercury arc rectifier - imagine my surprise as a young engineer to see those still around in 1990! They were all phased out in 1991. If I recall, there were two pots in series, to make one 12-pulse 3kV, 3MW traction rectifier. All sorts of vacuum pumps, gauges, back-flash detectors, exciter/energising? circuit, etc. http://www.electricstuff.co.uk/mar.gif

And in line with the topic of discussion - all the 400V AC power & 110V DC control busbars and wires were accessible from the open rear of the cabinet. No-one got injured, not even the illiterate assistants, they were taught well (and we were lucky!). New panels much safer, but a pain to work in due to the small size!

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#13
In reply to #10

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:06 AM

MAR's.. we had hundreds of them in the steel works as all the OH cranes were DC. I hated doing the maintenance on them.

But not a lot of people know about them...

__________________
The square root of nothing is what you make it!
Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#15
In reply to #13

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:38 AM

In 1984/85 I was working at Westinghouse where we were building solid state rectifiers for London and Glasgow Underground traction supplies. These were replacing mercury arc units. I believe mercury arc rectifiers were still being used in traction supplies into the 90's. I think the London Underground had 6 phase rectifiers whereas the Glasgow Underground had 12 phase rectifiers when (at least when it was rebuilt). However it was some time ago and my memory may not be accurate.

The mercury arc system lent itself to building multiphase rectifiers without using additional components.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11

Re: Ingenious Isolation ! ! ! !

12/23/2010 6:55 AM

Before RN ships were built to the NATO 440VAC 3 Ph. standard, they were open faced 220VDC switchboards, with only a guardrail between you and the open switchgear.

The switchgear on frigates and destroyers looked a lot like this picture......so called "Tree System" distribution. Only Aircraft carriers used a giant "Ring Main" 220VDC system with mostly closed switchgear......

Due to the "knockoff" effects of DC at that potential, I actually never heard of anyone getting killed on them, though I know of several people with burns and "arc eye" for being stupid. (I am sure that there were some fatal accidents, but very, very seldom! I could not find any RN statistics on the web.....)

The NATO standard changed that radically, the first ship built using it was a Daring Class destroyer of the 50's which killed many people till the switchboards were finally boxed in properly.......

Marked as Off Topic as it probably mostly is!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#12
In reply to #11

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:00 AM

Actually.. very on topic.. its good to know that I'm not the only one who remembers open panels with the equipment fixed to the front of Bakelite panels with the wiring all open and exposed at the back.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#14

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:16 AM

and for a further trip down memory lane...

Note the Wipp & Bourne hand isolators bottom right of photo.

I'm getting all weepie...

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#16

Re: Ingenious Isolation ! ! ! !

12/23/2010 3:42 PM

I am sure that many of us who started our apprenticeships in maintenance back in the 60/70s remember such gear.

I did and this thread is like a walk down memory lane...

This was a rotogravure printing plant built in the 40s and modernized by the addition of new stuff in the 60s and 70s. We had...

Six phase MARs running 400 HP DC motors turning printing presses.

Old C-H wound rotor drives, three motors on the same press shaft, so we had ganged motor driven vertical wound rotor controllers with "shorting trucks" that ran up and down between brass bars on worm screws. All three towers shuttles were tied together with common drive shafts and clutches on them. This get up had a 1.5 HP motor that turned the shafts that turned the worm screws that lifted the shorting trucks. There was a whole room full of plate resistors. The heat in the summer was wild.

Great big huge "blue glow" thyratron's" that ran 25 HP motors on paper reel stands.

Whole rooms filled with open motor controls and the associated wiring and knife switches mounted on phenolic/slate backboards. Beautiful wire work. Wish I had pictures...

The wildest... was an explosion proof 500 HP "Star/Delta" oil bath manual starter. Took two of us to throw the "arm" from "start" to "run" mode.

This plant was a 230 volt delta corner grounded facility, so EVERYTHING was huge.

You should have seen the size of the contactor on the old hydraulic elevator, each phase contact was a silver puck of about 3" diameter. The arm on the starter was about 2.5 feet wide.

I miss the printing plant to this day...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#19

Re: Ingenious Isolation ! ! ! !

12/23/2010 6:27 PM

There was one beauty of the old systems, you could repair them. I wonder how many maiteance guys cary a file with them now for dressing contacts. When I moved from quarrying to the steel industry the young "lads" thought I was mad when I'd dress live slip-ringss or a comutator with a Martindale stone. It saved changing motors though.

Happy times

__________________
The reports of my death are greatly exaggerated.
Register to Reply
3
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#22
In reply to #19

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:47 PM

Your comment reminds me: not so long ago I was 'gifted' quite a modern and expensive machine, due to continual performance and service cost issues.

I removed the staple (obviously by which a part ticket was previously attached) from the rubber anti vibration bearing cup, re-machined the oval commutator, and it has run faultlessly ever since.

I think one can actually do quite well, in an impatient throwaway society, by knowing how things work, how they are made/produced, so how to 'correctly re-make' them.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#20

Re: Ingenious Isolation ! ! ! !

12/23/2010 6:50 PM

lets be real honest to each other... we're all old farts!!

Yeah, yeah.. I know speak for ya self!! :)

__________________
The square root of nothing is what you make it!
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#23
In reply to #20

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:50 PM

I'm not sure age (ours, or the gear) has that bigger bearing - just length and breadth of learning might infer 'more calender years'.

How about "experienced farts"

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#27
In reply to #23

Re: Ingenious Isolation ! ! ! !

12/24/2010 2:05 AM

"Experienced" old farts it is!!

Have a great Christmas everyone.

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#21

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:42 PM

At my uncle's fertilizer plant was a pretty big hammer-mill, 60hp at least. It was my job to start it, using a large start/run switch. It was quite the thrill to go to start and hear the hammers rattling about, and then go to run when they flung out and got quieter. It gave us a pretty good feel on the speed of the motor, and made it easy to learn when to make the change.

__________________
mike k
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#24
In reply to #21

Re: Ingenious Isolation ! ! ! !

12/23/2010 7:51 PM

Um - I wonder if that was a star/delta starter

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#29
In reply to #24

Re: Ingenious Isolation ! ! ! !

12/24/2010 1:18 PM

Gee, I dunno. It took both hands to move the switch up for start, then down through the middle to run. The hammer-mill was a good twenty feet tall, an awesome piece of machinery.

We were processing leather scraps into high-nitrogen fertilizer, a rather stinky process, as the blow-down tube from the pressure cooker had a leak at a turn.

__________________
mike k
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#25

Re: Ingenious Isolation ! ! ! !

12/23/2010 10:26 PM

11KV RMU incoming switch.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster
#30

Re: Ingenious Isolation ! ! ! !

12/25/2010 11:25 AM

Known as an OLD 3 pole double throw switch. It was made to carry lots of current and probably 3-phase current since 3 switches. Since double pole, has 2 sides to switch 3 single inputs between 2 loads. Of course since it is old it might not carry much current. Seems in the ole days, back in 1920s and before they built every thing big. I guess to make sure it lasted. Being exposed would be considered a safety factor, definitely not UL, but then back long ago safety was not considered much and this is why we got unions. Of course the switch could have been mounted inside a cabinet, but never know. ron

Register to Reply
Power-User

Join Date: Jan 2008
Location: New Hampshire
Posts: 106
Good Answers: 3
#31

Re: Ingenious Isolation ! ! ! !

12/27/2010 9:18 AM

I remember when I started work at a local foundry as an electronic tech in the 70's, we had 2 Brown Brovaries (ya, I know, not spelled right) induction melters. Both were motor/generator sets, both MG's were water cooled, so an ocasional water leak got real interesting. The best one that allways scared the crap out of me, was the panels were missing on the control cabinets and the operators would change capacitor taps by kicking the ceramic contactors with their steel toe boots, and yes, the leather on the steel toes was missing. This cap circuit ran at 3Kv to the induction furnace.

One furnace was small one at 200Kw and the other was a 350Kw. Both had the arm on the side that you had to pull down to start the MG, and then throw the handle to run position. Once in a while, an operator would miss and the switch would destroy the contacts.

I know, I am showing my age!

Jim

__________________
rrnut-2
Register to Reply
Register to Reply 31 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: