Filtration of Cooling Tower Water

01/17/2011 2:24 AM

We are using cooling towers for machine cooling. Cooled water header is running across shop floor and connections are taken from header to individual machines.

PROBLEM - Cooling towers attract lot of dust particles from atmosphere which settles in pipe lines where flow rates reduce. What method should be adopted to filtration of water of cooling tower. Most of the people suggest side stream filtration. Problem here is that it cannot ensure 100% filtration by concept and effectiveness of filtration could be low to 70% also. In case of inline filtration, there are certain obvious issues - pressure drop across the filter should be given proper attention while desigining, too frequent choking of filters specially in dusty environment and high cost of filter. Can any one suggest what are new trends in filtration of cooling tower water. Adding of coagulants like alum before filter unit can also help.

__________________
Sangeet Kumar Jain
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Filtration of cooling tower water

01/17/2011 3:09 AM

One thing that might help is a closed-circuit evaporative-cooled tower. Then the machine cooling water would not be exposed to atmospheric dust. The cooling tower water would still have this issue, but it wouldn't be as sensitive. Side-stream filtration would then be suitable. Because of the interposing heat exchange step (about 15°F difference), the tower would be somewhat larger.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#13
In reply to #1

Re: Filtration of cooling tower water

01/18/2011 12:13 PM

Agreed.

Plate - Frame heat exchanger, http://chemicalengineeringspot.blogspot.com/2008/11/plate-and-frame-heat-exchangers.html

Dolphin - water treatment system - not chemical http://www.clearwater-dolphin.com/

Monthly blow downs out of tower strainer basket.

That should do it!

__________________
To be or not to be........ok that's a trick question.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Filtration of cooling tower water

01/17/2011 5:16 AM

Please describe the current cooling water treatment regime.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Aug 2009
Posts: 21
#3

Re: Filtration of Cooling Tower Water

01/17/2011 6:32 PM

Full flow centrifugal separator(s) are good but must be sized properly and located where the flow rate is fairly constant.

Is the water open to the atmosphere at the individual machines with gravity flow? You could use bag filter material to catch solids. Perhaps cycle between multiple bags for uninterupted flow. If a single bag fills up, it will just overflow without compromising flow.

Avoid oversized piping and provide a large sump/settling tank?

While not perfect, side stream filtration will help.

Register to Reply
Active Contributor

Join Date: Sep 2010
Posts: 22
#4

Re: Filtration of Cooling Tower Water

01/17/2011 10:49 PM

Side stream filtration. These are self-cleaning type so would be less of a hassle for maintenance. I would think that bag filters will choke very easily and replacement costs (for bags) may render it uneconomical.

__________________
"Engineers simplify complex problems, and scientists vice versa."
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#5

Re: Filtration of Cooling Tower Water

01/17/2011 11:42 PM

Installation of sand or carbon filters which is used in water treatment plants shall be considered. Regular draining and cleaning of the cooling tower basin will reduce the scale formation.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Filtration of Cooling Tower Water

01/18/2011 3:31 AM

Carbon filters are for the removal of organics and chlorine. The OP has a problem with solids. Carbon filters are not suitable for the removal of solids. Further, being catalytically active, they might interfere with the OP's existing cooling water dosing regime.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#9
In reply to #8

Re: Filtration of Cooling Tower Water

01/18/2011 5:05 AM

Thanks Sir. I have suggested general methods used in water treatment plant like R.O Plant. I agree with your comments that carbon filters may pose problem with the Ops system.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #9

Re: Filtration of Cooling Tower Water

01/18/2011 9:27 AM

<...Sir...>

How abstruse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2010
Location: Chennai India
Posts: 20
#6

Re: Filtration of Cooling Tower Water

01/18/2011 1:11 AM

The cooling tower by virtue of its function picks up dust and water needs to bleed off from the tower to keep the concentration of the solid particles.

It is necessary to have double fitration at the outlet of cooling tower so that your machines get relatively clear water. It would be better to provide individual stariners also atthe entry point of each load wharer the cooling water is circulated.You may get some chemicals added to keep the dust in collaidal form which can be removed.You try contacting VASU Chemicals who are specialized in treating the cooling water.

__________________
enervac
Register to Reply
Member

Join Date: Nov 2009
Location: Gurgaon, India
Posts: 8
#10
In reply to #6

Re: Filtration of Cooling Tower Water

01/18/2011 6:18 AM

Thanks dear enervac. I called up Vasu Chemicals person. They are suggesting use of dispersantswhich will not allow suspended impurities to settle in the system and will be removed from the system through regular blowdowns.

I think I should give it a try. I am studying MSDS and other relevant information.

__________________
Sangeet Kumar Jain
Register to Reply
Associate
India - Member - New Member

Join Date: Dec 2006
Location: Ahmedabad, Gujarat State, India
Posts: 32
#14
In reply to #10

Re: Filtration of Cooling Tower Water

01/19/2011 12:41 AM

Dear Sangeetkumar,

All process cooling water circulation is riddled with clogging of supply lines to machines. Marble sawing is a perfect example. If you need your supply arteries without clogging a bit, filtration is the only solution.

I have my patented vacuum filtration technology for continuous recycling of process water in a closed system removing solid particles without letting them accumulate in the system. you can refer to Indian Patent # 208362 on the Patent department's net portal.

If you find it useful, contact me with a pm Mahess

Register to Reply
Participant

Join Date: Jan 2011
Location: Aurangabad
Posts: 1
#7

Re: Filtration of Cooling Tower Water

01/18/2011 1:38 AM

Are you use baccomber in your cooling tower it protects the scale formation.... clean the stainer filters regularly.

Register to Reply
2
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11

Re: Filtration of Cooling Tower Water

01/18/2011 8:02 AM

You can use a sand filtration system with a backwash facility. If the pressure drop is critical, i.e. you need the pressure to be higher than what a sand filter can allow (maybe > 2bar), you could have an additional tank where the filtered water will be collected before circulating to your machines, using a different, appropriate pump. The cooling tower tank can be just enough as an intermediate tank.

On the long run, more economical: Backwash can be done automatically, no need to change the elements, easy to maintain. It will filter most of the dust and debris brought in by the air...

Register to Reply Good Answer (Score 2)
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

DonDavis (1); enervac (1); LAA_Lucke (1); Mahess Desai (1); mrswamy (2); nikhil.joshi (1); pjquek (1); PWSlack (3); sangeetkumarjain (1); Stedou73ish (1); Tornado (1)

Previous in Forum: Lowest Life Cycle Cost for Pumping Systems   Next in Forum: Hydraulic Oil Filtration

Advertisement