Inrush Current Time of Squirral Cage Motor

01/23/2011 8:18 AM

how many cycle will the inrush current lasts when motor starts at DOL. do anyone have graph of inrush transient? can any factor influence this time?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Inrush current time of squirral cage motor

01/23/2011 8:31 AM

The inertia of the load affects inrush time.

  • If the motor had no load, then it would come up to speed quickly, and the inrush current would start to fall off after only a few cycles.
  • If the motor were driving a shaft with a dirty-great-flywheel on it, then the fall-off point could be many tens of cycles away from the energise time.

So, without knowing what the motor is coupled to, it is impossible to say.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Anonymous Poster
#3
In reply to #1

Re: Inrush current time of squirral cage motor

01/23/2011 9:05 AM

ok.. suppose it is connected with load. so tell me how many cycle will it lasts?

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #3

Re: Inrush current time of squirral cage motor

01/23/2011 4:08 PM

Please refer to the final sentence in #1.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: May 2010
Posts: 570
Good Answers: 55
#9
In reply to #3

Re: Inrush current time of squirral cage motor

01/23/2011 10:23 PM

Light load. 2 seconds. About a 100 - 120 cycles.

Heavy load. 5 seconds. About 150 - 300 cycles.

__________________
Si hoc signum legere potes, operis boni in rebus Latinis alacribus et fructuosis potiri potes!
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Inrush Current Time of Squirral Cage Motor

01/23/2011 9:05 AM

What do you mean by: "how many cycle"? Do you mean 50/60 Hz "cycle", or revolutions of the motor shaft "cycle"?

Reply
Anonymous Poster
#5
In reply to #2

Re: Inrush Current Time of Squirral Cage Motor

01/23/2011 9:23 AM

cycles of 50Hz supply...

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Inrush Current Time of Squirral Cage Motor

01/23/2011 9:08 AM

This isn't going to be easy.

Bye bye.

Reply
Anonymous Poster
#12
In reply to #4

Re: Inrush Current Time of Squirral Cage Motor

01/24/2011 7:39 AM

What, you could not manage to google the answer - yeah I guess that must constitute something not easy.

Bye bye

Reply Score 1 for Off Topic
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6

Re: Inrush Current Time of Squirral Cage Motor

01/23/2011 9:59 AM

Is the question for motor inrush current or motor starting current (they have different meanings)?

These threads, including the reference links, may help.

http://cr4.globalspec.com/thread/60035/Induction-Motor-Inrush-Current-vs-Locked-Rotor-Current

http://cr4.globalspec.com/thread/42981/Starting-Torque-of-a-Motor

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#7

Re: Inrush Current Time of Squirral Cage Motor

01/23/2011 12:46 PM

This is a typical torque-speed curve.

The equation is J*dω/dt= M-Mresistant where ω is the rotational speed, M is the motor torque and M resistant is the resistance the motor has from the load.

As you see the value of M is function of ω and the resistant torque is also function of speed (ω or even ω² as in fans or pumps) and/or angle. This makes an answer quite difficult if no information about the load is available.

In the case of loadless start the whole torque (less internal frictions, very small in modern motors) is used only for acceleration so that the functional zone at the right end of the graph is very soon reached.

Reply
Anonymous Poster
#10
In reply to #7

Re: Inrush Current Time of Squirral Cage Motor

01/24/2011 12:01 AM

As the fellows said before: it takes as long as it takes. You can measure it in your setup.

In the meantime: goodbye.

Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#11
In reply to #10

Re: Inrush Current Time of Squirral Cage Motor

01/24/2011 2:45 AM

If the load and motor are not chosen the right way then you can also measure a burned coil! It is better when you can estimate the time before assembly and measurements. But one has to know how to do it and unfortunately not many master it.

Reply
Anonymous Poster
#13

Re: Inrush Current Time of Squirral Cage Motor

01/24/2011 7:54 AM

why are you concerned with inrush on a motor, I am currently trying to figure the thyristor value on a samsung projection tv, the inrush limiter has a strange number on it, samsuck wants me to by a primary board from them, mouser elect had the bracket value thyristors for .90c a piece so I bought four of different values since the tv is 43 miles away, now I will see if I can measure resistance value of the one that blew the solder from circuit and replace, the tv is friends or I would not be trying to fix, anyhoo the unrush circuit for it is for a reason to bring the cold side up without shock trauma, a squr cage motor does not have this sensativity, I would like to hear from others why this circuit yoyr trying is needed,

Sinc
Mitch ret peugeot mech

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14

Re: Inrush Current Time of Squirral Cage Motor

01/24/2011 2:09 PM
  1. Post #6 is correct. Like any inductor switched onto an AC supply, a motor stator winding draws a current which depends on the point in the voltage wave at which it is connected.
  2. Worst point is zero volts. The fundamental law, back-emf voltage = N x rate of change of flux (N= no. of turns, flux = that coupled with the winding) governs. Back emf = supply voltage less any resistance drops.
  3. Doubling of the normal on-load peak flux occurs at 2. - this causes saturation and currents which can be very high because only leakage inductance and resistance limit current. N.B. Leakage inductance is inductance of winding without iron core.
  4. When there is a remanent magnetization of the core, flux can be more than doubled, because core is even closer to saturation when energized.
  5. On a 3 ph motor, there is always one phase which hits a bad point on wave when switched on!
  6. Locked rotor and starting currents are a different issue. The starting current duration and shape depends on the load inertia and drive torque at below rated speed.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#15

Re: Inrush Current Time of Squirral Cage Motor

01/25/2011 6:06 AM

Please look at posts #6 & #14. The factors that affect the time that the magnetising current takes to die down to normal steady state are the damping from resistance and the magnetic core losses. In transformers the transient can be 10s of seconds. Motors are not so bad, because the designed flux densities overall are not so high. The magnetic core losses depend on the hysteresis loop of flux through which the core passes on each cycle. With saturation this is not a fixed value, so it is very difficult to calculate the decay curve and not productive anyhow - since it is different every time the motor is started!

Reply
Reply to Forum Thread 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); Anonymous Poster (5); lyn (2); MoronicBumble (1); msamad (1); nick name (2); PWSlack (2)

Previous in Forum: Bare Copper Conductor Sizing   Next in Forum: Open Delta

Advertisement