Dual Voltage 3 Phase AC Generator

12/29/2010 1:04 PM

hi all,

would you please help me to understand this,

i understand that when i change connection from high to low ''380v to 220v'' on 3 phase dual voltage ac generator, i am making two coils on parallel between each two lines, so they will be two ac 3 phase generators running on parallel excited from the same rotor, and when i connect to high i am making each two coils on series between two lines, thats on dual voltages 6 coils ac generator.

so if its 200kva generator: when its connect on high it can carry 300amps, while when its connected on low it can carry 600amps.

how about when its dual voltage generator with 3 coils only, i mean when its on high it will be star connection while when its on low it will be delta connection, will the amps be different while its on high and low? because when its on high, two coils will be on series. while on low, one coil will be between two line voltages.

hope you got what i mean

thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: dual voltage 3 phase ac generator

12/29/2010 1:17 PM

Power is power... 3 phase kW = V * I * 1.73 * PF / 1000.

For the same amount of delivered power... When you double the voltage you half the current and vice versa... when you half the voltage you double the current.

A genset will deliver 60kW... at 600 volts... kW * 1000 / V * 1.73 * PF = 57 amps (assumes unity PF).

A genset will deliver 60kW... at 300 volts... kW * 1000 / V * 1.73 * PF = 115 amps (assumes unity PF).

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2

Re: dual voltage 3 phase ac generator

12/29/2010 2:14 PM

Recall the relation between line current and phase current in Star as well as Delta circuit.

The current capacity of coil is remains same.

When Coils are connected in Star, The voltage at terminal shall be high i.e. V (line) = Sqrt (3). V (Phase) and Line current would be equal to phase current.

When Coils are connected in Delta , The voltage at terminal shall be low i.e. V (line) = V (Phase) and Line current would be I (line) = Sqrt (3). I (Phase) .

__________________
When was last time you did something for first time.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Dual Voltage 3 Phase AC Generator

12/29/2010 3:03 PM

380/220 is a star-delta combination.

In a series/parallel combination, the high voltage would be twice the low; e.g., 480/240.

__________________