To Tape or Not To Tape?

01/14/2011 10:11 AM

On a NEMA 4 installation, where you have an aluminum housing for a 4-20ma transmitter with 1/2" FNPT threaded access ports and a mini style 5 pin nickel plated brass receptacle in 1/2" MNPT to install in one of the housing ports, must the male threads be teflon taped to achieve the NEMA 4 rating? (the end user will hose wash the device the instrument is mounted on daily)

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: To Tape or Not To Tape?

01/14/2011 11:16 AM

In 31 years of looking around instumentation on process plants of all shapes and sizes in several countries, not a single example of taped threads has occurred on glandings, housings and openings of proprietary instruments.

Is this a case of plumbing practices being applied to instrumentation due to excessive enthusiasm?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9
In reply to #1

Re: To Tape or Not To Tape?

01/14/2011 1:22 PM

See the white area on the threads of the receptacle? Now you've seen taped electrical threads instaled by Rosemount at the customer's request. Welcome to the world of pharmacia.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #9

Re: To Tape or Not To Tape?

01/14/2011 1:33 PM

Where is the equipotential bonding?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: To Tape or Not To Tape?

01/14/2011 11:40 AM

NEMA 4 enclosures are not intended to be water tight. They provide a "degree of protection". Put the fittings on the bottom of the box.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#4
In reply to #2

Re: To Tape or Not To Tape?

01/14/2011 11:47 AM

I should have mentioned this is the weired world of pharmacia. Different rules than the real world.

It's an instrument enclosure which is pre-mounted to the sensor and mounts the way the vendor (Rosemount) intends it to be installed on the piping run.

Doesn't matter - customer still questions it pointed down as about 12 are mounted that way.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #4

Re: To Tape or Not To Tape?

01/14/2011 1:10 PM

The 31 years' observations include eight in primary pharmaceutical manufacturing and two in secondary.

How is intended to earth this equipment for personal protection in the event of a fault - not the cable armour, surely?

Is there anything else the forum needs to know to give a complete answer to this posting?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#11
In reply to #7

Re: To Tape or Not To Tape?

01/14/2011 1:29 PM

See response 10 to response 5 for grounding info and picture submitted above your response.

Sorry I'm short on supplying info. This is signal wiring. Seriously doubt if a fault in a 4-20ma circuit will hurt someone.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #11

Re: To Tape or Not To Tape?

01/14/2011 1:37 PM

Equipotential bonding is there to operate the circuit protective device(s) in the event of a fault.

  • For example, one possible fault is an inadvertent connection between mains power supply live to the instrument loop cables. How do the circuit protective device(s) clear this fault without endangering an operative that just happens to be hosing down the instrument?
  1. Where is the equipotential bonding?
  2. Why is the customer insisting on the threads being sealed? Surely there is no concern about fluids coming out or going in?
  3. Is there a hazardous area consideration that the forum needs to know about?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#17
In reply to #13

Re: To Tape or Not To Tape?

01/14/2011 4:07 PM

Re: "Why is the customer insisting on the threads being sealed? Surely there is no concern about fluids coming out or going in?"

Nema 4 is intended to protect ("to provide a degree of protection") against water:

"NEMA 4 – Enclosures constructed for either indoor or outdoor use to provide a degree of protection to personnel against incidental contact with the enclosed equipment; to provide a degree of protection against falling dirt, rain, sleet, snow, windblown dust, splashing water, and hose-directed water; and that will be undamaged by the external formation of ice on the enclosure."

Presumably, Nema 4 would not have been specified if there was "no concern about fluids going in or coming out".

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: To Tape or Not To Tape?

01/14/2011 11:47 AM

No wonder electrical boxes get full of water.

On the other hand, tape could disrupt the grounding scheme.

(Over to you, Hobson.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
2
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5

Re: To Tape or Not To Tape?

01/14/2011 11:51 AM

On brass fitting they do not need to be taped in any application to get a seal. The brass is soft and malleable enough that it will form to the threads to seal. Would also question the use of teflon or any sealant on electrical applications. Pipe should be grounded these sealants can act as insulators. Failure of a conductor in the raceway may leave the raceway hot and a hazard.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#10
In reply to #5

Re: To Tape or Not To Tape?

01/14/2011 1:26 PM

The receptacle does not ground. A seperate conductor can be run for grounding the instrument if required. Usually the customer does not want the instrument grounded on a pharmaceutical installation, because the process skid ground and the PLC or DCS ground may not be the same and ground loops can occur.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #10

Re: To Tape or Not To Tape?

01/14/2011 1:45 PM

Aaaargh! There is no issue with a clean earth for the instruments and a dirty earth for the power distribution! This is the way that control systems have been done for decades.

The purpose of sealing the threads is unclear. Why bother? What would be implications of doing it? And of not doing it? What does the customer's Engineering Standards say about it (something else the forum hasn't been told yet) and why?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#15
In reply to #14

Re: To Tape or Not To Tape?

01/14/2011 2:22 PM

The electrical engineers of the customer we have in house today for a FAT are the ones asking the question. We have 28 of the receptacles installed on transmitters we supplied for them sans the tape, and one believes the teflon tape is necessary to seal to NEMA 4 and the other has no opinion. They are waiting for someone above them to make the call.

Looking at pictures of past projects we have done, I can find these same model receptacles factory installed on the same model transmitters by Rosemount for customer supplied instruments, one project has transmitters with teflon tape for pharma giant L, and the other has transmitters without tape for pharma giant M. Who is right? I tried Turck, who makes the receptacles, and all they will say is the front portion, ahead of the threads is NEMA 4. From threads to the housing is our problem. Note they put an o-ring on these same receptacles at one time, but have dropped them in the last few years. You can't bury enough threads to hit the o-ring on a tapered thread installation. This lack of depth also eliminates the idea of using a sealing gland like T&B makes for cable glands.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#29
In reply to #15

Re: To Tape or Not To Tape?

01/18/2011 7:27 AM

You need to look better at the NEMA 4 specs. It is not complete a water tight seal. That I believe is more the problem. That the one questioning it believes it is and that is what he is trying to do with the teflon tape.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#30
In reply to #29

Re: To Tape or Not To Tape?

01/18/2011 8:17 AM

Not really - the real problem is this is pharmaceutical, and once a machine is accepted and the very long and tedious validation for the FDA is done, absolutely nothing can ever change without a very long and tedious re-validation. Even a change as small as taping a fitting on an instrument after validation, because it is leaking water, creates a need for re-validation. (wonder why you have to pay so much for medicines and drugs?) On the plus side, this creates guaranteed re-makes of equipment that might wear out, as they can replace with exact duplicates from the original source.

We were told this particular company has a whole plant shut down because they accepted some tanks and skids with minor errors and the process to re-validate the entire lot was more expensive than closing the facility. That is why they are so particular to details such as this.

We currently are FAT testing 14 tanks with a temp and pressure sensor, mixer, and some valves. The cabinets are merely junction boxes for the instrumentation to connect to a plant system via the old method of multiconductor cables. The mixer VFD is also plant mounted, so not part of the test. The test to accept these is going to take 3 weeks with 12 hour days and Saturdays included. (about 200 hours, or 14.25 hours per tank) Pharmaceuticals are that particular because of FDA.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#33
In reply to #30

Re: To Tape or Not To Tape?

01/18/2011 10:17 AM

Ok but if the they required a sealed tight then they should have spec out NEMA 6 or higher. Not NEMA 4. The sealing properties on NEMA 4 is limited. You didn't say what the raceways are they EMT or rigid pipe?

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#34
In reply to #33

Re: To Tape or Not To Tape?

01/18/2011 10:47 AM

No raceways - this is a clean room tank with runs of much less than 3 meters - see picture above in my response, I believe it is 9 or 10. A Turck Eurofast receptacle with 1/2" NPT threads and an attached cable. There is also an issue with the plug on the opposite side un-used entry port to seal to NEMA 4 standards. Turck guarantees the cable and recptacle interface to be NEMA 4, but won't touch the threaded side issue.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#6

Re: To Tape or Not To Tape?

01/14/2011 12:22 PM
__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: To Tape or Not To Tape?

01/14/2011 1:15 PM

More plumbing stuff....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#22
In reply to #6

Re: To Tape or Not To Tape?

01/15/2011 8:05 AM

Welllll - Did I mention this is for pharma use? - FDA approved goop only.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Participant

Join Date: Jan 2011
Posts: 2
#24
In reply to #22

Re: To Tape or Not To Tape?

01/15/2011 8:50 PM

As an alternate to tape,use Dow Corning 111 instead. I have use this compound on these fittings for ease in removing them later. This is great product for industrial use. This compound is used on the main valve for industrial water softeners that comes in contact with the water supply. It is also great for lubricating o-rings. I have used this product on many types of applications that are exposed to elements for over 30 years. Owe, this is a very safe product to handle.

Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16

Re: To Tape or Not To Tape?

01/14/2011 3:58 PM

NEMA 4 is not an enforceable standard and even as such, never had anything to do with threaded fittings. Only the enclosure manufacturer is therefore going to be able to give you a definitive answer to that specific question. Taping or doping of joints is a plumbing specification necessary for attaining a pressure seal specification. The NEMA 4 standard was all about hose directed water at 100 GPM from any angle, it was never a pressure specification. NEMA testing and ratings have however been taken over by UL, so you would refer to it as UL type 4.

If a Type 4 rated enclosure with threaded hubs passed Type 4 tests without tape, then tape is not necessary. Ff the manufacturer taped the threads when they tested, then tape is necessary. Only they can tell you what they did.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#18
In reply to #16

Re: To Tape or Not To Tape?

01/14/2011 4:23 PM

As I mentioned in response 15, the manufacturer sells them with the same receptacles facory installed as an option in both versions. We never have received taped ones when we order the standard option for the mini receptacle from them. I suspect the client who sends us the taped ones requested them that way and it is a non-standard issue. (I know the money they spend/project with Emerson (Rosemount), so they can get whatever they want)

This, to me, would imply if the manufacturer will sell them as NEMA 4 with un-taped receptacles, they must have tested them that way.

This is just an exercise by myself to let off steam - in the end we will do what ever the customer wants even if it is not a legitimate request.

Want to hear about cutting open every completed and installed cable to prove which drain wire for the shield goes with which twisted pair in a cable with 4 sets of twisted pairs, where the pairs are all foil wrapped and touching each other?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#19

Re: To Tape or Not To Tape?

01/14/2011 4:41 PM

Having many years of food manufacturing experience from an electrical perspective, while perhaps not as anally retentive as the pharmaceutical folks, the interest was pretty much the same...

The transmitter is bonded through the installed sanitary grade piping. As such the equipotential ground plane is assured.

I would not have taped this fitting. If water ingress is of concern, one of the things we often did, was to coat the threads on such a fitting with a high temperature anti- seize product made by Locktight. The Locktight product was conductive and provided an additional barrier to water penetration.

In fact... on some sensors on a food powder handling system consisting of Teflon components, the sensors routinely died from being drowned during a sanitation cycle. Silicone and tape was tried, the problem then was... static buildup on the sensor body due to the body not being bonded to ground. The Locktight product solved the problem as it bonded the body of the sensor and provided the required water barrier. As a bonus... fitting removal was much easier when sensor replacement was required.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#20
In reply to #19

Re: To Tape or Not To Tape?

01/14/2011 5:06 PM

Pharma is a bit tougher - we can't use the anti-seize grease you mention.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#21

Re: To Tape or Not To Tape?

01/14/2011 11:37 PM

Huh...

There is no real debate until you know what the mfr did when testing and listing the devices. Sounds to me as though they probably listed it without tape, most do because as I said, it's not about a pressure seal. Adding tape probably does not violate the Type 4 listing however, because it would be considered an enhancement to the procedure. Either that or they are not sweating the details by taping them on request.

I should add that personally, I sometimes tape the fittings if I know there is a possible corrosion issue because I find that teflon tape makes it easier to remove connections later. I used to do a lot of NEMA 4X stainless steel enclosured control panels for a food machinery OEM where the use was around spice dispensing. Many spices are highly corrosive,if we didn't use teflon tape it was impossible to remove conduits after 2-3 months. Our UL inspector never questioned it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Sep 2009
Location: Wilmington, NC
Posts: 140
Good Answers: 8
#23

Re: To Tape or Not To Tape?

01/15/2011 11:20 AM

Apply the tape ONLY to the last few threads of engagement (those farthest from the lead tip of the threaded piece). 1. full mechanical/electrical engagement 2. full seal 3. looks as required 4. aids in future disassembly

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#25

Re: To Tape or Not To Tape?

01/16/2011 1:54 PM

Use of tape just doesn't seem right. From my limited experience in the pharmaceutical industry the point of the seal is to prevent contamination (hence special limited or no use of sealants), and tape is not allowed due to the fact that it can wear and contaminate the environment when the threaded connection is loosened and tightened repeatedly.

The use of tape seems strange, almost someones idea of providing a seal with something other than silicon sealant which is not allowed (has the customer approved this). NEMA 4 has an equivalent IP rating of IP66, does the transmitter have an IP rating of at least IP66?

If not, perhaps the use of an approved sealant would be better. I don't know what the standards say but the pharmaceutical industry site designers/engineers are generally good at telling you exactly what you can and cannot use in this case.

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#26
In reply to #25

Re: To Tape or Not To Tape?

01/17/2011 8:11 AM

Teflon tape is used all the time by major pharmaceutical companies, but not always on electronic installations. We have built equipment by most of them. Try as you might, there is usually some device not made with sanitary fittings and the threads on that get teflon taped. Never pipe doped, just taped. See response #9 by myself and note the required teflon tape on the transmitter by a huge pharmaceutical company. They supplied this transmitter and had the tape installed by Rosemount's distributor.

Yes the transmitter is NEMA 4 and my argument to our customer is we have received them on past projects with Rosemount factory installed receptacles sans the tape, so this application should not require tape to meet NEMA 4. (I am looking at un-wiring and re-installing 28 receptacles if the tape is needed - oh, and then the customer would have to do all electrical tests over that involve these instruments and yes they would take the extra day or two to do just that)

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#27

Re: To Tape or Not To Tape?

01/17/2011 8:46 AM

An ideal solution to this would be an electrically conductive pipe thread sealant. I don't know if any of the Loc-Tite or other products do this. If so, there could be a decent specialty market.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#28
In reply to #27

Re: To Tape or Not To Tape?

01/17/2011 9:42 AM

Conductive is not necessary - as stated above, the receptacles by Turck do not connect ground through the body - ground is only by wire. Many pharmas do not want the equipment ground connected to their DCS instrumentation system.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#31

Re: To Tape or Not To Tape?

01/18/2011 9:17 AM

I guess after reading all the postings on this subject... this comes down to two factors only.

1) Your customer wants it done, and...

2) The FDA will allow it.

If both factors are true, then tape the joints.

There is no electrical issue, with respect to the body of the transmitter being bonded to ground, as it is bonded through the stainless piping.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#32
In reply to #31

Re: To Tape or Not To Tape?

01/18/2011 10:16 AM

Maybe. The inspecting engineers are not sure if the tape is necessary or not. To tape now requires removing 28 receptacles and rewiring. Then retesting all electrical tests involving the 28 instruments affected. I suspect that since we are 8 days into the process and all electrical testing is done, just mechanical remains, that the taping may be over looked if we prove that Rosemount tested without taping the threads.

I've been a bit chicken to call them in fear they will recommend taping.

The most likely scenario is they will take the same position as Turck on NEMA 4 - that is our problem to assure sealing to the standard, not theirs, as the liability issue arises in a large way with a pharmaceutical installation. Lose one batch and you are out hundreds of thousands of dollars.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#35

Re: To Tape or Not To Tape?

01/20/2011 12:05 PM

Final outcome - we had to pull all receptacles and put teflon tape on the threads.

The one instrument had a "live" feed in one side (not disconnectable through a plug and receptacle) through a cable gland made of nylon. No tape required on that. I thought it most interesting who made that call. It was neither of the EE's at our site, but the Documentation/Validation Engineer that made the final call for tape on metal threads but not on plastic threads.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Register to Reply 35 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jack of all trades (1); JRaef (2); lyn (1); mog (1); North of 60 (2); ozzb (3); Phys (14); PWSlack (6); RDGRNR (1); RFincke (1); rhkramer (1); Tornado (2)

Previous in Forum: Use of Resistors?   Next in Forum: Project Searching

Advertisement